NEED BIG help choosing Charge Controller/controllers please?
Collapse
X
-
-
The truth is out guys, I'm evolving lol
Comment
-
The truth is out guys, I'm evolving lol
http://www.battcon.com/papersfinal20...lpaper2002.pdf
In a home power plant, the strings are cycle 10,000% more and the batteries quickly diverge in performance.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
-
If you series 2 panels, the voltage doubles, but the amp rating stays the same as just one panel. 12 volt stuff needs AMPS / raw current. I think your fine and better off staying with 12 volt batteries. I might have missed how batteries you have, but i think you mentioned 1200 ah which means you might have 12 batteries. They are gonna love and NEED all of that 70 amps of charging. If you run them down a bit, 70 amps is going to take awhile to get them back to float.Comment
-
I see this in a different light. 8 panels x 8.74 amps ea paralleled should be 70 amps of current.
Yes with this setup, before I got the last 4 panels(1000Watt, 8.75 x 4)...only 4 panels but same everything else...CC(Intrinsic MPPT CC) was sending 50 amps to battery bank. Now for the fun of it I just bought another one(they're good up to 78amps, made in usa)...I talked with the head guy(which is also the electronics engineer) in Massachusetts and he said to put 4 solar panels on one controller, the other 4 to other controller and connect both CC to battery bank on same + and - posts. That will give me 100amps(50 x 2) @peak sunlight here in central Florida.
12 volt applications like amperage. House stuff likes volts and watts. That Xantrex 2000 watt inverter is going to need that 166 amps (or more) that you came up with. And depending on your wire run from the batteries to the inverter, you might need anywhere from 1/0 to 3/0 cable to hook it up.
I'm actually using 250mcm (one size bigger than than or soow 4/0 all with equally sized lugs/terminals and professionally crimped.
If you series 2 panels, the voltage doubles, but the amp rating stays the same as just one panel. 12 volt stuff needs AMPS / raw current. I think your fine and better off staying with 12 volt batteries. I might have missed how batteries you have, but i think you mentioned 1200 ah which means you might have 12 batteries.
Correct. Exactly.
They are gonna love and NEED all of that 70 amps of charging. If you run them down a bit, 70 amps is going to take awhile to get them back to float.Comment
-
Those charge controllers are stepping up the amperage which is a great thing. I would agree with going with two of those as it's more efficient and they aren't tapped out. They don't have to work as hard. 100 amp charging will be good.
4/0 cable is also great. How long is your cable run from the battery to the inverter? Just curious.Comment
-
Comment
-
I see this in a different light. 8 panels x 8.74 amps ea paralleled should be 70 amps of current. 12 volt applications like amperage. House stuff likes volts and watts. That Xantrex 2000 watt inverter is going to need that 166 amps (or more) that you came up with. And depending on your wire run from the batteries to the inverter, you might need anywhere from 1/0 to 3/0 cable to hook it up.
If you series 2 panels, the voltage doubles, but the amp rating stays the same as just one panel. 12 volt stuff needs AMPS / raw current. I think your fine and better off staying with 12 volt batteries. I might have missed how batteries you have, but i think you mentioned 1200 ah which means you might have 12 batteries. They are gonna love and NEED all of that 70 amps of charging. If you run them down a bit, 70 amps is going to take awhile to get them back to float.1150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
So that charge controller is going to take 70 amps into it and turn it into 166 amps to the batteries? If that is the technology, okay. But I don't buy it. I know the MPPT controllers can step up current, but not in that quantity. I'm not looking to argue, so please don't take this that way, I'm just starting my opinion.Comment
-
Guys I keep saying that despite the math and any other factors, with my system, with 4 panels to one CC at the height of the day delivered 50amps(maybe 51). I was there I recorded it. So , not in theory but in factual actual reality, with 4 more panels to one other CC I will be receiving exactly 100amps to battery bank(maybe 102).Comment
-
Guys I keep saying that despite the math and any other factors, with my system, with 4 panels to one CC at the height of the day delivered 50amps(maybe 51). I was there I recorded it. So , not in theory but in factual actual reality, with 4 more panels to one other CC I will be receiving exactly 100amps to battery bank(maybe 102).1150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
So that charge controller is going to take 70 amps into it and turn it into 166 amps to the batteries? If that is the technology, okay. But I don't buy it. I know the MPPT controllers can step up current, but not in that quantity. I'm not looking to argue, so please don't take this that way, I'm just starting my opinion.1150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
The good people here helped me decide on a controller for my 750w system. Both the big Outback and Midnite had fans and that took them out of the running because I don't want to listen to them. The Morningstar TS-MPPT-60 has just a big heat sink.
I did a driveway test of our system running the little air conditioner in 95 degree heat. That controller was rather hot by the end of the test and it was only pushing 45a from 10 am to 5 pm. It made me realize that there was no way I would get away with having the controller inside of the trailer. 45a is actually on the low end as the panels were in series and it was hot. They can run as high as 55a in parallel on a cooler day, a fourth panel would keep the controller maxed during peak sun.
I have the controller set up with a remote display as well as connected to a laptop. The laptop allows me to log info and customize the settings. The only issue I have is I can't customize the temperature compensation values and they don't agree with Lifeline below 20 F or above 90 F.Comment
-
Comment
Comment