Ok so lets get off to a good start and say that I am a smart guy and with that the knowledge of the benefits of a good solar installer! I may not ask questions perfectly or may not know all the lingo but I still hope someone can assist in resolving our rather large issue.
To get started I have built and installed a 40kw system that is located on my property in the power transmission company ROW with permits from them as alternative use, it has restrictions from hydro such as being built entirely on wood for safety, fencing to their specs etc. My installer is also following all rules and regulations of the national code so we are 100% above board as he has been doing this for a long time.
Everything is completed as far as install goes, inverters, disconnects, main panel all enclosed in weather cabinets also located under the ROW but for 4 days we are trouble shooting a big issue. The systems seem to only run at about 20% or less so where they should be upward of 9500w each inverter at peak time they are only providing 1200-1500w, turns on late in the am and off late afternoon simply because panel production seems low. The system starts in AM producing about 3000w but declines quick by lunch time . We have tested panels individually volts and amps and find no flaws everything in range and as a point of interest there is the same system running at the house away from the ROW working perfectly. All 4 inverters react the same so kind of eliminates equipment failure and the installer has checked, checked and rechecked everything he and I can think of but can not come up with a good reason why they functions the way they do. This is not the first ROW install as a matter of interest there are many large systems around the world doing a good job in similar locations so what the heck?
The only thing we can think of is perhaps harmonic distortion or interference from above lines but find no reference to such things so here we are asking the questions!
Anyone with ideas I would love to hear from you.
Tech info: Inverters Growatt 10000TL-US
solar panels : Blue Sun 250
4 Strings of 12 panels total 48 (allowable oversize based on location)
Location: Lower Vancouver Island British Columbia Canada
Ambient Temp: day 25c night 18c (summer)
Thanks in advance
Grant
To get started I have built and installed a 40kw system that is located on my property in the power transmission company ROW with permits from them as alternative use, it has restrictions from hydro such as being built entirely on wood for safety, fencing to their specs etc. My installer is also following all rules and regulations of the national code so we are 100% above board as he has been doing this for a long time.
Everything is completed as far as install goes, inverters, disconnects, main panel all enclosed in weather cabinets also located under the ROW but for 4 days we are trouble shooting a big issue. The systems seem to only run at about 20% or less so where they should be upward of 9500w each inverter at peak time they are only providing 1200-1500w, turns on late in the am and off late afternoon simply because panel production seems low. The system starts in AM producing about 3000w but declines quick by lunch time . We have tested panels individually volts and amps and find no flaws everything in range and as a point of interest there is the same system running at the house away from the ROW working perfectly. All 4 inverters react the same so kind of eliminates equipment failure and the installer has checked, checked and rechecked everything he and I can think of but can not come up with a good reason why they functions the way they do. This is not the first ROW install as a matter of interest there are many large systems around the world doing a good job in similar locations so what the heck?
The only thing we can think of is perhaps harmonic distortion or interference from above lines but find no reference to such things so here we are asking the questions!
Anyone with ideas I would love to hear from you.
Tech info: Inverters Growatt 10000TL-US
solar panels : Blue Sun 250
4 Strings of 12 panels total 48 (allowable oversize based on location)
Location: Lower Vancouver Island British Columbia Canada
Ambient Temp: day 25c night 18c (summer)
Thanks in advance
Grant
Comment