1 inverter 100 KW
10 x MPPT
20 x string inputs
Max. Input Voltage 1100 Volt
Start Voltage 200V
Panel 540 Watt
VOC Panel 49 Volts
So we can make strings of 20 Panels
1 String is 10,800 Watt
So with 10 strings we have 108 KW
That means that 10 Slots for strings will remain unused.
My question is if this is a good idee?
Or must we make smaller strings so we can end up with occupying more slots?
For example string of 16 panels
1 string 8,640 Watt
This means 12 strings
Or even 12 panels (we will still reach the Start Voltage 200V)
1 string 6,480 Watt
16 strings
What is the best thing to do and why?