    Array Series / Parallel configuration dilemma

    Hi guys, new to this forum, my first post. I am performing my first solar installation for my home – will draw the permit myself and will do the installation myself.

    My PV specs are:
    • Pmax=327W
    • IMP= 5.98A
    • VMP=54.7V
    • VOC=64.9A
    • ISC=6.46A


    Total #of panels = 9 -> System DC Power = 9*327W = 2943W. The panels will be arranged in two rows one above another with 4 panels in first row and 5 panels in second row

    I want to use SMA 3000TL-US string inverter that has following specs:
    • MAX DC VOLT RATING=600V
    • MPPT operating voltage range=125V to 500V
    • MAX POWER @ 40C= 3200W
    • MAX DC CURRENT=15A


    My Temperature correction factor = 1.1292

    If I wire all 9 panels in series on 1 string, I get DC VMAX = 64.9*9*1.1292 = 660V which is more than the inverters max DC Volt rating. That I cannot do.

    If I have two strings: 7 panels in first string, and 2 panels in second string, I get DC VMAX = 64.9*7*1.1292 = 513V than is below Inverters max DC volt rating, but above MPPT operating max voltage of 500V.

    Question: what will happen to MMPT if my system gets to 513V on a very cold but sunny day? Will MMPT go to maximum load resistor and that’s it, or will MPPT circuitry will be bypassed completely? Is it wise to exceed MMPT operating max voltage on paper?

    My other option is to have 6 panels in first string, and 3 panels in second string, DC VMAX=440V, but that will delay my electricity production start time because my PV system will be operating at lower Voltage.

    Thanks, Tomas
    17xE20-327+SMA 5000
    6xSuniva 325+ABB micros
  • PVAndy
    Solar Fanatic
    • Aug 2014
    • 230

    #2
    Originally posted by samotlietuvis
    Hi guys, new to this forum, my first post. I am performing my first solar installation for my home – will draw the permit myself and will do the installation myself.

    My PV specs are:
    • Pmax=327W
    • IMP= 5.98A
    • VMP=54.7V
    • VOC=64.9A
    • ISC=6.46A


    Total #of panels = 9 -> System DC Power = 9*327W = 2943W. The panels will be arranged in two rows one above another with 4 panels in first row and 5 panels in second row

    I want to use SMA 3000TL-US string inverter that has following specs:
    • MAX DC VOLT RATING=600V
    • MPPT operating voltage range=125V to 500V
    • MAX POWER @ 40C= 3200W
    • MAX DC CURRENT=15A


    My Temperature correction factor = 1.1292

    If I wire all 9 panels in series on 1 string, I get DC VMAX = 64.9*9*1.1292 = 660V which is more than the inverters max DC Volt rating. That I cannot do.

    If I have two strings: 7 panels in first string, and 2 panels in second string, I get DC VMAX = 64.9*7*1.1292 = 513V than is below Inverters max DC volt rating, but above MPPT operating max voltage of 500V.

    Question: what will happen to MMPT if my system gets to 513V on a very cold but sunny day? Will MMPT go to maximum load resistor and that’s it, or will MPPT circuitry will be bypassed completely? Is it wise to exceed MMPT operating max voltage on paper?

    My other option is to have 6 panels in first string, and 3 panels in second string, DC VMAX=440V, but that will delay my electricity production start time because my PV system will be operating at lower Voltage.

    Thanks, Tomas
    Strings of 7 and 2 or 6 and 3 won't work. The only string possibility with 9 panels with those characteristics are one of 5 and 1 of 4.

    The problem with a string of 2 is that you won't reach the start voltage of the inverter which is 150 V DC. You need the Voc temp compensated for the hottest day in your local to be greater than the start voltage. The Vmp again compensated for temperature must stay above the 125 V minimum operating voltage. Your not going to have a problem with it not starting early as Vmp is primarily of function of temp and not irradiance.

    Andy

    NABCEP Certified Installation Professional
    PV Design Engineer

    Comment

    • samotlietuvis
      Member
      • Oct 2014
      • 53

      #3
      Andy, I agree with you, but what if I wire 7 in series, and two in series, and on the roof I combine the two in parallel into the junction box; Only one set of wire would go down to the inverter. I understand by doing so I will be sending 2x current down to the inverter, but the inverter can handle 2x the current, and I will used thicker wire to account for the current. Is there any concern with doing 7+2 combined in parallel?

      Would the current from the 7 in series flow to the 2 in series because the 7 in series is at higher Voltage?

      Thanks, Tomas

      Originally posted by PVAndy
      Strings of 7 and 2 or 6 and 3 won't work. The only string possibility with 9 panels with those characteristics are one of 5 and 1 of 4.

      The problem with a string of 2 is that you won't reach the start voltage of the inverter which is 150 V DC. You need the Voc temp compensated for the hottest day in your local to be greater than the start voltage. The Vmp again compensated for temperature must stay above the 125 V minimum operating voltage. Your not going to have a problem with it not starting early as Vmp is primarily of function of temp and not irradiance.

      Andy

      NABCEP Certified Installation Professional
      PV Design Engineer
      17xE20-327+SMA 5000
      6xSuniva 325+ABB micros

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        As Sunking says, Odd or Prime numbers of panels won't work 90% of the time.

        You need one more panel, or hold one back as a spare.

        unless your inverter has 2 separate MPPT inputs, you can only parallel the same number of panels:
        2 parallel strings of 4 or 5 panels. You can't parallel mis-matched strings.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • PVAndy
          Solar Fanatic
          • Aug 2014
          • 230

          #5
          Originally posted by samotlietuvis
          Andy, I agree with you, but what if I wire 7 in series, and two in series, and on the roof I combine the two in parallel into the junction box; Only one set of wire would go down to the inverter. I understand by doing so I will be sending 2x current down to the inverter, but the inverter can handle 2x the current, and I will used thicker wire to account for the current. Is there any concern with doing 7+2 combined in parallel?

          Would the current from the 7 in series flow to the 2 in series because the 7 in series is at higher Voltage?

          Thanks, Tomas
          You would effectively only have 7 panels. The 2 in the short string would not contribute at all. Basic series parallel network analysis.

          The only combination that will work with those panels and inverter are strings of 4 and 5 connected to separate MPPT's. With that inverter with it's low start voltage and very low operating voltage you'll be fine. Remember to turn on Global Optitrac which which by default is off when you receive the inverter. It requires you purchase a SMA Speedwire/Webconnect module and use a laptop to program.

          Andy

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            With 9 panels you only have 3 options. Al in parallel, all in series or 3 x 3. Take your pick. As you have discovered you cannot use any of those 3 options. Trust me you have a lot more expensive surprises just waiting for you to discover.
            MSEE, PE

            Comment

            • inetdog
              Super Moderator
              • May 2012
              • 9909

              #7
              If you get the current model, TL-3000-US-22, which has two independent MPPT inputs, you could use a 5 and 4 combination with no problems.
              If you have the older, non-22, model, then as Sunking stated, you are screwed.
              SunnyBoy 3000 US, 18 BP Solar 175B panels.

              Comment

              • PVAndy
                Solar Fanatic
                • Aug 2014
                • 230

                #8
                Originally posted by inetdog
                If you get the current model, TL-3000-US-22, which has two independent MPPT inputs, you could use a 5 and 4 combination with no problems.
                If you have the older, non-22, model, then as Sunking stated, you are screwed.
                Since it is a 3000TL I believe it has to be a -22 with 2 MPPT. With inverters wide MPPT Range the OP's concerns about string length are unwarranteed

                Andy

                Comment

                • samotlietuvis
                  Member
                  • Oct 2014
                  • 53

                  #9
                  Thanks for all the replies guys - very good points. Did more research to find out that:
                  1) only solar panels of exact or similar current should be wired together in series.
                  2) only solar panels of exact or similar voltage should be wired together in parallel.

                  I am leaning towards using 8 panels only that will give me DC VMAX = 64.9*8*1.1292 = 586V < 600V Max Inverter DC Voltage, and keeping 1 panel as a spare, as Mike90250 recommended.

                  The SMA-3000-TL-US does have two MPPT inputs, and 5 in series + 4 in series will work as well.

                  The size of the panels, 61" x 41" makes them so hard to handle, and I need to take them outside before installing to test each one. I haven't even figured out how I am going to haul them on the roof.

                  Originally posted by Sunking
                  With 9 panels you only have 3 options. Al in parallel, all in series or 3 x 3. Take your pick. As you have discovered you cannot use any of those 3 options. Trust me you have a lot more expensive surprises just waiting for you to discover.
                  Sunking, I hope there will be very few surprises, but you are probably right - this is my first solar job, and the first permit I am drawing in my lifetime

                  I purchased my 2nd home that is 2X bigger than the one I am doing solar for, has pool, and has Spanish Tile Architectural Roof. Closing in a month, moving in after Christmas. Now that will be pain to do, but I already bought solar panels for the home as well. My current home - single story shingle roof south facing space over garage enough for 9x jumbo panels I got is a primer for the job I will do next year.

                  Originally posted by Mike90250
                  As Sunking says, Odd or Prime numbers of panels won't work 90% of the time.

                  You need one more panel, or hold one back as a spare.

                  unless your inverter has 2 separate MPPT inputs, you can only parallel the same number of panels:
                  2 parallel strings of 4 or 5 panels. You can't parallel mis-matched strings.
                  I like the spare option. I do have an extra panels, but no room for it.

                  Originally posted by inetdog
                  If you get the current model, TL-3000-US-22, which has two independent MPPT inputs, you could use a 5 and 4 combination with no problems.
                  If you have the older, non-22, model, then as Sunking stated, you are screwed.
                  It is the new model that has 2x MPPT inputs, and 5x String with 4x String is something I am considering.
                  17xE20-327+SMA 5000
                  6xSuniva 325+ABB micros

                  Comment

                  • sensij
                    Solar Fanatic
                    • Sep 2014
                    • 5074

                    #10
                    Originally posted by samotlietuvis

                    I am leaning towards using 8 panels only that will give me DC VMAX = 64.9*8*1.1292 = 586V < 600V Max Inverter DC Voltage, and keeping 1 panel as a spare, as Mike90250 recommended.

                    I like the spare option. I do have an extra panels, but no room for it.

                    It is the new model that has 2x MPPT inputs, and 5x String with 4x String is something I am considering.
                    5 and 4 on the -22 inverter is fine. Have you gotten any professional quotes? For your next job, doing an installation on those tiles without breaking them or damaging the roof might be challenging. A 3kW system should run between $10k - $12k installed, although the 327 W panels are expensive. Maybe you'll find someone willing to cut you a deal if you agree for them to do the work on both houses.
                    CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                    Comment

                    • samotlietuvis
                      Member
                      • Oct 2014
                      • 53

                      #11
                      Originally posted by sensij
                      5 and 4 on that inverter is fine. Have you gotten any professional quotes? For your next job, doing an installation on those tiles without breaking them or damaging the roof might be challenging. A 3kW system should run between $10k - $12k installed, although the 327 W panels are expensive. Maybe you'll find someone willing to cut you a deal if you agree for them to do the work on both houses.
                      sensij, I agree, the Spanish tiles look very dreadful. The Spanish tile roof I am taking possession is only 9 years old, so hopefully I can find replacement tiles of exactly the same type for the ones that the roofer will break. That 3200sqft home with pool screams for Solar, especially me being in the desert.

                      As far as price goes, I will get done for 1/2 of that before tax rebates, and I will gain solar experience that is on my list of things to know how to do. I already know how to do, do and have done HVAC. If my current job ever goes away, I become PE and do both - Solar and HVAC. Both have very good profit margins.

                      I already bought all the 327 panels for both installs, got lucky on that one. I already have everything I need for my 1st install - SnapNRack System, Inverter / AC Disconnect, Wires, Connectors, Conduit, Professional Crimper, built MC4 connector solar panel tester, thinking about buying irradiance meter. I am drawing permit and performing systems level engineering myself. I am hiring licensed roofer for both jobs - he has have done solar panels before. My neighbor and friend who will be renting my current home from me is an electrical contractor. He is very interested in solar and will be helping me along electrical work during install. According to him Romex 10/2 wire for AC wire run inside garage is per code, and it does not need to be in conduit since it is in garage. I need to confirm that.

                      Tomas
                      17xE20-327+SMA 5000
                      6xSuniva 325+ABB micros

                      Comment

                      • sensij
                        Solar Fanatic
                        • Sep 2014
                        • 5074

                        #12
                        Originally posted by samotlietuvis
                        sensij, I agree, the Spanish tiles look very dreadful. The Spanish tile roof I am taking possession is only 9 years old, so hopefully I can find replacement tiles of exactly the same type for the ones that the roofer will break. That 3200sqft home with pool screams for Solar, especially me being in the desert.

                        As far as price goes, I will get done for 1/2 of that before tax rebates, and I will gain solar experience that is on my list of things to know how to do. I already know how to do, do and have done HVAC. If my current job ever goes away, I become PE and do both - Solar and HVAC. Both have very good profit margins.

                        I already bought all the 327 panels for both installs, got lucky on that one. I already have everything I need for my 1st install - SnapNRack System, Inverter / AC Disconnect, Wires, Connectors, Conduit, Professional Crimper, built MC4 connector solar panel tester, thinking about buying irradiance meter. I am drawing permit and performing systems level engineering myself. I am hiring licensed roofer for both jobs - he has have done solar panels before. My neighbor and friend who will be renting my current home from me is an electrical contractor. He is very interested in solar and will be helping me along electrical work during install. According to him Romex 10/2 wire for AC wire run inside garage is per code, and it does not need to be in conduit since it is in garage. I need to confirm that.

                        Tomas
                        You might find the Mike Holt forums to be a good source of education on the code-compliant electrical design. Do a search for any of your questions, almost everything you can think to ask has been answered there before.
                        CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                        Comment

                        • samotlietuvis
                          Member
                          • Oct 2014
                          • 53

                          #13
                          Originally posted by sensij
                          You might find the Mike Holt forums to be a good source of education on the code-compliant electrical design. Do a search for any of your questions, almost everything you can think to ask has been answered there before.

                          Thanks. I read through Mike Holt's "WIRING METHODS AND MATERIALS" publication, and I have all the solar code applicable to where I live compiled in one folder, and I reference every calculation and tables I am using in my permit so that Permit Approver understands that I understand. I do use search quite a bit. Trying to bounce a few ideas to see what's per code, and what's not. If I were not to do the permit myself, them I would not gain the experience I am looking for.
                          17xE20-327+SMA 5000
                          6xSuniva 325+ABB micros

                          Comment

                          • sensij
                            Solar Fanatic
                            • Sep 2014
                            • 5074

                            #14
                            Originally posted by samotlietuvis
                            Thanks. I read through Mike Holt's "WIRING METHODS AND MATERIALS" publication, and I have all the solar code applicable to where I live compiled in one folder, and I reference every calculation and tables I am using in my permit so that Permit Approver understands that I understand. I do use search quite a bit. Trying to bounce a few ideas to see what's per code, and what's not. If I were not to do the permit myself, them I would not gain the experience I am looking for.
                            Ideas for more problems you might run into can be found here found here. Good luck!
                            CS6P-260P/SE3000 - http://tiny.cc/ed5ozx