I have a 1000 watt solar setup now. We have lots of wind so I'm wanting to add a wind generator with a 500 watt inverter. But, if I put 2 grid-tie inverters on the same circuit, with they interact badly? I don't want the anti-islanding to be compromised nor do I want them to damage each other. One is 20' from the house and the other will be about 200' away from it. Any thoughts or warnings about it?
two grid-tie inverters and how they interact with each other
Collapse
X
-
-
I have a 1000 watt solar setup now. We have lots of wind so I'm wanting to add a wind generator with a 500 watt inverter. But, if I put 2 grid-tie inverters on the same circuit, with they interact badly? I don't want the anti-islanding to be compromised nor do I want them to damage each other. One is 20' from the house and the other will be about 200' away from it. Any thoughts or warnings about it?
Multiple Micro-Inverters are used without compromise to anti-islanding...
You've given no details on your 2 GT inverters... I'm guessing their quality would help answer your question.[CENTER]SunLight @ Night[/CENTER] -
I have a 1000 watt solar setup now. We have lots of wind so I'm wanting to add a wind generator with a 500 watt inverter. But, if I put 2 grid-tie inverters on the same circuit, with they interact badly? I don't want the anti-islanding to be compromised nor do I want them to damage each other. One is 20' from the house and the other will be about 200' away from it. Any thoughts or warnings about it?[SIGPIC][/SIGPIC]Comment
-
It is common to put many microinverters on the same circuit. Whether this will work for you depends on what equipment you are using, how your system is wired etc. In general inverters designed to meet UL 1741 / IEEE 1547, and installed correctly, will not "interact badly" with each other - they are designed to operate on grids with (potentially) multiple inverters.Comment
-
It is common to put many microinverters on the same circuit. Whether this will work for you depends on what equipment you are using, how your system is wired etc. In general inverters designed to meet UL 1741 / IEEE 1547, and installed correctly, will not "interact badly" with each other - they are designed to operate on grids with (potentially) multiple inverters.
If you have a very small wire in any GTI inverter to grid connection, the voltage at the inverter terminals will rise and you will waste power.
But a resistance beyond some point will also trigger the anti-islanding circuitry.
A wire connection to grid which is just good enough to satisfy the anti-islanding algorithm could still be high enough resistance to allow for some interaction among the microinverters or string inverters, but it seems very unlikely, and only in connection with a poor installation.
I would be sure to size the 200' run of wire large enough to keep the voltage drop (voltage rise when the GTI is running) below 3%, and lower than that if practical.
Consider using aluminum wire (with proper terminations on both ends and NO-OX-ID type antioxidant grease) to keep the cost down. Sunking swears by that product.Last edited by inetdog; 04-25-2014, 06:31 PM.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Were I to add a second GTI, I would put it on the other leg of my 220V feed. No scientific reason, just my gut feeling about keeping things balanced.Comment
-
2 Power Jack inverters. I know they are not the best quality but i haven't had any problems for the first year of operation.Comment
-
Bad idea![SIGPIC][/SIGPIC]Comment
-
NOT GOOD, as Russ stated above.
I have a 1000 watt solar setup now. We have lots of wind so I'm wanting to add a wind generator with a 500 watt inverter. But, if I put 2 grid-tie inverters on the same circuit, with they interact badly? I don't want the anti-islanding to be compromised nor do I want them to damage each other. One is 20' from the house and the other will be about 200' away from it. Any thoughts or warnings about it?
Yes, they will interact badly, and damage each other.
Anti-Islanding will be compromised.
Thoughts or warnings:
You are putting your property at risk of fire damage,
and the lives of line-men and neighbors at risk of injury or death.[CENTER]SunLight @ Night[/CENTER]Comment