Hi all
My original install was 16 amerisolar panels (250W) with a tranergy pvi4000 inverter, worked no problems for several years.
I recently upgraded to a solaredge system, incorporating 16 p300 optimisers and a SE3680H HD Wave inverter. The dc string is on 4mm2 wire and the inverter is 5 meters from the consumer unit on 4mm2 twin and earth.
The system had been working rock solid for 2 weeks and then on wednesday this week it threw a series of errors; RSD error, HW error and AC voltage high error, and since then the inverter will just not work.
I contacted solaredge who have remotely updated the firmware, but now, every time the inverter wakes up to go into production mode it throws the 18x6F AC Voltage too high fault. Solar edge are now telling me its a problem with the grid / my domestic wiring, which I dont agree with, as every time the error occurs the AC voltage is not high, it sits around 235volts. This has been checked at the utility meter as well.
What I have seen a change in is the DC Voltage. For the two weeks it worked, it sat around 360volts, but on the wednesday when the system broke, it shot up to 450, and now every time the inverter tries to go into production mode the DC voltage goes to 450, faults and stops production.
Here is a link to some graphs and pics on inverter screen, shared from my onedrive: https://1drv.ms/f/s!Aj9zNAQZl-OcoLN3S-h2RlpMeE-2Hw
Any advice would be most appreciated. I did notice another post around this error and the
John
My original install was 16 amerisolar panels (250W) with a tranergy pvi4000 inverter, worked no problems for several years.
I recently upgraded to a solaredge system, incorporating 16 p300 optimisers and a SE3680H HD Wave inverter. The dc string is on 4mm2 wire and the inverter is 5 meters from the consumer unit on 4mm2 twin and earth.
The system had been working rock solid for 2 weeks and then on wednesday this week it threw a series of errors; RSD error, HW error and AC voltage high error, and since then the inverter will just not work.
I contacted solaredge who have remotely updated the firmware, but now, every time the inverter wakes up to go into production mode it throws the 18x6F AC Voltage too high fault. Solar edge are now telling me its a problem with the grid / my domestic wiring, which I dont agree with, as every time the error occurs the AC voltage is not high, it sits around 235volts. This has been checked at the utility meter as well.
What I have seen a change in is the DC Voltage. For the two weeks it worked, it sat around 360volts, but on the wednesday when the system broke, it shot up to 450, and now every time the inverter tries to go into production mode the DC voltage goes to 450, faults and stops production.
Here is a link to some graphs and pics on inverter screen, shared from my onedrive: https://1drv.ms/f/s!Aj9zNAQZl-OcoLN3S-h2RlpMeE-2Hw
Any advice would be most appreciated. I did notice another post around this error and the
John