I am installing a grid-tied ground-mounted 7500W PV system. The AHJ annotated my permit with a sticker that says: "RAPID SHUT DOWN AND LABEL REQUIRED PER ART. 690.12 AND 690.56(C)."
Everything that I can find about the requirements of 690.12 discuss roof-mount systems, PV-related circuits (and primarily DC wiring) within the house, and firefighter safety. My inverter will be at the ground-mount PV array, some 300+ feet of underground buried (AC) cable away from the house. The AC disconnect mounted at the house will serve to totally disconnect all solar PV system related supply immediately upon dropping that switch. While there will be about 10 feet of AC cable within the house associated with this system (i.e., between that exterior mounted and labeled AC disconnect and my load center panel in the basement), that can be isolated from the entire solar power supply by dropping the AC disconnect.
In my estimation, my remote-ground-mounted array/inverter and AC disconnect at the house meets the requirement of 690.12. I'm looking for others' thoughts on the matter before I call up the AHJ to discuss... I note that my county only adopted the 2014 NEC a few months ago, so I anticipate the plan reviewers and inspectors are learning the ins-and-outs of interpreting this new requirement, too.
Assuming I am correct, I am also a bit confused about the application of the labeling of 690.56(C) - "PHOTOVOLTAIC SYSTEM EQUIPPED WITH RAPID SHUTDOWN".... while the AC disconnect effectively has an immediate shutdown for the PV-related wiring inside the house to the panel, it isn't a "rapid shutdown" in the sense of the 690.12 requirement, and the inverter and equipment out at the array are still energized.... so do I put that sticker on the AC disconnect or not?
Everything that I can find about the requirements of 690.12 discuss roof-mount systems, PV-related circuits (and primarily DC wiring) within the house, and firefighter safety. My inverter will be at the ground-mount PV array, some 300+ feet of underground buried (AC) cable away from the house. The AC disconnect mounted at the house will serve to totally disconnect all solar PV system related supply immediately upon dropping that switch. While there will be about 10 feet of AC cable within the house associated with this system (i.e., between that exterior mounted and labeled AC disconnect and my load center panel in the basement), that can be isolated from the entire solar power supply by dropping the AC disconnect.
In my estimation, my remote-ground-mounted array/inverter and AC disconnect at the house meets the requirement of 690.12. I'm looking for others' thoughts on the matter before I call up the AHJ to discuss... I note that my county only adopted the 2014 NEC a few months ago, so I anticipate the plan reviewers and inspectors are learning the ins-and-outs of interpreting this new requirement, too.
Assuming I am correct, I am also a bit confused about the application of the labeling of 690.56(C) - "PHOTOVOLTAIC SYSTEM EQUIPPED WITH RAPID SHUTDOWN".... while the AC disconnect effectively has an immediate shutdown for the PV-related wiring inside the house to the panel, it isn't a "rapid shutdown" in the sense of the 690.12 requirement, and the inverter and equipment out at the array are still energized.... so do I put that sticker on the AC disconnect or not?