Please refer to the attached one line diagram of my PV system.
My system consists of 28 panels arranged in 4 strings of 7 panels. For simplicity I’ll call each string of panels string#1, string#2, string#3, string#4.
In my hybrid all-in-one inverter there is 2 charge controllers called PV1 and PV2. Each charge controller has independent input terminals to accept 2 strings of panels so strings #1 and #2 will be run to charge controller PV1 and strings #3 and #4 will be run to charge controller PV2. String #1 and #2 are paralleled at the inverter on PV1 and String #3 and #4 are paralleled at the inverter on PV2.
My inverter limits the input current on PV1 and PV2 to 20amps max on each charge controller. The solar panels have a Isc=11.66A and a max series fuse rating of 25A.
Am I correct to understand that the electrical code does not require any over current device (i.e. fuse or breaker) for installations with 2 strings in parallel due to the fact that the fault current cannot exceed the max fuse rating size of the panels nor does it exceed the amperage rating of the cables?
Am I also correct to assume that I do not require a combiner box as I am only paralleling 2 strings and all that is required is a 4 pole DC disconnect switch for String#1 and String #2 and a 4 pole disconnect switch for Strings #3 and #4?
Solar oneline.png
My system consists of 28 panels arranged in 4 strings of 7 panels. For simplicity I’ll call each string of panels string#1, string#2, string#3, string#4.
In my hybrid all-in-one inverter there is 2 charge controllers called PV1 and PV2. Each charge controller has independent input terminals to accept 2 strings of panels so strings #1 and #2 will be run to charge controller PV1 and strings #3 and #4 will be run to charge controller PV2. String #1 and #2 are paralleled at the inverter on PV1 and String #3 and #4 are paralleled at the inverter on PV2.
My inverter limits the input current on PV1 and PV2 to 20amps max on each charge controller. The solar panels have a Isc=11.66A and a max series fuse rating of 25A.
Am I correct to understand that the electrical code does not require any over current device (i.e. fuse or breaker) for installations with 2 strings in parallel due to the fact that the fault current cannot exceed the max fuse rating size of the panels nor does it exceed the amperage rating of the cables?
Am I also correct to assume that I do not require a combiner box as I am only paralleling 2 strings and all that is required is a 4 pole DC disconnect switch for String#1 and String #2 and a 4 pole disconnect switch for Strings #3 and #4?
Solar oneline.png
Comment