Hi, I'm a newbie here and I'm just starting a solar installation using 21 of the new Enphase micro inverters - each one will be fed by a BP175 panel. (The Enphase units convert DC to 240VAC in a small inverter right behind the panels and the AC circuits connect in series).
My question is this. I have to install a 240VAC load panel for the power coming from the 2 240V circuits coming from the roof. The inverters wire in AC strings with a max of 15Amp capacity. So I'm running 12/3 cable to the roof from the load panel in short runs of no more than 12 feet. But I'm not sure what wire size to use for the 25+ ft. run from the load panel to the main load center. In theory it will be carrying up to 30 Amps at 240VAC, so can I use the same 12/3 BX? or do I need to go up to 10 gauge wire?
You can read my blog about this installation at:
Thanks
Guy
My question is this. I have to install a 240VAC load panel for the power coming from the 2 240V circuits coming from the roof. The inverters wire in AC strings with a max of 15Amp capacity. So I'm running 12/3 cable to the roof from the load panel in short runs of no more than 12 feet. But I'm not sure what wire size to use for the 25+ ft. run from the load panel to the main load center. In theory it will be carrying up to 30 Amps at 240VAC, so can I use the same 12/3 BX? or do I need to go up to 10 gauge wire?
You can read my blog about this installation at:
Thanks
Guy