I have no idea about where to find a pump that size. But just for an example of the size PV system you are talking, with VERY rough numbers, if 1HP = 750W x 40HP = 30,000W for 1 pump. You said pumps, but not how many, so I'll do again, very rough math for 1 pump running 1 hour. You can do the math out from there.
30,000W x 1 hour = 30,000 Wh / 5.34 sun hours / .67 efficiencies = 8385W of solar per hour one pump is running.
30,000Wh /.92 inverter efficiency x 1 day autonomy x 50% DoD /48V = 1359Ah 48V battery bank per one hour one pump running
I see a large generator in your future.
Recommendation on water pumping system
Collapse
X
-
Thanks for the replys. The water source is the water stream of a river in a place with an average insolation of 5.34 kWh/m^2/day. The connection to the Utility is not an option on this case basically because there is no grid connection nearby. The PV system is going to be definitely big, but I was thinking that maybe it has more sense to use as back up a diesel genset instead of a huge bank of batteries. Any ideas?
Unless you find a small DC pump that can run directly from a solar panel and controller you will need some type of battery system to keep the pump motor running consistently.
Once the batteries system is sized you can calculate your panel wattage size.
All solar/battery systems will require a genset of some kind. Either big enough to run the pump if the batteries fail or big enough to recharge the batteries if the sun don't come out for a couple of days.
I would also imagine the entire pump, solar array, battery and genset will require some type of security fencing to keep out the 2 and 4 legged critters.
IMO I would seriously look at the total cost to install the solar/battery/generator system and compare it to only a genset with a large fuel tank. Unless getting more fuel to the genset requires a helicopter the cost of installing and running it will be much less than the cost of installing and maintaining a solar/battery system.Leave a comment:
-
Thanks for the replys. The water source is the water stream of a river in a place with an average insolation of 5.34 kWh/m^2/day. The connection to the Utility is not an option on this case basically because there is no grid connection nearby. The PV system is going to be definitely big, but I was thinking that maybe it has more sense to use as back up a diesel genset instead of a huge bank of batteries. Any ideas?Leave a comment:
-
We need to know more like where he plans on installing the pump and why he doesn't want to go with a Utility connection for his power.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
40 HP pumps? Not going to happen with solar.
WWWLeave a comment:
-
What's the water source? is it a well that you need a submersible pump, or an open water supply like a pond or stream where you need a surface pump?Leave a comment:
-
Recommendation on water pumping system
Hi everyone,
The requirements for a water pumping system that is going to be powered entirely by solar energy is the use of 40 HP pumps to pump the water to around 300m with a flow rate of 36 liters/sec. Based on your experiences do you have any suggestions on good manufacturers where I can find pumps with the mentioned characteristics? There are no restrictions on the selection of AC or DC pumps.
Thanks for your support!
Leave a comment: