    Originally posted by Ravi
    Sorry for misunderstanding, but no need to be so harsh.
    Sorry but I am not being harsh, just direct. Ask questions.

    Originally posted by Ravi
    Can I still use my 14 guage wire from each string (set of 4 in series tied by 14 guage wire) to bus bar, is that going to be a problem as far as power loss or do I need to change my wiring to a thicker wire going to my bus bar.
    Most certainly that was my point. With 4 panels in series your Vmp now goes up to 70 volts @ 7 amps. That will result in .88 volt drop or a 1.2% power loss. Target is 2% or less. !4 AWG meets the objective.

    Originally posted by Ravi
    Also, I will go with 24 volt battery setup where each connection is exactly the same length to equalize wire resistance so each battery is equally charged and discharged. (2-12 volt batteries in series and 8 such connections in parallel to a bus bar since I have 16 batteries total. I am using 0 guage stranded wire for all battery and battery to inverter connection) and an AIMS 4000W pure sine wave inverter (industrial grade since its surge is 12000W for 30 seconds.
    Have you bought the batteries yet? If not you really need different plan. Parallel batteries are a horrible plan full of regrets, countless hours of trouble shooting, premature battery failures, battery replacements, and will cause great pain in the wallet. You want one single string if possible and it is always possible. There is no reason for parallel batteries. You just gotta get out of that 12 volt box your mind is trapped in.

    It also appears you might be walking into another trap, an expensive one. There are limits to panel wattage, battery size, and inverter load sizes. Get them out of acceptable limits and you will have a failure, an expensive one. With 800 watts of panel power, MPPT Controller, your battery capacity is limited to 24 volts at 260 to 400 Amp Hours. That limits your inverter size to 800 to 1200 watts max.
    MSEE, PE

    Comment

    • Ravi
      Junior Member
      • Aug 2013
      • 16

      #17
      I have purchased 16 - 12 volt deep cycle batteries (105Am each) and can configure them anyway you suggest, 24 or 48 volts. It sounds like I ought to configure my 16 batteries as 4 strings of 48 volt batteries which would then be in parallel. I would like to start out small but be able to expand in the near future without wasting money and equipment. It also seems that I ought to go with a 48 volt inverter. Did I get that right?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #18
        Originally posted by Ravi
        I have purchased 16 - 12 volt deep cycle batteries (105Am each) and can configure them anyway you suggest, 24 or 48 volts. It sounds like I ought to configure my 16 batteries as 4 strings of 48 volt batteries which would then be in parallel. I would like to start out small but be able to expand in the near future without wasting money and equipment. It also seems that I ought to go with a 48 volt inverter. Did I get that right?
        Pretty close. Read about connecting parallel batteries at the smartguage site

        even with 48V, 4 parallel banks will be a bit of a problem.

        With all those interconnects, you should buy a hydraulic crimper in the +6 ton range,
        and make cables yourself. Will save a bunch of cash.

        And with 4 banks, you will need 4 fuses or breakers - one on each bank, before they combine to the inverter & charge source.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • Ravi
          Junior Member
          • Aug 2013
          • 16

          #19
          Thats the website where i got the idea of keeping all the battery cables to the same lengths. I was proposing going with Method 3 in which each battery (in my case of a 48 volt system, each battery set is made of 4 twelve volt batteries in series) is connected to a single point (1 point for positive and 1 point for negative) as shown in the picture.

          Since my batteries are 12 volt and not 48 volt batteries, I would connect them in sets of 4 in series. Then each series set would go to a common bus bar (1 bar for positive and 1 bar for negative) just like method 3 shows.

          I figured going with 48v battery system would allow me to add more panels in the future until I reach 3200w from the solar array going into charging the 48 volt battery system.

          I got a great deal on 12v 115ah deep cycle marine battiers ($105 each). Strangely enough, I work for an electric company and have access to a hydraulic crimper, so thats no problem. These guys here however work in Megawatts and their controllers and inverters are for power plants and huge city wide installations. So I have little help for my little startup installation for home except academic questions

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #20
            Originally posted by Ravi
            Thats the website where i got the idea of keeping all the battery cables to the same lengths. I was proposing going with Method 3 in which each battery (in my case of a 48 volt system, each battery set is made of 4 twelve volt batteries in series) is connected to a single point (1 point for positive and 1 point for negative) as shown in the picture.

            Since my batteries are 12 volt and not 48 volt batteries, I would connect them in sets of 4 in series. Then each series set would go to a common bus bar (1 bar for positive and 1 bar for negative) just like method 3 shows.

            I figured going with 48v battery system would allow me to add more panels in the future until I reach 3200w from the solar array going into charging the 48 volt battery system.

            I got a great deal on 12v 115ah deep cycle marine battiers ($105 each)
            Remember plan for the future. If you see going 48 volts, do it now. All it takes is a different inverter. Everything remains the same. It also cuts the parallel battery strings in half. That means less wire and connectors.

            Marine batteries are not really a deal, they are not deep cycle, they are hybird a cross between cranking and deep cycle and will only last about half as long as a deep cycle.
            MSEE, PE

            Comment

            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #21
              I am done here. Any more help from me cost money.
              MSEE, PE

              Comment

              • Ravi
                Junior Member
                • Aug 2013
                • 16

                #22
                Thank you all sooooo much for your input. I have taken all your advice and created a design that I am enclosing in PDF form. I have gone with 48v battery bank and 48v strings for PV and have the circuit breakers as you suggested. Does everything look ok now? I built in plenty of future expandability. I hope I did the math right.
                Attached Files

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #23
                  Breakers protect wires. If you use a 300A breaker, you need wire good for 300A. O wire is not enough for for 300A if I recall. Smaller breakers or larger wire.
                  Be sure its a DC rated breaker for 75VDC.

                  Charge controller. I have a morningstar MPPT60, and like it. But I like the Midnight Classic better, and it comes with meter built in. (MS sells the optional meter, it ships with a blank faceplate)

                  And PDF seemed to hard to read, but I have a 10 yr old laptop too.

                  Inverter, does it have a built in charger, so your generator can efficiently charge your batteries when the sun fails (clouds) ? I don't see any generator in the system
                  Last edited by Mike90250; 08-07-2013, 07:18 PM. Reason: typos, inverter?'s
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • Ravi
                    Junior Member
                    • Aug 2013
                    • 16

                    #24
                    I see I made a mistake in my drawing. Since the inverter can have a 14000W surge and my battery would be 48v (14000/48 = 292Amps DC); 292 amps/4 parallel strings of batteries = 72 amps per 48v battery set.
                    A 0 gauge wire is rated for upto 150A.

                    So I will use 150A breakers not the 300A breakers as shown to go between battery and bus bar for the batteries. This way up to 2 parallel strings can fail and I still have plenty of power coming from the batteries without any hazards.

                    I will also change the 0 guage wire from the battery bus bar to 300 amp breaker and to inverter with a A THHN 350 MCM wire since it is rated for upto 350 amps.

                    Also, the reason i went with the morningstar mppt60 is because i am a programmer familiar with modbus and can write my own monitoring app if I dont like the MSview app that I can use to monitor everything over the web or msview app.

                    Finally, no, there is no generator in the system because if there is not enough juice in the battery, the system will automatically switch over to grid power via my automatic transfer switches.

                    Aside from the breakers, any concerns?

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #25
                      Originally posted by Ravi
                      ...

                      Finally, no, there is no generator in the system because if there is not enough juice in the battery, the system will automatically switch over to grid power via my automatic transfer switches...

                      You have calculated out (haven't you) that the battery replacement cost from using all their cycles, is way more than grid cost. Have you considered grid as primary power, and the batteries as backup, and use a hybrid inverter to backfeed the grid and unwind the meter ? (if that's permitted in your area)
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • Ravi
                        Junior Member
                        • Aug 2013
                        • 16

                        #26
                        SolarSetup.pdfI am just starting out and from everything I read, I gathered that I needed the batteries and so I purchased them. Currently, my total cost is less than $6000 since I did all the work myself. I sized the number of batteries as follows:
                        I have 800w being produced from PV and typically 500 being used (I monitored using Killawatt device). This leaves me 300W going to battery. 300W * 5 hours (full sunlight -- I usually get 8 hours of full sun) = 1500wh to battery. I figured that this 1500Wh would be used at night when I have no solar and then get recharged in the day while I still have enough juice in the batteries.

                        16 batteries * 105ah per battery * 12 volt battery = 20160 Wh (fully discharged). I dont want the batteries to suffer so I planned on 10% daily discharge = 2016 watt hours being drawn from batteries (thus keeping the inverter going without shutting down due to low battery voltage). This along with routine de-sulfination (the MPPT controller has this built in) should make the batteries last 15-20 years (i am told). I also have a portable 12 volt desulfator that I can use if necessary to revive dead batteries. My return on ivestment should be about 7 years.

                        Going with the 16 batteries also provides me that surge of power when things like my refrigerator, microwave, sumb pump, furnace kick in.

                        If all goes well, I can forget the batteries in the future, change my inverter to grid tie (cant do that in my city yet) and continue onward.

                        I have enclosed the modified drawing of my system. I realize theoretical is not necessarily practical so i certainly expect my design to have flaws and welcome all input as I have no practical experience in this area. This is my first system and I am doing it for my home in southern illinois close to st.louis, missouri.
                        Attached Files

                        Comment

                        • Ravi
                          Junior Member
                          • Aug 2013
                          • 16

                          #27
                          I am just starting out and from everything I read, I gathered that I needed the batteries and so I purchased them. Currently, my total cost is less than $6000 since I did all the work myself. I sized the number of batteries as follows:
                          I have 800w being produced from PV and typically 500 being used (I monitored using Killawatt device). This leaves me 300W going to battery. 300W * 5 hours (full sunlight -- I usually get 8 hours of full sun) = 1500wh to battery. I figured that this 1500Wh would be used at night when I have no solar and then get recharged in the day while I still have enough juice in the batteries.

                          16 batteries * 105ah per battery * 12 volt battery = 20160 Wh (fully discharged). I dont want the batteries to suffer so I planned on 10% daily discharge = 2016 watt hours being drawn from batteries (thus keeping the inverter going without shutting down due to low battery voltage). This along with routine de-sulfination (the MPPT controller has this built in) should make the batteries last 15-20 years (i am told). I also have a portable 12 volt desulfator that I can use if necessary to revive dead batteries. My return on ivestment should be about 7 years.

                          Going with the 16 batteries also provides me that surge of power when things like my refrigerator, microwave, sumb pump, furnace kick in.

                          If all goes well, I can forget the batteries in the future, change my inverter to grid tie (cant do that in my city yet) and continue onward.

                          I have enclosed the modified drawing of my system. I realize theoretical is not necessarily practical so i certainly expect my design to have flaws and welcome all input as I have no practical experience in this area. This is my first system and I am doing it for my home in southern illinois close to st.louis, missouri.
                          Attached Files

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #28
                            Originally posted by Ravi
                            [ATTACH]3063[/ATTACH]I have 800w being produced from PV and typically 500 being used (I monitored using Killawatt device). This leaves me 300W going to battery. 300W * 5 hours (full sunlight -- I usually get 8 hours of full sun) = 1500wh to battery. I figured that this 1500Wh would be used at night when I have no solar and then get recharged in the day while I still have enough juice in the batteries.
                            Well it is going to fail. You have done about every thing wrong so far. One huge eror is you assume you have 5 sun hours. You do not have anything close to that especially if the panels only get 8 hours of direct light a day. Only in June/July does your area even get close to 5 sun hours and that is only if you have complete unobstructed veiw of the East West South horizon, perfect solar south orientation, and optimum tilt angle where sun falls on the panel surface from sun up to sun down. . Come November-December, January and February will be 2 hours and less.

                            Off grid battery systems are designed for worse case. Come winter when your sun hours fall to less than 2 hours (less than 1 in your case with obstructions) your batteries will be dead and you will be in the dark all winter needing to buy all new batteries next spring. That is when you will discover you need a lot more panel wattage and much larger batteries.

                            Right now you do not even know how many watt hours you need in a day or Sun Hours have.
                            MSEE, PE

                            Comment

                            • Wy_White_Wolf
                              Solar Fanatic
                              • Oct 2011
                              • 1179

                              #29
                              If your only using 500W why are you installing a 7000W inverter? Losses from the inverter are going to be more than your load.

                              WWW

                              Comment

                              • Ravi
                                Junior Member
                                • Aug 2013
                                • 16

                                #30
                                I am just trieng to plan for the future. I want to put more and more of my AC circuits on solar. I measured the current of all the circuits that I wish to slowly migrate and it came in at about 33 amps AC which gives me about 4000 watts. Some of the items are motors and have a huge surge.