I'm confused about many of the details of wiring my DIY ground-mount system. I have extensive experience with ordinary home wiring. My jurisdiction is subject to the 2017 NEC; DIY wiring is allowed by a homeowner (subject to inspection of course). Here is my current thinking:
Screen Shot 2020-02-26 at 4.44.23 PM.png
I'll have 16 panels connected in two strings to the two MPPT inputs on an SMA SunnyBoy SB 3.8-1SP-US-41 inverter.; the inverter has an integrated DC disconnect. The inverter will be attached to the ground-mount, so I'll be running 240vac to the house. My grid connection is 240v split-phase.
I'll also be adding an essential-loads sub-panel next to my main panel, for use with a small generator. It'll be a main lug panel, with two interlocked double-pole breakers, one connected to a generator jack and the other to a double-pole breaker in the main panel. Possibly if the generator has an un-defeatable ground/neutral bond, I'll need to use a transfer switch or interlocked 3-pole breakers.
Being ground-mount, the system does not require rapid-shutdown. In fact, the DC will remain active during grid outages, so that I may use the inverter's "secure power" outlet (thus enabling a little grid-down power when the sun is shining). The UL1741 compliant inverter will shut down the 240vac feed coming into the utility room during grid outages.
Questions:
1. Am I missing any components, or are there some I might omit ?
- I don't need a DC disconnect as that is built into the inverter.
- Do I need an AC disconnect near the POCO meter, since the AC line will go dead when the grid is down anyhow ?
- Must I (or might I want to) add a meter for solar generated power ? Or will the inverter monitor that for me ?
2. How do I go from the male and female MC4 connections at each end of each string to the bare wire ends for connection to the inverter ? Are there simply MC4 cables I can buy ?
3. Should the AC from the inverter be connected to a double-pole breaker in the main panel (as shown) ? I'm pretty sure I've seen diagrams where the AC is simply spliced into the cables from the meter to the main breaker.
4. I understand the AC connection between inverter and house should be 3-conductor plus ground (this inverter requires neutral connection). The panels will be mounted a treated-wood structure, so each will require a grounding lug. The panel grounds are connected to the inverter, the ground in the AC cable and a grounding rod. However, I'm unclear if it's necessary (or possible) to connected the '-' MPPT inputs to ground.
Screen Shot 2020-02-26 at 4.44.23 PM.png
I'll have 16 panels connected in two strings to the two MPPT inputs on an SMA SunnyBoy SB 3.8-1SP-US-41 inverter.; the inverter has an integrated DC disconnect. The inverter will be attached to the ground-mount, so I'll be running 240vac to the house. My grid connection is 240v split-phase.
I'll also be adding an essential-loads sub-panel next to my main panel, for use with a small generator. It'll be a main lug panel, with two interlocked double-pole breakers, one connected to a generator jack and the other to a double-pole breaker in the main panel. Possibly if the generator has an un-defeatable ground/neutral bond, I'll need to use a transfer switch or interlocked 3-pole breakers.
Being ground-mount, the system does not require rapid-shutdown. In fact, the DC will remain active during grid outages, so that I may use the inverter's "secure power" outlet (thus enabling a little grid-down power when the sun is shining). The UL1741 compliant inverter will shut down the 240vac feed coming into the utility room during grid outages.
Questions:
1. Am I missing any components, or are there some I might omit ?
- I don't need a DC disconnect as that is built into the inverter.
- Do I need an AC disconnect near the POCO meter, since the AC line will go dead when the grid is down anyhow ?
- Must I (or might I want to) add a meter for solar generated power ? Or will the inverter monitor that for me ?
2. How do I go from the male and female MC4 connections at each end of each string to the bare wire ends for connection to the inverter ? Are there simply MC4 cables I can buy ?
3. Should the AC from the inverter be connected to a double-pole breaker in the main panel (as shown) ? I'm pretty sure I've seen diagrams where the AC is simply spliced into the cables from the meter to the main breaker.
4. I understand the AC connection between inverter and house should be 3-conductor plus ground (this inverter requires neutral connection). The panels will be mounted a treated-wood structure, so each will require a grounding lug. The panel grounds are connected to the inverter, the ground in the AC cable and a grounding rod. However, I'm unclear if it's necessary (or possible) to connected the '-' MPPT inputs to ground.
Comment