Hi.
As outlined below I'm upgrading/improving a small solar set-up powering a remote wireless relay system.
Presently it has nothing in the way of breakers between the panels and the controller or the controller and the battery, but I understand they are a good thing to have there.
It's a small set-up, with three panels in parallel putting out (in theory) 13.82 amps at 17.6v. Our supplier's price list has DC breakers for 10, 15, 20, 50 Amps and upwards all at 150v, and all at the same price.
I think I'm right to say a 15 Amp breaker would do between the panels and the controller but we'd need a 20 Amp one between the controller (MPPT) and the battery as it would be putting out 13v float at >18 Amps, but as they're the same price is there any penalty to having oversized breakers - say 2 x 50 Amp ones - to allow for future expansion?
As outlined below I'm upgrading/improving a small solar set-up powering a remote wireless relay system.
Presently it has nothing in the way of breakers between the panels and the controller or the controller and the battery, but I understand they are a good thing to have there.
It's a small set-up, with three panels in parallel putting out (in theory) 13.82 amps at 17.6v. Our supplier's price list has DC breakers for 10, 15, 20, 50 Amps and upwards all at 150v, and all at the same price.
I think I'm right to say a 15 Amp breaker would do between the panels and the controller but we'd need a 20 Amp one between the controller (MPPT) and the battery as it would be putting out 13v float at >18 Amps, but as they're the same price is there any penalty to having oversized breakers - say 2 x 50 Amp ones - to allow for future expansion?