    How to protect photovoltaic system from lightning and surge

    A damaging surge can occur from lightning and surge that strikes a long distance from the system, or even between clouds. Lightning and surge is a common cause of failures in photovoltaic (PV) and wind-electric systems. But most lightning and surge damage is preventable. Here are some of the most cost-effective techniques that are generally accepted by power system installers, based on decades of experience. Follow this advice, and you have a very good chance of avoiding lightning and surge damage to your renewable energy (RE) photovoltaic system.


    Lightning and Surge Protection


    Specialized surge arrestors (DC surge arrestors and AC surge protection devices) and (possibly) lightning rods are recommended for sites with any of the following conditions:

    • Isolated location on high ground in a severe lightning area
    • Dry, rocky, or otherwise poorly conductive soil
    • Wire runs longer than 100 feet (30 m)


    Surge Arrestors


    Surge arresters are designed to absorb voltage spikes caused by electrical storms (or out-of-spec utility power), and effectively allow the surge to bypass power wiring and your equipment. Surge arresters should be installed at both ends of any long wire run that is connected to any part of your system, including AC lines from an inverter. Surge arresters are made for various voltages for both AC and DC. Be sure to use the appropriate surge arresters for your application.


    Lightning Rods

    “Lightning rods” are static discharge devices that are placed above buildings and solar-electric arrays, and connected to ground. They are meant to prevent the buildup of static charge and eventual ionization of the surrounding atmosphere. They can help prevent a strike, and can provide a path for very high current to ground if a strike does occur. Modern devices are spike-shaped, often with multiple points.

    Lighting rods are typically only used at sites that experience extreme electrical storms. If you think your site falls into this category, hire a contractor who has experience in lightning protection. If your system installer is not so qualified, consider consulting with a lightning protection specialist before the system is installed.

    Get Grounded

    Class I Lightning arresters, Class II surge arresters and Class III surge protectors are designed to protect electronic equipment by absorbing electrical surges. However, these devices are not a substitute for good grounding. They function only in conjunction with effective grounding.

    Grounding is the most fundamental technique for protection against lightning and surge damage. You can’t stop a lightning surge, but you can give it a direct path to ground that bypasses your valuable equipment, and safely discharges the surge into the earth. An electrical path to ground will constantly discharge static electricity that accumulates in an aboveground structure. Often, this prevents the attraction of lightning in the first place.


    Step one in grounding is to construct a discharge path to ground by bonding (interconnecting) all the metal structural components and electrical enclosures, such as PV module frames, mounting racks, and wind generator towers. Avoid sharp bends in ground wires—high current surges don’t like to turn tight corners and can easily jump to nearby wiring. Pay special attention to attachments of copper wire to aluminum structural elements (particularly the PV module frames). Use connectors labeled “AL/CU” and stainless steel fasteners, which reduce the potential for corrosion. The ground wires of both DC and AC circuits will also be connected to this grounding system. (Refer to Code Corner articles on PV array grounding in HP102 and HP103 for more advice.)

    Ground Rods

    The weakest aspect of many installations is the connection to the earth itself, you must bury or hammer a rod of conductive, noncorrosive metal (generally copper) into the ground, and make sure most of its surface area contacts conductive (that means moist) soil. This way, when static electricity or a surge comes down the line, the electrons can drain into the ground with minimal resistance.


    In a similar way to how a drain field dissipates water, grounding acts to dissipate electrons. If a drainpipe doesn’t discharge adequately into the ground, backups occur. When electrons back up, they jump the gap (forming an electrical arc) to your power wiring, through your equipment, and only then to ground.
    To prevent what mentioned above, to install one or more 8-foot-long (2.4 m), 5/8-inch (16 mm) copper-plated ground rods, preferably in moist earth. A single rod is usually not sufficient, especially in dry ground. In areas where the ground gets extremely dry, install several rods, spacing them at least 6 feet (3 m) apart and connecting them together with bare copper wire, buried. An alternate approach is to bury #6 (13 mm2), double #8 (8 mm2), or larger bare copper wire in a trench at least 100 feet (30 m) long. (The bare copper ground wire also can be run along the bottom of a trench that carries water or sewer pipes, or other electrical wires.) Or, cut the ground wire in half and spread it in two directions. Connect one end of each buried wire to the grounding system.


    Try to route part of the system into wetter areas, like where a roof drains or where plants are to be watered. If there is steel well-casing nearby, you can use it as a ground rod (make a strong, bolted connection to the casing).


    In moist climates, the concrete footers of a ground- or pole-mounted array, or a wind generator tower, or ground rods encased in concrete will not provide ideal grounding. In these locations, concrete will typically be less conductive than the moist soil surrounding the footings. If this is the case, install a ground rod in earth next to the concrete at the base of an array, or at the base of your wind generator tower and at each guy wire anchor, then connect them all together with bare, buried wire.


    In dry or arid climates, the opposite is often true— concrete footings may have higher moisture content than the surrounding soil, and offer an economical opportunity for grounding. If 20-foot-long (or longer) rebar is to be embedded in concrete, the rebar itself can serve as a ground rod. (Note: This must be planned before the concrete is poured.) This method of grounding is common in dry locations, and is described in the NEC, Article 250.52 (A3), “Concrete-Encased Electrode.”


    Grounding Power Systems

    For building wiring, it requires one side of a DC power system to be connected—or “bonded”—to ground. The AC portion of such a system must also be grounded in the conventional manner of any grid-connected system. It is essential that the DC negative and the AC neutral are bonded to ground at only one point in their respective systems and both to the same point in the grounding system. This is done at the central power panel.


    Producers of some single-purpose, stand-alone systems (like solar water pumps and radio repeaters) recommend not grounding the power circuit. Refer to the manufacturer’s instructions for specific recommendations.

    Array Wiring & “Twisted Pair” Technique



    Array wiring should use minimum lengths of wire, tucked into the metal framework. Positive and negative wires should be of equal length, and be run together whenever possible. This will minimize induction of excessive voltage between the conductors. Metal conduit (grounded) also adds a layer of protection. Bury long outdoor wire runs instead of running them overhead. A wire run of 100 feet(30 m) or more is like an antenna—it will receive surges even from lightning in the clouds. Similar surges can still occur even if the wires are buried, but most installers agree that buried transmission wiring further limits the possibility of lightning damage.


    A simple strategy to reduce susceptibility to surges is the “twisted pair” technique, which helps equalize and cancel out any induced voltages between the two or more conductors. It can be difficult to find suitable power cable that is already twisted, so here’s what to do: Lay out a pair of power wires along the ground. Insert a stick between the wires, and twist them together. Every 30 feet (10 m), alternate the direction. (This is much easier than trying to twist the whole distance in one direction.) A power drill can sometimes be used to twist wiring as well, depending on the wire size. Just secure the ends of the wiring into the drill’s chuck and let the drill’s action twist the cables together. Make sure to run the drill at the lowest possible speed if you try this technique.
    The ground wire need not be twisted with the power wires. For burial runs, use bare copper wire; if you use conduit, run the ground wire outside the conduit. The additional earth contact will improve the grounding of the system.


    Use twisted-pair cable for any communication or control cables (for example, a float-switch cable for full-tank shutoff of a solar water pump). This smaller gauge wire is readily available in pre-twisted, multiple, or single pair cables. You also can purchase shielded twisted-pair cable, which has a metallic foil surrounding the twisted wires, and typically a separate, bare “drain” wire as well. Ground the cable shield and drain wire at one end only, to eliminate the possibility of creating a ground loop (less direct path to ground) in the wiring.
    Last edited by russ; 01-21-2011, 08:43 AM. Reason: removed links
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    To bad a lot of your information is incorrect and myth. CCE is the best GES there is and is why the military uses it for all its ammunition shelters. Do your research for Herbert Ufer.
    MSEE, PE

    Comment

    • russ
      Solar Fanatic
      • Jul 2009
      • 10360

      #3
      This fellow was using this for free advertising - until I removed all links.

      Should it be deleted as incorrect?

      Russ
      [SIGPIC][/SIGPIC]

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        Originally posted by russ
        This fellow was using this for free advertising - until I removed all links.

        Should it be deleted as incorrect?

        Russ
        It is not completely incorrect, just a lot of myths that do no harm but no good either. What set me off was his statement Concrete Encased Electrodes are not good enough in most climates. Well fact is CCE is the best ground electrode money can buy and is whey the NEC requires it to be used for any and all new construction.

        Herbert Ufre worked for DuPont back in WWII when the military was having static and lightning problems with Ammo Bunkers being built in the Arizona desert. Desert soils conditions are the toughest conditions to achieve conductance. Ufer designed a Concrete Encased Electrode by using the rebar on the concrete. The huge surface area and pernament moisture in contact with the earth is the lowest impedance anyone has ever obtained. Ufer was getting 2 to 10 ohms impedance at power frequencies with his system in the dessert.

        There are two names it goes by: Ufer Ground and Concrete Encased Electrode. NEC adopted the CEE which is a downscale version of the Ufer Ground and required to be used in all new construction if available. Commercial and industry have been using it since WWII
        MSEE, PE

        Comment

        • russ
          Solar Fanatic
          • Jul 2009
          • 10360

          #5
          Thanks Sunking!
          [SIGPIC][/SIGPIC]

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by chris2011
            Lightning and Surge Protection

            ......

            In moist climates, the concrete footers of a ground- or pole-mounted array, or a wind generator tower, or ground rods encased in concrete will not provide ideal grounding. In these locations, concrete will typically be less conductive than the moist soil surrounding the footings. If this is the case, install a ground rod in earth next to the concrete at the base of an array, or at the base of your wind generator tower and at each guy wire anchor, then connect them all together with bare, buried wire.


            In dry or arid climates, the opposite is often true— concrete footings may have higher moisture content than the surrounding soil, and offer an economical opportunity for grounding. If 20-foot-long (or longer) rebar is to be embedded in concrete, the rebar itself can serve as a ground rod. (Note: This must be planned before the concrete is poured.) This method of grounding is common in dry locations, and is described in the NEC, Article 250.52 (A3), “Concrete-Encased Electrode.”......
            I think this qualifies as a "FAIL" for our poster.

            Mike - with 6 UFER grounds on 3 slabs.
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #7
              Yeah Mike that is what set me off. Concrete is a huge sponge, alkaline, with massive surface area which makes it super conductive in moist soil conditions, and extremely effective in dry desert alkaline soils.
              MSEE, PE

              Comment

              • chris2011
                Junior Member
                • Jan 2011
                • 4

                #8
                Originally posted by Sunking
                It is not completely incorrect, just a lot of myths that do no harm but no good either. What set me off was his statement Concrete Encased Electrodes are not good enough in most climates. Well fact is CCE is the best ground electrode money can buy and is whey the NEC requires it to be used for any and all new construction.

                Herbert Ufre worked for DuPont back in WWII when the military was having static and lightning problems with Ammo Bunkers being built in the Arizona desert. Desert soils conditions are the toughest conditions to achieve conductance. Ufer designed a Concrete Encased Electrode by using the rebar on the concrete. The huge surface area and pernament moisture in contact with the earth is the lowest impedance anyone has ever obtained. Ufer was getting 2 to 10 ohms impedance at power frequencies with his system in the dessert.

                There are two names it goes by: Ufer Ground and Concrete Encased Electrode. NEC adopted the CEE which is a downscale version of the Ufer Ground and required to be used in all new construction if available. Commercial and industry have been using it since WWII

                Hi, Thank you for your comments. which mistake you found? it will be happy to discuss with you.

                Comment

                • totfcboatski
                  Solar Fanatic
                  • Sep 2011
                  • 181

                  #9
                  using my concrete deck footers as an earth ground?

                  I have 2 panels mounted on my deck.
                  Can I ground them together using the stainless fasteners to ties them together and then terminate them at the huge lag screw coming out of my
                  concrete footer/wood deck pillar?.ill this be adequate for an earth ground for my panel frames
                  thanks in advance for your patience with the newbie question!

                  Jeff

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Originally posted by totfcboatski
                    I have 2 panels mounted on my deck.
                    Can I ground them together using the stainless fasteners to ties them together and then terminate them at the huge lag screw coming out of my
                    concrete footer/wood deck pillar?.ill this be adequate for an earth ground for my panel frames
                    thanks in advance for your patience with the newbie question!

                    Jeff
                    Likely not. Unless you KNOW that the rebar in the footer (20' of 1/2" is the mininum) is present, and you can get a ground clamp on it, it's not a good ground.

                    Are you in a lightning prone area ?
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • totfcboatski
                      Solar Fanatic
                      • Sep 2011
                      • 181

                      #11
                      mike

                      MIke
                      I live in maine about 25 miles from the coast. We get lightning about a dozen times mostly during summer with a few odd storms in the fall or spring. Im in a pasture with about 100 feet from Nearest tree. Though lightning strikes are rare i have my panels (now only 2 but two more coming)
                      on my deck anchored to a metal terminal post so obviously i want to be agressive about my protection. NeC says i only need and earth ground for
                      my frames so my thinking then (not using the concrete footer)is to using the steel fasteners on the panel mounting and connect the two together and then 6 awg bare wire (solid or stranded??) to an earth ground. Correct? with a max of 4 12v/ 65 watt panels do you think i need to ground the
                      battery or any other equipment?. [I]m miy reading it sounds like i dont have to but will if its the prudent thing to do... thoughts??
                      thanks! this helps support my reading and affirm my undestanding. im not hooking anything up till i have a full understanding of whati need to protect0 my house
                      Jeff

                      Comment

                      • Mike90250
                        Moderator
                        • May 2009
                        • 16020

                        #12
                        Lightning cares not a bit, about the size of your system or the # of batteries. If you are in a L'ng prone area (and it sounds like it to me) you will need help to get it right, to NOT attract a strike into your house/deck/battery room.
                        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                        solar: http://tinyurl.com/LMR-Solar
                        gen: http://tinyurl.com/LMR-Lister

                        Comment

                        • totfcboatski
                          Solar Fanatic
                          • Sep 2011
                          • 181

                          #13
                          mike

                          Thanks
                          Im going to have a master eletrician consult with me. Just wanted to pick your brains and see how far off i am in my thinking. my panels will be earth grounded they run 12 feet to a midnite combiner box there I wil have midnite solar SPD and chassis ground then its a 8 foot run outside to the
                          entrance through the wall to my finished basement and the output conductors hit a blue sea battery switch (using as my pv diconnect) then my CC and then my three batteries on wich the positive terminal leading to the inverter has a blue sea terminal block. [I] also plan to use inline fuses before any after the CC. just would like your thoughts on my system as it pertains to safety.. am i on the right track or another misguided diyer im ok with any feedback you have just want to learn!
                          thanks!