I'm in the process of planning a photovoltaic system that will include initially two arrays on west- and east-facing roofs of our pool house (total of 3.65 kW), and later, I'd also like to include a separate south-facing roof from over the BBQ island (2.2 kW). The pool-house is wired to the main breaker panel (rated 200A, main breaker is 150A) on the house via a 50A breaker and 8 gauge copper (2 hots, neutral and ground), about 100 ft of underground wiring in conduit. This feeder wire connects to a main lug sub-panel (rated 100A) on the back of the pool house that feeds the pool house and pool equipment sub-panel. This pool house sub-panel also feeds a second sub-panel (rated 100A) via underground conduit (10 gauge copper, 2 hots, neutral and ground) via a 30A breaker in the sub-panel. The idea is to take the output from the two arrays (which will use micro-inverters) on the pool-house roof and connect them to the pool house sub-panel via a 20A/220 backfeed breaker. When I add the additional array on top of the BBQ island roof, I plan to wire that array into a 15A back-feed breaker in the second sub-panel on the BBQ island. Based on my reading of the NEC code regarding this (690.64 Point of Connection), this should be permissible since the total wattage back-fed to the main panel will be less than 25A. The permissible back-feed on a 200A panel with a 150A main breaker would be 90A.
I was originally thinking that I would have to install new conduit to do home-runs from the three arrays back to the main panel, but after reading the NEC, it seems I can just back-feed the existing wiring, assuming I stay within the 120% rule and respect the wire gauge ampacity ratings. Note that all sub-panels have separate ground buses, and all are tied to the ground bus on the main panel. I may need to add an additional grounding rod at the pool house panel... I'm not quite sure about that (likely depends on what our building inspector requires). Any thoughts?
I was originally thinking that I would have to install new conduit to do home-runs from the three arrays back to the main panel, but after reading the NEC, it seems I can just back-feed the existing wiring, assuming I stay within the 120% rule and respect the wire gauge ampacity ratings. Note that all sub-panels have separate ground buses, and all are tied to the ground bus on the main panel. I may need to add an additional grounding rod at the pool house panel... I'm not quite sure about that (likely depends on what our building inspector requires). Any thoughts?
Comment