Hi guys, i know your not meant to parallel regulators that are not designed for it, but what about a reg with lots of manual settings, can you trick it? I should be able to create a manual master based on charge volts keeping one behind the other.
Two MPPT solar regulators in parallel - manual settings
Collapse
X
-
Two MPPT solar regulators in parallel - manual settings
You do not have permission to view this gallery.
This gallery has 1 photos. -
I do it all day long. Anyone with a large battery bank has to have 2 or more charge controllers.
even different brands work well together - IF you configure them properly
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
Comment
-
I have a Tristar MPPT-60 and a Classic 200. Both are configured to a custom charge voltage via factory software, Very easy to do, once you have all the cables and software installed on the windows computer Midday it's very easy to dial in the Classic in both Absorb and Float settings. Set the Absorb time to about the same 2 hours on each, I adjust the classic so that both controllers have a proportionate amount of charge running through each,
You must know what you are doing, if you just try stuffing settings in at random, you get to buy new batteries,Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
What you do want to avoid, however, is connecting more than one CC or GTI to the same set of panels. Each device must have its own dedicated subset of your total panel count.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
WWWComment
-
To emphasize - you don't actually "parallel" the charge controllers. You parallel the outputs only. I contacted Midnight Solar once, and the tech support was sure to make this clear to me when I used the terminology "parallel".Comment
-
Mike I assume you mean you have two separate panel arrays, each with its own controller charging a common battery right? If correct I agree you can use two of any charge controllers you want be it MPPT or PWM.MSEE, PEComment
-
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Yes, a 2000 ah battery bank needs 200ah of charging and there are no single controllers for that. So you would use about 4 PV arrays, each feeding it's own Controller and the controllers all connect to the battery bank (in parallel) But the PV panels are split to 4 arrays, each feeding 1 controller.MSEE, PEComment