yesterday, my pump would not stay running, the Motor Protector circuit kept shutting it off after 20 seconds. I tried cleaning the filter, and running the outlet into a bucket, minimal backpressure, and it would still shut off. I really did not like the idea of having to repair a bum system in the rain, Rain. Clouds. Generator. Pump always worked on the other 3Kw generator (1930's gear) But the new generator - won't run the pump. Something about the PF of the pump, and the lightweight rotor of the alternator. The Subaru/Hatz diesel genset is rated 3.3Kw peak, 3Kw cont. But it's so lightweight (my old alternator weighs more than the new genset) I seldom run it at more than 2.5Kw charging batteries,
Goes to show that sometimes small is too small. With no other loads or battery charging going on, I can barely run a 1/2 hp pump off a 3Kw genset. What a pain that Power Factor can be. I guess the motor protector circuit did not like something in the power quality and shut the pump down.