So I bought a new electric panel that is solar ready to allow for higher amps from the about to be installed solar system. The panel is an Eaton CH 200 Amp 42-Circuit EUSERC Solar Power Meter Breaker Outdoor Surface Mount (225Bus,200amp breaker), that says it allows 70amp solar backfeed. Soooo, when I spoke with the solar vendor, they said the 70 amps had to be reduced by the 120% rule which would only allow about a 13.4kw inverter. Since the 2 inverters would be 2 7.6KW inverters and would max out at 64 amps, this would not work. Supposedly their senior engineer confirmed this. So, I called Eaton tech support, who confirmed with a supervisor, that the full 70 amps could be used and the 64 amps from my 2 inverters would be fine. Makes sense as how do they advertise it as a 70amp solar ready panel? So, who is right? And why is that not just written plainly somewhere
????