    4kw new off grid system

    Hi everyone,

    I have just installed 16x 250w panels, total of 4kw

    1x Outback Flexmax 80 amp CC

    12x 230ah 12v batteries wired in parallel, total 2760 amp @ 12v

    1x 3000w inverter @ 12v

    Fow now I am forced to use the system at 12v because I only have the 12v inverter, but I plan on getting the 48v inverter to benefit from all 16 panels which can all be handled by the CC @ 48v (CC max watts at 48v is 6000w acording to the manual and max 1250w @12v)


    CC max voc is 150v, each panel has a 37v voc and 30v vmp......now I use 6 panels in parallel to get the max 80 amps at peak (with 5 panels in parallel I only get 70-72 amps at peak)

    my question with the 12v system I use now: can I wire more than 6 panels in parallel to get the 80 amps even in early mornings and late afternoons? ..voc and vmp will remain unchanged.


    thanks.
    Off-grid 4kw | Outback 80A MPPT | Victron 48v/5kw
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    Originally posted by Ionelissy
    12x 230ah 12v batteries wired in parallel, total 2760 amp @ 12v
    That was a huge mistake that will cost you dearly in about a year when you end up replacing the batteries. When that time comes buy yourself some 4 or 6 volt batteries @ 800 AH.
    MSEE, PE

    Comment

    • Ionelissy
      Member
      • Nov 2011
      • 63

      #3
      Originally posted by Sunking
      That was a huge mistake that will cost you dearly in about a year when you end up replacing the batteries. When that time comes buy yourself some 4 or 6 volt batteries @ 800 AH.
      thanks for that, I will get the 48v inverter in a month ....

      how about answering my question?
      Off-grid 4kw | Outback 80A MPPT | Victron 48v/5kw

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        If I remember correct the max power input for the FM 80 operating @ 12 volts is 1200 watts or 1250 watts. Check the manual.

        But you might have a huge problem on your hands. With 5 panels only leaves you the option of wiring them only in parallel which means the Imp panel current is up around 45 amps. What size wire is used from the panels to controller, and what gauge is it? Minimum required is # 8 AWG but if the 1-way distance is more than 5 feet would mean significant losses and would explain why you are not getting the current you are expecting.

        You might try the panels in a 2 x 3 config to get the current down to 22 amps and cut the losses 50%. But again I cannot tell if what you have is adequate or not by not knowing the gauge and distance.
        MSEE, PE

        Comment

        • inetdog
          Super Moderator
          • May 2012
          • 9909

          #5
          Originally posted by Sunking
          If I remember correct the max power input for the FM 80 operating @ 12 volts is 1200 watts or 1250 watts. Check the manual.

          But you might have a huge problem on your hands. With 5 panels only leaves you the option of wiring them only in parallel which means the Imp panel current is up around 45 amps. What size wire is used from the panels to controller, and what gauge is it? Minimum required is # 8 AWG but if the 1-way distance is more than 5 feet would mean significant losses and would explain why you are not getting the current you are expecting.

          You might try the panels in a 2 x 3 config to get the current down to 22 amps and cut the losses 50%. But again I cannot tell if what you have is adequate or not by not knowing the gauge and distance.
          The reason this depends on your CC is that some CCs will limit the amount of input power they take from the panels and so can be used with oversized panel arrays. This lets them use the full output from the panels during off-peak sun hours but will not try to accept more than their input rating during peak hours when the panels will potentially generate power above the CCs input limit. Other CCs expect the panel maximum output to be kept below their input power limit. The design limits on the CCs ability to tolerate overpowered solar arrays varies from manufacturer to manufacturer and model to model.
          They all, however, set a maximum voltage limit which has to be respected on cold as well as hot days. This puts a limit on how many panels you can put in series.
          SunnyBoy 3000 US, 18 BP Solar 175B panels.

          Comment

          • Ionelissy
            Member
            • Nov 2011
            • 63

            #6
            Originally posted by Sunking
            If I remember correct the max power input for the FM 80 operating @ 12 volts is 1200 watts or 1250 watts. Check the manual.

            But you might have a huge problem on your hands. With 5 panels only leaves you the option of wiring them only in parallel which means the Imp panel current is up around 45 amps. What size wire is used from the panels to controller, and what gauge is it? Minimum required is # 8 AWG but if the 1-way distance is more than 5 feet would mean significant losses and would explain why you are not getting the current you are expecting.

            You might try the panels in a 2 x 3 config to get the current down to 22 amps and cut the losses 50%. But again I cannot tell if what you have is adequate or not by not knowing the gauge and distance.
            I have 10 meters distance from the panels to the CC and solar cable size is 16 sq.mm which supports 4-10kw.

            thanks.
            Off-grid 4kw | Outback 80A MPPT | Victron 48v/5kw

            Comment

            • Ionelissy
              Member
              • Nov 2011
              • 63

              #7
              Originally posted by inetdog
              The reason this depends on your CC is that some CCs will limit the amount of input power they take from the panels and so can be used with oversized panel arrays. This lets them use the full output from the panels during off-peak sun hours but will not try to accept more than their input rating during peak hours when the panels will potentially generate power above the CCs input limit. Other CCs expect the panel maximum output to be kept below their input power limit. The design limits on the CCs ability to tolerate overpowered solar arrays varies from manufacturer to manufacturer and model to model.
              They all, however, set a maximum voltage limit which has to be respected on cold as well as hot days. This puts a limit on how many panels you can put in series.

              I tried 8 panels in parallel and of course voc and vmp stays the same even if I connect all 16 panels in parallel.... the CC does not have to limit anything, because wiring in parallel does not increase vmp and voc, it increases only watts.... which is what I need for off-peak hours, the only limit CC does it the output amps to 80.

              thanks.
              Off-grid 4kw | Outback 80A MPPT | Victron 48v/5kw

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                No matter how many more panels you add, you are limited to 80amps. If you stay at 12V, no need to add more panels. When you re-wire to a 48V battery bank, then you can add up to 4,000 watts of panels.

                Your battery strings should be wired on the diagonal, like this article describes
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by Ionelissy
                  I have 10 meters distance from the panels to the CC and solar cable size is 16 sq.mm
                  Right there is your problem. You are taking a 7% voltage loss when you need to be at 2% or less. You can cut your losses by 75% by reconfiguring your panels 2 x 3. That will bring the loss down to 1.5%
                  MSEE, PE

                  Comment

                  • Ionelissy
                    Member
                    • Nov 2011
                    • 63

                    #10
                    finally got my 48v inverter... set all my batteries @ 48v and now I have a 690ah battery bank charged by the 80 amp mppt Outback controller ...from the 4kw of LG solar panels.

                    So far, got a max of 3055w/55amps charging at peak... but measuring the sun I got only 807w/mp ... so everything is OK!


                    thank you all.
                    Off-grid 4kw | Outback 80A MPPT | Victron 48v/5kw

                    Comment

                    • sk_gc
                      Junior Member
                      • Sep 2012
                      • 3

                      #11
                      96v instead of 48v on array side?

                      Glad that you got it right.

                      Just speculating;

                      Why not 96v on array side and 48v on battery side? that you are using MPPT 80 amps CC.

                      Requesting experts here to suggest.

                      Comment

                      • Ionelissy
                        Member
                        • Nov 2011
                        • 63

                        #12
                        Originally posted by sk_gc
                        Glad that you got it right.

                        Just speculating;

                        Why not 96v on array side and 48v on battery side? that you are using MPPT 80 amps CC.

                        Requesting experts here to suggest.

                        I actually have the array set in series of 4 panels, giving me a total of 120 volts.
                        Off-grid 4kw | Outback 80A MPPT | Victron 48v/5kw