1) Use SolarEdge or microinverters
2) Use two SMA inverters (SB4000TL-US-22), which have a 175 V MPPT minimum and would be fine with strings of 6. In that case, you would have 4 mppt inputs. On inverter 1, input 1, you could have 6 panels, inverter 1 input 2 7 panels, inverter 2 input 1 7 panels, inverter 2 input 2 7 panels.
3) Use a Fronius Primo 7.6 inverter. It has a min MPPT of 150 V, or maybe as low as 80 V. Then split into two strings of 6 into one input, and two strings of 7 into the other input, dropping the odd panel as you suggested.
4) Use a different panel, preferably 60 cell, that operates at a lower voltage as has more flexibility.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
Comment
-
However, your point is well taken that using large panels on string inverters is again becoming pretty restrictive. On the older inverters, with narrow voltage operating ranges, there was a time when the panels sizes got up around 200W that strings had to be 10, 11, or 12 panels - period. Now with the >300W panels, we're running into these problems again... We find that the mainstream panels sizes of ~260W are better in that they have less string sizing problems, give us more flexibility fitting them onto most roofs, are about the limit that can be handled by one installer carrying them, and are better value. Of a course the high efficiency panels get around some of these problems but cost way more.BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installedComment
-
I'm doing a SB7700 right now that has 12 260W panels facing south and 2 strings of 8 facing west and another string of 8 facing west. It takes a DC combiner to put all three strings of 8 in parallel on one inverter input, but the alternative was 2 inverters. Putting the east and west strings on the same input is a good trick because they will lose very little productivity and still allow doing this roof with one inverter. My quote won out over the competition because of this.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
This is a hot Phoenix site with 6/12 pitch and 60-cell panels with Vmp= 8.53Vdc so there is never a time when both the East and West sides peak out. There may me instances when the inverter will have to throttle back a bit, but this design comes straight from the advice of a SMA app. engr and it checks out fine on their string sizer.BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installedComment
-
This is a hot Phoenix site with 6/12 pitch and 60-cell panels with Vmp= 8.53Vdc so there is never a time when both the East and West sides peak out. There may me instances when the inverter will have to throttle back a bit, but this design comes straight from the advice of a SMA app. engr and it checks out fine on their string sizer.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
Use two SMA inverters (SB4000TL-US-22), which have a 175 V MPPT minimum and would be fine with strings of 6. In that case, you would have 4 mppt inputs. On inverter 1, input 1, you could have 6 panels, inverter 1 input 2 7 panels, inverter 2 input 1 7 panels, inverter 2 input 2 7 panels.
Also, I'm very confused by SMA's string sizing spreadsheet at SunnyBoyTLUS-22_QDR_v1.10.xlsx. It seems to indicate that the modules per string can vary from 5 to 13.Comment
-
I don't think the spreadsheet is accounting for the difference in MPPT range between the different models of inverter.
4550 / 4000 = 1.14... this is a good loading ratio. The panels will typically produce less than their rating, so you won't really be missing out on any power.
You might actually be better off going for a pair of the SB3800TL, with a 1.20 ratio. You can use a 40 A breaker to protect two of those, which in some cases will help avoid the expense of a panel upgrade, in addition to the savings from going with the smaller inverter.
You can use PVWatts and vary the DC-AC ratio in the Advanced Parameters to get a feel for how much energy you might miss out on by undersizing the inverter. Until the ratio gets to 1.25 or more, with a good array orientation, it usually isn't much.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
Agreed. But I'm still wondering if it's possible to make a single 7.7kw work well. How do you like dropping the odd panel to reach 26, then have 2 strings of 9 panels and 1 string of 8 panels? I guess I'm asking, how much do the different panel orientations mess things up?Comment
-
sensij, are you sure you are looking at this correctly? Isn't the Rated MPPT voltage range the sum total of both strings on the MPPT? For example, suppose I have 2 strings and each is running at 150V. They both meet the start up Voltage requirements (125V/150V) per string. They combine for 300V total, putting them above the 270V MPPT range minimum. Can you confirm or disconfirm?Comment
-
Agreed. But I'm still wondering if it's possible to make a single 7.7kw work well. How do you like dropping the odd panel to reach 26, then have 2 strings of 9 panels and 1 string of 8 panels? I guess I'm asking, how much do the different panel orientations mess things up?
sensij, are you sure you are looking at this correctly? Isn't the Rated MPPT voltage range the sum total of both strings on the MPPT? For example, suppose I have 2 strings and each is running at 150V. They both meet the start up Voltage requirements (125V/150V) per string. They combine for 300V total, putting them above the 270V MPPT range minimum. Can you confirm or disconfirm?CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
sensij, SMA tech support addressed my question today and they say the single 7.7kw inverter will only suffer a slight (1%) efficiency loss if operated below the Rated MPPT voltage range lower limit of 270V. In other words, not enough to justify the expense and trouble of 2 inverters.
As support, they cited data obtained from http://www.gosolarcalifornia.org/equ...-22_240Vac.pdf . I've attached the actual graph they sent me.
Your thoughts?Attached FilesComment
-
sensij, SMA tech support addressed my question today and they say the single 7.7kw inverter will only suffer a slight (1%) efficiency loss if operated below the Rated MPPT voltage range lower limit of 270V. In other words, not enough to justify the expense and trouble of 2 inverters.
As support, they cited data obtained from http://www.gosolarcalifornia.org/equ...-22_240Vac.pdf . I've attached the actual graph they sent me.
Your thoughts?CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment