So, you must have several strings of PV wired to the charge controller. At your combiner box, shut all strings but one, down. let controller stabilize, and record the power, and then add another string, remove the first, let stabilize, and record the power until you have tested and recorded all strings. All should be within a couple % of the rest. You may have some bad panels, and comparing strings is the quick way to test for them.
I've got 800ah of batteries @ 48V, and 5kw of PV, and just able to get by in winter with 7kwh daily usage, 2 cloudy days, and I need generator. If you are over paneled, you can switch some strings off in the summer and bring them back on for cloudy conditions. Having a decent combiner box with breakers is critical.
I've got 800ah of batteries @ 48V, and 5kw of PV, and just able to get by in winter with 7kwh daily usage, 2 cloudy days, and I need generator. If you are over paneled, you can switch some strings off in the summer and bring them back on for cloudy conditions. Having a decent combiner box with breakers is critical.