I was curious, say for instance if I have 2 strings producing 2100 watts @ 5 amps per string would it be better to have 3 strings producing 2100 watts @ 5 amps per strings. The real question is the amperage of having 3 0r 2 strings. Im guessing the 3 strings would be better, but Im asking just in case. Thanks
More strings with less panels or less strings with more panels!
Collapse
X
-
More strings with less panels or less strings with more panels!
Smart Meters are Smart, but if you know how to outsmart them. Well its still all good! -
I was curious, say for instance if I have 2 strings producing 2100 watts @ 5 amps per string would it be better to have 3 strings producing 2100 watts @ 5 amps per strings. The real question is the amperage of having 3 0r 2 strings. Im guessing the 3 strings would be better, but Im asking just in case. Thanks
Meanwhile, your inverter has a sweet spot for input voltage. My SMA inverter likes 240VDC input, it's efficiency is highest in that range. Your inverter might be different. I'd optimize your string voltage for the maximum inverter efficiency (this time using the maximum power point voltage, not Voc).
Quite often, all of these factors will dictate a maximum number of panels lower than you'd guess.Lawrence Lile, PE -
I was curious, say for instance if I have 2 strings producing 2100 watts @ 5 amps per string would it be better to have 3 strings producing 2100 watts @ 5 amps per strings. The real question is the amperage of having 3 0r 2 strings. Im guessing the 3 strings would be better, but Im asking just in case. Thanks
Most of the inverters i've worked with like higher voltages better (more efficient) than lower (still within range).
If there is a possibility of shading, i would rather have more strings.Comment
-
I was curious, say for instance if I have 2 strings producing 2100 watts @ 5 amps per string would it be better to have 3 strings producing 2100 watts @ 5 amps per strings. The real question is the amperage of having 3 0r 2 strings. Im guessing the 3 strings would be better, but Im asking just in case. ThanksComment
-
Fewer strings, higher voltage, to the limit of the inverter on a cold day, reduces the "copper loss" of amps in wires. Inverter efficency begins to fall off, if input voltage is way above the sell voltage, but it's only a couple %. Better manuals will have charts.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
I recommend using the fewest strings possible with the most modules per string to reduce BOS costs/components.
Thats the whole idea behind bipolar inverters and 1200V max DC utility systems, since it is current not voltage that requires you to use bigger wire.Comment