In the past, our practice would be to size a panelboard's amps to only 1.25* the total maximum continuous current of the inverters. The panelboard gets treated as a "No Loads Panel", dedicated to the PV System, with a label on it saying not to add loads.
Now, the 2014 NEC 690.12 and 690.13, requires solutions which often imply auxiliary circuits for the PV system that consume power instead of produce power. Usually power supplies that operate contactors and AFCI circuitry in the combiners, or similar. This could also include revenue grade meter power supplies. This is negligible in current compared to the total inverters, but this is a load.
Is it acceptable to connect 160 operating Amperes of inverters (i.e. 200A total of OCPD) to a dedicated 200A panelboard with a 200A main breaker, and still have these small loads connected at 15A breaker(s)? The sum of breakers (excluding the main supply) will exceed the rating of the busbar. But only the inverter breakers will load the panel anywhere near its ampere rating.
Now, the 2014 NEC 690.12 and 690.13, requires solutions which often imply auxiliary circuits for the PV system that consume power instead of produce power. Usually power supplies that operate contactors and AFCI circuitry in the combiners, or similar. This could also include revenue grade meter power supplies. This is negligible in current compared to the total inverters, but this is a load.
Is it acceptable to connect 160 operating Amperes of inverters (i.e. 200A total of OCPD) to a dedicated 200A panelboard with a 200A main breaker, and still have these small loads connected at 15A breaker(s)? The sum of breakers (excluding the main supply) will exceed the rating of the busbar. But only the inverter breakers will load the panel anywhere near its ampere rating.