    Riso Low

    Dear friends,
    i have searched "riso low" in forum but it returned nothing.
    I guess it is impossible not to talk about "riso low" issue at this forum but i have to open a new therad anyway.
    The situation is , one of my inverter's (transformerless) DC input channel IGBTs are burned. I look at the plant's messages and i see this invertor has "riso low" messages.

    The question is how can i handle "riso low" issue? what is the inspection steps for insulation, which meters should i use?
    thanks!
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    bummer. The transformer - less inverters are pretty new, it should be covered by warranty I hope.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • PNjunction
      Solar Fanatic
      • Jul 2012
      • 2179

      #3
      A Fluke 1587 insulation meter might help pin point the problem on the system. The most obvious stuff to me would be to inspect the array for "frog-hairs", or other hurried construction techniques.

      I have never worked with one, so I can't really comment on it.

      Comment

      • inetdog
        Super Moderator
        • May 2012
        • 9909

        #4
        Just a guess that "riso low" is referring to a low isolation resistance, probably on the DC input side somewhere. That could be a ground in what should be an ungrounded panel array, or it could be the result of an internal failure in the inverter.
        Can you at least tell us whether this is a GTI, and give us manufacturer and model?
        SunnyBoy 3000 US, 18 BP Solar 175B panels.

        Comment

        • karagoncoloz
          Junior Member
          • Mar 2014
          • 11

          #5
          Seems to be Solved

          Dear friends,
          I did a lot of inspections, measurements of Voltage and current etc...
          I observed some big mistakes and solved them. But it still gives the same error less occasion.
          Then i find out that some underground DC cables are remains wet always.
          After some magic trick made on strings, all DC cables are rescued from underground.
          Now Inverter seems just fine...

          thank you!

          Comment

          • bcroe
            Solar Fanatic
            • Jan 2012
            • 5209

            #6
            Originally posted by karagoncoloz
            Dear friends,
            I did a lot of inspections, measurements of Voltage and current etc...
            I observed some big mistakes and solved them. But it still gives the same error less occasion.
            Then i find out that some underground DC cables are remains wet always.
            After some magic trick made on strings, all DC cables are rescued from underground.
            Now Inverter seems just fine... thank you!
            Glad you found the ground leakage. Here is how I test that. With some decent sun, the
            array is completely disconnected from the inverter. My 2 pole DC disconnect switch does
            that. This tester has enough bulbs in series, to about match the open circuit voltage of
            my array, some 450 volts. Connecting it to the 2 array wires, it should light drawing a
            fraction of an amp. Then connect it between a good ground (the inverter ground) and
            one array terminal; it should be completely dark. Then connect it between ground and
            the other array terminal, same thing. If there is any sign of power through the bulbs,
            you have a low resistance to ground somewhere. A DVDM can't do this alone, because
            it will read static charges. An analog meter could be used for very high resistance
            faults. Bruce Roe
            Attached Files

            Comment

            • karagoncoloz
              Junior Member
              • Mar 2014
              • 11

              #7
              Originally posted by bcroe
              Glad you found the ground leakage. Here is how I test that. With some decent sun, the
              array is completely disconnected from the inverter. My 2 pole DC disconnect switch does
              that. This tester has enough bulbs in series, to about match the open circuit voltage of
              my array, some 450 volts. Connecting it to the 2 array wires, it should light drawing a
              fraction of an amp. Then connect it between a good ground (the inverter ground) and
              one array terminal; it should be completely dark. Then connect it between ground and
              the other array terminal, same thing. If there is any sign of power through the bulbs,
              you have a low resistance to ground somewhere. A DVDM can't do this alone, because
              it will read static charges. An analog meter could be used for very high resistance
              faults. Bruce Roe
              Man, you rock!
              I read about this shape of measurement in an article or some panel producer application manual, but i did not understand what it says. now i got it.
              what a fool i am ))
              thank you!