Hello all,
We put in a irrigation pump for our small farm. The pump works fine, we can run it with our 4000w generator without problems (no grid-tie at the farm).
However, today I finally got our inverter connected, and it kept coming up with an overload error and shutting down.
So, some details. The pump is a Sta-Rite DS3HF - 1.5 HP centrifugal above-ground pump. Our well is very shallow, there's water at about 6' down. So the pump has no problem pumping it, as noted above, with adequate pressure and terrific flow rates for our purposes. The pump manual says it has a maximum current of 20 amps at 120v, 10 amps at 240v. We've been running it off our generator using 120v.
Our PV system is a single 240w panel going into a Tracer MPPT charge controller (yes, I know it could be better). The controller is charging our 4 deep cycle batteries in parallel, so our system is 12v. The batteries are connected together with 2/0 AWG interconnects. The batteries themselves are Tractor Supply Stowaway marine batteries, rated at about 100 amp-hrs and 700 cranking amps each (yes, I know not the best brand).
The inverter is a Cobra 2500w inverter (probably the biggest problem). It's connected to the batteries using Cobra 4 AWG cables, two pairs at 5' long. I connected the cables at the two middle batteries, so not perfect, but should get close to optimal current draw from the batteries.
My test runs were using a not-good-enough extension cord, 50' 14 gauge rated for 15 amps (yes, I know that's a problem, but I doubt it's *the* problem). When we use the generator, we use a 12 gauge, 5' power cord.
The pump *started* to shoot out water but the inverter very quickly indicated a low voltage fault, then changed it to a current overload fault and shut down.
So, I suspect my problems are: 1) too much in-rush current to the pump, 2) trying to run the pump on 120v, 3) trying to run the pump on a too-small consumer-grade inverter, 4) too small cable from inverter to pump (though a safety issue, not part of this problem, really), and 5) maybe too big a current draw from the batteries.
Going from least to most, I'm a little surprised that the inverter first says low voltage. The inverter said the voltage was 13.6v coming from the batteries. Would putting a starting battery in the mix help with this problem?
I'm going to hard-wire the pump to the barn before I'm done, so the not-good-enough cord shouldn't be a long-term issue. Besides, shouldn't that have limited the current draw at the inverter a smidge?
Would some kind of soft-starter help with 1 and 3? I've looked into this, but I want to be able to software-control the starter, and haven't found (yet, only been looking an hour) a soft starter for 120v, 20amps full load, that's 24v controllable.
Which leaves the 120v issue. This pump is selectable to run at 240, and the generator can produce 240 too. I was hoping to stick with 120v for various reasons, including cheaper inverters. Should I give up on that idea?
Thanks for any suggestions!
We put in a irrigation pump for our small farm. The pump works fine, we can run it with our 4000w generator without problems (no grid-tie at the farm).
However, today I finally got our inverter connected, and it kept coming up with an overload error and shutting down.
So, some details. The pump is a Sta-Rite DS3HF - 1.5 HP centrifugal above-ground pump. Our well is very shallow, there's water at about 6' down. So the pump has no problem pumping it, as noted above, with adequate pressure and terrific flow rates for our purposes. The pump manual says it has a maximum current of 20 amps at 120v, 10 amps at 240v. We've been running it off our generator using 120v.
Our PV system is a single 240w panel going into a Tracer MPPT charge controller (yes, I know it could be better). The controller is charging our 4 deep cycle batteries in parallel, so our system is 12v. The batteries are connected together with 2/0 AWG interconnects. The batteries themselves are Tractor Supply Stowaway marine batteries, rated at about 100 amp-hrs and 700 cranking amps each (yes, I know not the best brand).
The inverter is a Cobra 2500w inverter (probably the biggest problem). It's connected to the batteries using Cobra 4 AWG cables, two pairs at 5' long. I connected the cables at the two middle batteries, so not perfect, but should get close to optimal current draw from the batteries.
My test runs were using a not-good-enough extension cord, 50' 14 gauge rated for 15 amps (yes, I know that's a problem, but I doubt it's *the* problem). When we use the generator, we use a 12 gauge, 5' power cord.
The pump *started* to shoot out water but the inverter very quickly indicated a low voltage fault, then changed it to a current overload fault and shut down.
So, I suspect my problems are: 1) too much in-rush current to the pump, 2) trying to run the pump on 120v, 3) trying to run the pump on a too-small consumer-grade inverter, 4) too small cable from inverter to pump (though a safety issue, not part of this problem, really), and 5) maybe too big a current draw from the batteries.
Going from least to most, I'm a little surprised that the inverter first says low voltage. The inverter said the voltage was 13.6v coming from the batteries. Would putting a starting battery in the mix help with this problem?
I'm going to hard-wire the pump to the barn before I'm done, so the not-good-enough cord shouldn't be a long-term issue. Besides, shouldn't that have limited the current draw at the inverter a smidge?
Would some kind of soft-starter help with 1 and 3? I've looked into this, but I want to be able to software-control the starter, and haven't found (yet, only been looking an hour) a soft starter for 120v, 20amps full load, that's 24v controllable.
Which leaves the 120v issue. This pump is selectable to run at 240, and the generator can produce 240 too. I was hoping to stick with 120v for various reasons, including cheaper inverters. Should I give up on that idea?
Thanks for any suggestions!