Setup:
Underground utilities
Outside meter
Outside main breaker leading to inside subpanels.
A new inverter will be inside of the basement, about 1 meter away.
Where must the AC and DC disconnect be?
Standing right in front of either the main panel or the inverter, you can't see the other, without leaning over and looking out a window.
AC Disconnect Inside Basement.jpg
--
It seems that the fire department will want the disconnect at the main panel.
It seems a future solar tech will want the ac disconnect next to the inverter.
Section 690.15 says "an ac disconnecting means shall be mounted within sight or in each inverter.".
--
The 2020 code adds a safety requirement. Installing the AC disconnect indoors would increase the chance
of a child trying to open or operate it:
2020 NEC Significant Code Changes Part 4 690 โ Solar Photovoltaic (PV) Systems 690.15"
"Where disconnecting means of equipment operating above 30 volts are readily accessible to unqualified persons, any enclosure door or hinged cover that exposes live parts when open shall be locked or require a tool to open."
--
The 2020 code adds:
"An equipment disconnecting means shall be permitted to be remote from the equipment where the equipment disconnecting means can be remotely operated from within 3 m (10 ft) of the equipment."
So does that mean the AC disconnect can be outside, as that's less than 3 meters away? What does "remotely operated" mean?
Underground utilities
Outside meter
Outside main breaker leading to inside subpanels.
A new inverter will be inside of the basement, about 1 meter away.
Where must the AC and DC disconnect be?
Standing right in front of either the main panel or the inverter, you can't see the other, without leaning over and looking out a window.
AC Disconnect Inside Basement.jpg
--
It seems that the fire department will want the disconnect at the main panel.
It seems a future solar tech will want the ac disconnect next to the inverter.
Section 690.15 says "an ac disconnecting means shall be mounted within sight or in each inverter.".
--
The 2020 code adds a safety requirement. Installing the AC disconnect indoors would increase the chance
of a child trying to open or operate it:
2020 NEC Significant Code Changes Part 4 690 โ Solar Photovoltaic (PV) Systems 690.15"
"Where disconnecting means of equipment operating above 30 volts are readily accessible to unqualified persons, any enclosure door or hinged cover that exposes live parts when open shall be locked or require a tool to open."
--
The 2020 code adds:
"An equipment disconnecting means shall be permitted to be remote from the equipment where the equipment disconnecting means can be remotely operated from within 3 m (10 ft) of the equipment."
So does that mean the AC disconnect can be outside, as that's less than 3 meters away? What does "remotely operated" mean?
Comment