First, thanks to the many postings that I have learned from. So much to learn and read. I just built a 3.84 kW (4024/CL150) 12-Panel (on 3 posts) Heliene Off-Grid Solar System on a 21' trailer. It has 8 400ah batteries (24v) and a backup Onan P9500DF generator. I wanted to take it with me should I leave this location. I tied it to the house with an "emergency power" breaker box. Most of the home runs from this panel. My equipment is from Backwoods Solar in Sandpoint, Idaho. I have also spent hours with the customer service folks at Midnite Solar. He helped me fine tune the classic 150 settings. My generator was not accepted by the system. The Conext SCP showed a limit of 60Hz. Noticed the generator was putting out 60.1Hz. So a minor adjustment (60.2 Hz) to the allowable tolerances and my generator now interfaces nicely.
I am currently trying to figure out how to install the Schneider AGS. The AGS offers 14 "type" generator settings. I have not yet located this information for my P9500DF. Well, I'm back to researching this issue. Advice always welcome. Thanks again for so much information.