One thing that I think has not been addressed yet is that at least one circuit in the lower left portions of the panel, using dual breakers, may be a MultiWire Branch Circuit (MWBC) with a red wire, black wire, and possibly a common neutral. If all you do is move the half size breakers up one position to fill in the blank, then you would end up feeding the black and the red wire from the same L connection. This will double the maximum current on the shared neutral, causing as fire hazard and a code violation.
An electrician can tell you how to rearrange the half sized breakers to make sure that this does not happen.