Location of the AC Disconnect

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Swiss
    Junior Member
    • Dec 2009
    • 2

    #1

    Location of the AC Disconnect

    Hello everyone and Happy Holidays,
    I am installing a 62 panels on top of my parents shop (flat roof), but the meter is located at the main house at the other end of their property. The shop has a 200 amp sub panel where we would like to place the inverter, DC disconnect and other equipment. What is the code on the location of the AC disconnect? Can I use a knife disconnect at the meter for the subfeeds to the shop? I am an electrician not a solar guy go easy on me.
    Thanks
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    not sure what you are asking. You have DC panels, and need a DC rated dsconnect

    The inverter needs a lockable (by power co & FD) disconnect, they can access from outside. AC disconnect needs to be near where the inverter feeds into a panel. My disconnect has a large jumper block that gets removed to lock out.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Swiss
      Junior Member
      • Dec 2009
      • 2

      #3
      AC Disconnect

      I want to place the DC disconnects and inverters next to the subpanel that is in the shop (200amp). My question is does the AC disconnect need to be next to the meter/main electrical panel? Or can I place it on the outside of the shop (300' away from the meter/main)?
      There are 2 structures on my parents property the main electrical service w/ the meter is on their house (Split 200 amp service). The House and shop are about 300' apart. I would imagine the Utility and F.D. want the AC disconnect to be next to the meter, I dont know.
      Thanks

      Comment

      • lzr
        Junior Member
        • Jan 2010
        • 4

        #4
        Originally posted by Swiss
        ....The House and shop are about 300' apart. I would imagine the Utility and F.D. want the AC disconnect to be next to the meter, I dont know.
        Thanks
        It depends on your local codes. I don't believe there are any general requirements for an additional AC disconnect at all. The thing is, a grid tie inverter already has an automatic AC disconnect inside. Each local utility may have its own requirements and probably yes, they may want an additional AC disconnect be close to the main service disconnect.

        Comment

        • mountain
          Member
          • Nov 2009
          • 56

          #5
          I'm an electrician in Canada, but regardless of location, this logic should be applicable.

          1) Non permit electrical work, home-owner, only intended for replacement of damaged components, plugs, light-fixtures, on branch circuits. For direct connection of any electrical equipment directly to a 200A electrical feeder, you legally are required to take out an electrical permit. (unless you are located somewhere quite uncivilized).
          Illegal non-permitted electrical work will void your house insurance.

          2) Assuming you live in North America, and thus the voltage of a 200A feeder would likely be 240/120V, 1-phase, & include a neutral.
          If the inverter is not actually rated at 240V, 200A, then you must have some form of electrical protection, which may be a breaker, or else a fused disconnect.

          3) From an electrical protection perspective, the inverter should be viewed as both a energy source, and a potential load.

          M