    Grounding PV Modules / Mounting System

    Hello everyone,

    I'm a bit confused about if and how to ground PV Modules / Mounting Frames. Some people say it's not necessary some say it's mandatory.
    Some say you don't have to ground the PV Modules because they are class 2. Some say you only have to ground the metal mounting system?

    Some say I have to install a Grounf Fault Detector Interrupter (GFDI) Some say that's not necessary because all grid tied inverters these days have
    Ground Fault Monitoring.

    Can anybody explain to me what is the best thing to do and how to do it?

    Many thanks in advance

    Kind regards

    Johan










  • NEOH
    Solar Fanatic
    • Nov 2010
    • 478

    #2
    The National Electric Code states, "All non-current carrying metal must be grounded"

    There are low-voltage grounding exceptions.
    One of the current carrying conductors may or may not be bonded to ground, it depends upon Inverter Design.
    Last edited by NEOH; 10-01-2017, 08:33 AM.

    Comment

    • ButchDeal
      Solar Fanatic
      • Apr 2014
      • 3802

      #3
      Who are these some people?
      gfci is required but might be provided by the inverter or mppt, if not must be extrernal.
      some areas require afci as well
      almost all arrays need to be grounded and the racking.
      OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15161

        #4
        Originally posted by ButchDeal
        Who are these some people?
        gfci is required but might be provided by the inverter or mppt, if not must be extrernal.
        some areas require afci as well
        almost all arrays need to be grounded and the racking.
        Simple rule of thumb when it comes to electrical systems. "All metal objects, support structures, framing or equipment need to be grounded to avoid a voltage potential that can shock or kill"

        Another saying by most electrical experienced people I have met. "if it ain't grounded it ain't dead or safe"

        Comment

        • Syberdog
          Junior Member
          • Sep 2017
          • 65

          #5
          My understanding is that many of the modern racking components from the big name OEM's have integrated bonding (grounding) provisions.so that when you join the pieces together they from a ground connection.Many other products do not. If they don't then you have to provide grounding. Lookup WEEB clips and grounding jumpers if you need them. Even with self-bonding components you may still have to ground each row of PV modules to the rack frame then to a rebar driven into the ground or use another acceptable method. I am not an electrician so consult one before taking my advice.

          Comment

          • Murby
            Solar Fanatic
            • Jan 2017
            • 303

            #6

            I am using the IronRidge ground mounting system.. a lot of youtube videos show a continuous grounding wire running at the top of the mount that connects all of the XR rails together.. When I called up and talked to IronRidge, they said it wasn't required and that you only need to ground one of them.. the rest of the system grounds itself to that rail because its all metal and bolted together.

            When my electrical inspector looked at my system, he specifically looked at the earth ground and said it was fine. I only grounded one rail to an 8ft ground rod.

            Comment

            • sensij
              Solar Fanatic
              • Sep 2014
              • 5074

              #7
              Originally posted by Murby

              When my electrical inspector looked at my system, he specifically looked at the earth ground and said it was fine. I only grounded one rail to an 8ft ground rod.
              The IronRidge Ground Mount manual clearly agrees with this approach, see page 7. However, if the IronRidge rails were mounted to a structure that had not been tested for grounding (home-built or otherwise), copper tying one rail from each row together could be required.
              CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

              Comment

              • tyab
                Solar Fanatic
                • Sep 2016
                • 227

                #8
                Correct sensij&murby. Interesting side note - I was emailing IronRidge tech support about NFPA 780 testing (they have not done any UL 96/A listing), and ended up having a phone conversation with one of the techs and this subject came up and they said have run into AHJ's that not only want all the rails bonded but in addition want each rail bonded to the 3" pipe.

                So I asked my AHJ (sure helped I could pick his brain after early morning swimming) and he told me that he would accept a single rail bonded if the IronRidge grounding midclamp was properly used but he would rather see (but not required) all the rails bonded. In addition he wants to see a single bond to one of the 3" pipes. For the single pipe bond he said the there was only pressure of the rail mounting adapter to the pipe and with the mounting adapters being anodized it brings into question how good of a bond that will be over the life of the system. Sounds reasonable. I asked him about bonding all the rails and for him its an issue of proper installation of the mid clamps and correct torque values. In his experience - owner installs don't torque them correctly - so he would check a couple easy to access and if they were out of spec he would require all the rails bonded. For those contractors that he knows do a good job, he accepts it as is by IronRidge BUT does make them do a single bond to one of the 3" pipes.

                The church where I run scouts out of put in a large system a couple of years ago (IronRidge - 160 panels) and sure enough on the three mounts you can see where the contractor drilled and use a tap ground on one of the 3" pipes and it bonds to one of the rails. I guess a listed 3" pipe clamp was not on the truck

                So I just bonded all the rails (and did a bond to both of the horizontal pipes) as to not have any issues. For me on my four mounts, it was about an extra $180 in WEEB lugs and 3" pipe ground clamps.

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Originally posted by Syberdog
                  .........to a rebar driven into the ground or use another acceptable method. I am not an electrician so consult one before taking my advice.
                  Rebar is NOT a qualified ground rod.

                  Stores sell a 10' copper plated steel rod, designed and certified as a ground rod.


                  I am not an electrician so consult one before taking my advice.
                  Actually, that's good advice, consult a real person in your code area, to advise you.

                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||