wats, volts, ah, kwh OH MY ... chest freezer off grid questions

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • mrsray
    Junior Member
    • May 2015
    • 2

    #1

    wats, volts, ah, kwh OH MY ... chest freezer off grid questions

    I understand off-grid freezers are not cheap. With that being said, I have a ...

    Frigidaire
    5 Cubic Foot Capacity - FFC05C3CW
    115volt, 60 Hz., AC. 15 amp grounded outlet is required.
    *Wattage Range (Last 1⁄3 of cycle) 70-85


    Would like to solar power off grid

    I am totally confused about the electrical specs of all devices and how they need to work together

    new and stupid, please be gentle with me for your answers

    so far I have

    I have two Solar Panel PV 12V Poly 100 Watts
    and two deep cycle batteries 200 ah (which I know I should never drain more than 50%)
    plus 30A MPPT Solar Panel Regulator Charge Controller 12V/24V Auto Switch
    and a Battery Tender Plus - fully automatic and Microprocessor controlled 12-Volt 1.25-Amp battery charger


    I have lots of various UPS's laying around that I was hoping to do a UPS to Inverter Conversion
    need to know what UPS size would be best and ...

    what more would I need

    also what would be best for:
    a fuse or breaker between the inverter and the battery bank.


    thanks in advance
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Welcome.
    Most UPS's are for computers, and produce a mod-sine output, which is NOT good for motors. They cause motors to run about 20% hotter, and in a freezer (or fridge) that's extra heat it has to dump, making longer run times. You really want a pure sinewave inverter.
    For starting the motor, you need about 5x the running amps, sometimes even more. You can guess at it, or hire an electrician to bring his $350 peak hold AC amp meter and measure the start up current. Or you buy the meter yourself.
    Your inverter has to be large enough to provide this starting surge, and the batteries and cables need to not choke up the power.
    Most 500w inverters are just a tad too small to power the starting surge.

    Then use a $25 Kill-a-Watt meter to measure the running amps, and daily watt hour totals and that lets you size the battery bank you need.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • mrsray
      Junior Member
      • May 2015
      • 2

      #3
      all of my ups's are pure sinewave, it's all i buy
      for example one of them is
      CyberPower PP1100SW Smart App Sinewave UPS - 1100VA/700W AVR 7-Out Tower SNMP/HTTP
      Blogger is a blog publishing tool from Google for easily sharing your thoughts with the world. Blogger makes it simple to post text, photos and video onto your personal or team blog.


      and the rest of your post, you lost me on, sorry

      you need about 5x the running amps, sometimes even more. ... I have a Compact Digital Multimeter w/ Audible Continuity
      Multimeter Model: 421 ... can I use that to accurately measure the start up current

      Most 500w inverters are just a tad too small to power the starting surge. ... but something like my 700w pure sinewave ups might work, no?

      and what about a fuse or breaker between the inverter and the battery bank.

      thanks for your reply ... any other thoughts and tips?

      Comment

      • Bala
        Solar Fanatic
        • Dec 2010
        • 734

        #4
        Originally posted by mrsray
        all of my ups's are pure sinewave, it's all i buy
        for example one of them is
        CyberPower PP1100SW Smart App Sinewave UPS - 1100VA/700W AVR 7-Out Tower SNMP/HTTP
        Blogger is a blog publishing tool from Google for easily sharing your thoughts with the world. Blogger makes it simple to post text, photos and video onto your personal or team blog.


        and the rest of your post, you lost me on, sorry

        you need about 5x the running amps, sometimes even more. ... I have a Compact Digital Multimeter w/ Audible Continuity
        Multimeter Model: 421 ... can I use that to accurately measure the start up current

        Most 500w inverters are just a tad too small to power the starting surge. ... but something like my 700w pure sinewave ups might work, no?

        and what about a fuse or breaker between the inverter and the battery bank.

        thanks for your reply ... any other thoughts and tips?
        Unless your multimeter has an A/C amps setting then you wont be able to use it.

        I have a 7.5 cubic ft freezer, fairly late model so reasonable comparison for yours, and I have had a watt meter on it today.

        its rated current on its name plate is .3A and by the meter it is running at 73w after start up, so that works out.

        My system is 24V over 1000ah battery and 3000w quality inverter.

        The start up current by the meter is 1272w.

        Comment

        • Bucho
          Solar Fanatic
          • Dec 2013
          • 167

          #5
          Originally posted by mrsray
          I have two Solar Panel PV 12V Poly 100 Watts
          and two deep cycle batteries 200 ah (which I know I should never drain more than 50%)
          plus 30A MPPT Solar Panel Regulator Charge Controller 12V/24V Auto Switch
          and a Battery Tender Plus - fully automatic and Microprocessor controlled 12-Volt 1.25-Amp battery charger
          What deep cycle batteries are you using?

          Comment

          • Bucho
            Solar Fanatic
            • Dec 2013
            • 167

            #6
            Originally posted by Bala
            4RP1800
            Um that's a 4volt 1800AH battery....

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15151

              #7
              Originally posted by Bucho
              Um that's a 4volt 1800AH battery....
              Bucho

              Don't get the battery data from Bala mixed up with the data from the OP mrsray.

              mrsray

              What is the voltage of those 2 x 200Ah batteries and how do you plan on converting that UPS to only be used as an inverter and not try to charge those batteries?

              Comment

              • Bala
                Solar Fanatic
                • Dec 2010
                • 734

                #8
                Originally posted by SunEagle
                Bucho

                Don't get the battery data from Bala mixed up with the data from the OP mrsray.

                mrsray

                What is the voltage of those 2 x 200Ah batteries and how do you plan on converting that UPS to only be used as an inverter and not try to charge those batteries?
                Sorry I made the mistake of thinking that Question was directed at me, I will delete my responses.

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15151

                  #9
                  Originally posted by Bala
                  Sorry I made the mistake of thinking that Question was directed at me, I will delete my responses.
                  No problem. I was interested in your battery system and was happy you provided those details.

                  I just didn't want Bucho to get confused which is real easy when you get a lot of input from people.

                  Comment

                  • Bucho
                    Solar Fanatic
                    • Dec 2013
                    • 167

                    #10
                    Originally posted by SunEagle
                    Bucho

                    Don't get the battery data from Bala mixed up with the data from the OP mrsray.
                    Thanks, I was completely doing that.

                    Comment