Sorry how large of a project are we talking about? Unless this is a commercial or industrial sized project I seriously doubt any firm will even bother to respond. I own and operate a A/E design firm which does Solar Battery systems, I would not touch a single one-time customer smaller than say 50 Kwh/day. Anything smaller I just cannot make any money on. I site visit would blow all the profit. Now if you have multiple projects that is another story. Typical fees is T&E plus 15%MSEE, PEComment
-
Sorry how large of a project are we talking about? Unless this is a commercial or industrial sized project I seriously doubt any firm will even bother to respond. I own and operate a A/E design firm which does Solar Battery systems, I would not touch a single one-time customer smaller than say 50 Kwh/day. Anything smaller I just cannot make any money on. I site visit would blow all the profit. Now if you have multiple projects that is another story. Typical fees is T&E plus 15%
Electrical System
1) Primary Distribution
Incoming power Voltage: 110 KV, 3ph. 50Hz
Grounding: Resistor, 200A, 10 sec.
2) Secondary Distribution
Supply Voltage at Pumping Station PS1 & PS2
Nominal Voltage: 6.9 KV, 3ph., 50Hz
Operating Voltage: 6.6 KV, 3ph., 50Hz
Short Circuit: 41KA
Grounding: Resistor, 200A, 10 sec.
3) Secondary Distribution
Supply Voltage at holding Pond E-CL
Nominal Voltage: 4.16 KV, 3ph., 50Hz
Operating Voltage: 4.0 KV, 3ph., 50Hz
Short Circuit: 41KA
Grounding: Resistor, 200A, 10 sec.
4 Low Voltage Power Distribution at all stations
Nominal Voltage: 400 V, 3ph., 50Hz
Operating Voltage: 380 V, 3ph., 50Hz
Short Circuit: 61KA
Grounding: Solidly grounded
5 Low Voltage Auxiliary Distribution at all stations
Nominal Voltage: 220 V, 1ph + N, 50Hz
Control Voltage: 120 V, 1ph., 50Hz
Protection & service Voltage 125 VDC
Short Circuit: 25KA
Grounding: Solidly grounded
6 Low Voltage Instrumentation Distribution at all stations
Control Voltage: 120 V, 1ph., 50Hz
Short Circuit: 25KA
Grounding: Solidly grounded
General requirements
The E-Houses for the Pumping Station & The retention Pond shall be welded exterior walls. For outdoor installation in process are as PS1 in particular shall be protected against sea corrosive environment this will include the HVAC system, the Pressurization unit and the Air filters etc.
The E-Houses shall be fabricated from new and of the highest quality materials available on the Market. Al materials shall be inspected before being installed to ensure that they not damaged and are free of defects.
The equipments and materials used in the E-Houses shall be as per the established standards and of first quality approved by Sierra Gorda S.C.M.
The Following characteristics of the structures are to be met.
a) all the fabricated elements need to have 60 min Fire resistance (F60) as required per ASTM E119-10b Standard Test Methods for fire Test of Building Construction and Materials.
b) The equipment layout shall be functional, safe and ergonomic in its concept, for the safety of the equipment and the personnel in all its parts. All equipment shall be easily accessible to facilitate ease of maintenance and repair of all components.
c) The supplier shall verify and adjust the dimension of the E-Houses shown in the provided layouts according to the equipment chosen and ensure that adequate space is provided for a safe operation.
d) The E-Houses shall be manufactured with interlocked panels and with added members to mount the equipment on the walls as required and shown in the data sheets.
The manufacturer shall submit all documentation for review of the design conformance.
a) Structural design Calculations
b) Seismic design calculation for installation on piers
c) Thermal calculations
d) Fire suppression calculations
e) HVAC calculation for the Air condition and the Pressurization
f) Lighting calculation
g) Programming & Parameterization Details for the protection relays
Equipments to be included and installed in the Proposal for the E Houses
Estacion de Captacion Costa
a) MV SWG’R
b) LV MCC
c) LV Panel boards (Power, Lighting instrumentation & Control)
d) Batteries Systems c/w Battery Chargers
e) Dry type Lighting Transformers
f) Fire Alarm and Fire extinguishing system (FM200)
g) Lighting system incl. Emergency lighting
h) Air Conditioning
i) Air pressurization
j) Power Receptacles installed & prewired
k) Terminal blocks and relays
l) All internal interconnection cables prewired & installed in the E Houses
m) External Ladders and platforms
n) Internal electrical raceways ( Cable Trays, conduits, & straps)
o) All Warning and safety instructions and rescue to help avoid accidents to electrical personnel
p) All work included
All other equipment required per attached documentation not listed above. All equipment installed in the E house need to be interconnected, wired in provided raceways.
Pumping Stations PS1 & PS2
a) MV SWG’R
a. LV MCC
b. LV Panel boards (Power, Lighting instrumentation & Control)
c. Batteries Systems c/w Battery Chargers
d. Dry type Lighting Transformers
e. Fire Alarm and Fire extinguishing system (FM200)
f. Lighting system incl. Emergency lighting
g. Air Conditioning
h. Air pressurization
i. Power Receptacles installed & prewired
j. Terminal blocks and relays
k. All internal interconnection cables prewired & installed in the E Houses
l. External Ladders and platforms
m. Internal electrical raceways ( Cable Trays, conduits, & straps)
n. All Warning and safety instructions and rescue to help avoid accidents to electrical personnel
o. All work included
All other equipment required per attached documentation not listed above. All equipment installed in the E house need to be interconnected, wired in provided raceways.
Estation Repetidora ER
a. LV Panel boards (Power, Lighting instrumentation & Control)
b. Power Panel Solar Panels
c. Batteries Systems c/w Battery Chargers Solar system
d. Fire Alarm Panel
e. Lighting system incl. Emergency lighting
f. Fans
g. Air pressurization
h. Power Receptacles installed & prewired
i. Terminal blocks and relays
j. All internal interconnection cables prewired & installed in the E Houses
k. External Ladders and platforms
l. Internal electrical raceways ( Cable Trays, conduits, & straps)
All other equipment required per attached documentation not listed above. All equipment installed in the E house need to be interconnected, wired in provided raceways.
Space provision for Customer supplied Equipment
1) Pump Lubrication Center for horizontal pumps (PS1 & PS2)
2) PLC Panels
3) Communication Panel
The final dimensions of the above mentioned equipments have to be verified with the suppliers and with the customer before the installation of these Equipments can take place.
The interconnections and the cabling of these equipment shall be part of this proposal and all interfaces required for the communication with the HV Scada system.
The programming, the Parameterization and the testing of the protection relays shall be included. The Customer will perform the coordination study and the values will be entered by the customer.
Design loading
The structure shall be designed for the transportation and installation and the seismic stresses subjected to the supporting members of the E-Houses according to the Nch 2369 of 2003.
The wind load is 148 Km/h . as given in the Site conditions
The Roof shall be designed to support 300Kg /square meter as a minimum
The base shall be designed to support a distributed load of 3000Kg /square meter as a minimum in addition to the weight of the house.
The E-Houses will be installed on reinforced concrete piers as indicated in the Data sheets.
The Walls and the Roof of the E-Houses shall conform to the spec’s No MQCL-ST52-IND-6600-ESP-CV00-0006 “Especificacion Technica Estructura Metalicas”
The exterior/interior walls and the ceiling of the E-House shall be fabricated with interlocked galvanized steel panels, 1.9mm thickness minimum welded contnously in the corners together with is structural pattern. The roof cover shall be sheet metal zincalum coated type N10 of 0.6 mm min. with c profile ribs of high inertia to achieve the rigidity required.
The Roof will have one or two slopes 5 degrees min. to allow drainage during rain periods
The snow loads for the Roof shall be taken into the design the standard Nch 431 and to include a reduction due to the slope of the roof.
The average distance between the roof cover and the ceiling shall be 200mm to allow air circulation to impede the solar radiation from heating up the e-house interior.
The roof of the e-house shall have thermal insulation to minimize the AC requirements
All the seams shall be waterproofed with a marine type sealant.
Structure
The Structure of the E-Houses shall conform to the spec’s No MQCL-ST52-IND-6600-ESP-CV00-0006 “Especificacion Technica Estructura Metalicas”
The Main structure of the E-house is composed of a base fabricated with structural steel profiles welded into a chassis capable of supporting its own structure and the equipments installed in the E-house.
The secondary structures shall be adequate and accurately coordinated and conform to the requirements and to allow easy installation with adequate openings of all the equipments for opening inspection and the installation of raceways as required.
The supplier shall design the E-house base with provision to anchor the base frame to the Concrete piers. The anchoring bolts and the required area on the foundation piers shall be provided by the supplier in schematic diagrams.
The main Structural members shall be H or I beams of adequate dimension and of adequate stiffness to allow a floor loading of 3000kg per square meter. If a larger loading to remove some equipment is required the supplier shall revise its structural calculations and reinforce the area locally.
A minimum of four (4) lifting lugs shall be part of the E-house base for erection use and maintenance these will be calculated and designed by the supplier.
Thermal insulation and acoustic absorption
The thermal insulation type polyurethane shall be applied on the inside of the walls & roof to have R11 insulation value unless the ambient conditions require otherwise.
The under side of the floor shall be coated for weather proofing.
The final design of the thermal insulation shall take into consideration a pressurization and air condition systems as indicated in point 8.11.Comment
-
Wished I had a license for GA
Let me do some checking with my peers and see if I can come up with some names for you. I take it you are an Engineer or Project Manager in charge of the project with signature authority? You do understand there is no equipment made to do what you want and the system components will all be custom made to fit the application. One thing I do not see and might of missed it is a minimum daily power requirements. I see the interconnect requirements, but no Mwh/day requirement to be met. I also do not see any generator requirement. To be honest with you I do not know of any company that has ever attempted to design such a system and do not know if it is even remotely possible. Now that I think about it there is only two design firms I know of that can tackle this if it can be done at all; Bechtel or Babcock & Wilcox.MSEE, PEComment
-
Over the Top
I know this is a ridiculous amount of information. We are a renewable energy company that specializes in medium size commercial and utility scale projects. Our sales team, has been receiving, RFP's for a fair amount of battery based systems. I would like to be able to have a reliable company to refer these customers to. Our website is U-renew.com. if you would like to research our company, and consider speaking? We may be able to become more clear on what we are looking for in a working relationship and it may create value for both parties involved.
Thank you,
Neal Erickson
Installation Manager
United Renewable EnergyComment
-
Wished I had a license for GA
Let me do some checking with my peers and see if I can come up with some names for you. I take it you are an Engineer or Project Manager in charge of the project with signature authority? You do understand there is no equipment made to do what you want and the system components will all be custom made to fit the application. One thing I do not see and might of missed it is a minimum daily power requirements. I see the interconnect requirements, but no Mwh/day requirement to be met. I also do not see any generator requirement. To be honest with you I do not know of any company that has ever attempted to design such a system and do not know if it is even remotely possible. Now that I think about it there is only two design firms I know of that can tackle this if it can be done at all; Bechtel or Babcock & Wilcox.
So Dereck how's your Spanish these days.
these sound a lot like shipping container type structures to house the batteries and related equipment.Last edited by Naptown; 09-06-2012, 10:48 PM.NABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-
Not bad. Enough I can start a fight in any bar, or order off a menu in any restaurant.
Honestly though I can speak a little as that comes from living in TX, but I am also taking the Rosetta Stone course for Spanish right now in anticipation of moving to Panama or Costa Rica early next year. Panama is no problem as English is the countries language along with the USD.
Costa Rica is another story. In the main cities most speak English or some English but outside that mostly Spanish. But most of the young population there does speak English as it is a required subject matter in their school system. Lot of large US companies there and many more moving there in the near future.MSEE, PEComment