I have 15KW Fronius Primo in a system with 2 inverters that is giving DC isolation faults at weird times. It gets down below 2kohms according to inverter error. The Primo doesn’t seem to monitor the DC isolation in realtime, only at startup. The only times I get the error is after a hot day “100+ deg” with NO dew overnight. If it’s raining or heavy dew it does fine.
I’ve tried to catch it when the isolation is low but the lowest reading I can get from the Primo is 8.5k. The inverter has four 12 panel strings on it and my only next step that I can think of is to isolate the strings and see if one is lower than the others but kinda wonder if that will really point to the problem string since I can never catch it doing it.
I’ve tried to catch it when the isolation is low but the lowest reading I can get from the Primo is 8.5k. The inverter has four 12 panel strings on it and my only next step that I can think of is to isolate the strings and see if one is lower than the others but kinda wonder if that will really point to the problem string since I can never catch it doing it.