The application is a ~30kW system root mounted on a steel building. The question is how to ground.
There will be four strings, and each one will feed an inverter in a different building. The string voltage will be about 600Vdc. The steel outbuilding has two connections to the main building: the first is an underground conduit with 100A 240Vac sub-feed to that building. The second is an underground conduit with 4 DC string loops, plus a ground conductor.
The 240 Vac subpanel will be grounded with a single rod.
Here is where my concern begins. The ground for the PV system also gets tied to that single grounding rod. Of course, the PV system being on a steel roof on a building with steel siding, means that in theory the entire building sits at the potential of the grounding rod, which has an implied 20 ohm impedance to the earth. The exact impedance is not really important, but the fact that there is a non-zero impedance is.
Consider that there could be a fault in the DC conduit, and that this could mean that PV potential of +/- 600Vdc could return via the ground to the steel building, it is possible that the building could be energized. Furthermore, this has a potential should the grounding rod fail in some way, of backfeeding HV DC into the main building. The setting is a farm, and the mainbuilding is a cluster of connected buildings including a residence.
I consider this risk to be significant, and would like to know how it might be mitigated. We have consulted with the code inspector, and confirmed his grounding expectations. Explaining our concern, he has acknowledged it. While he did not offer an alternative, he appears to be open to a rational solution. Any ideas or similar experiences.
There will be four strings, and each one will feed an inverter in a different building. The string voltage will be about 600Vdc. The steel outbuilding has two connections to the main building: the first is an underground conduit with 100A 240Vac sub-feed to that building. The second is an underground conduit with 4 DC string loops, plus a ground conductor.
The 240 Vac subpanel will be grounded with a single rod.
Here is where my concern begins. The ground for the PV system also gets tied to that single grounding rod. Of course, the PV system being on a steel roof on a building with steel siding, means that in theory the entire building sits at the potential of the grounding rod, which has an implied 20 ohm impedance to the earth. The exact impedance is not really important, but the fact that there is a non-zero impedance is.
Consider that there could be a fault in the DC conduit, and that this could mean that PV potential of +/- 600Vdc could return via the ground to the steel building, it is possible that the building could be energized. Furthermore, this has a potential should the grounding rod fail in some way, of backfeeding HV DC into the main building. The setting is a farm, and the mainbuilding is a cluster of connected buildings including a residence.
I consider this risk to be significant, and would like to know how it might be mitigated. We have consulted with the code inspector, and confirmed his grounding expectations. Explaining our concern, he has acknowledged it. While he did not offer an alternative, he appears to be open to a rational solution. Any ideas or similar experiences.