Hi everyone,
I have just installed 16x 250w panels, total of 4kw
1x Outback Flexmax 80 amp CC
12x 230ah 12v batteries wired in parallel, total 2760 amp @ 12v
1x 3000w inverter @ 12v
Fow now I am forced to use the system at 12v because I only have the 12v inverter, but I plan on getting the 48v inverter to benefit from all 16 panels which can all be handled by the CC @ 48v (CC max watts at 48v is 6000w acording to the manual and max 1250w @12v)
CC max voc is 150v, each panel has a 37v voc and 30v vmp......now I use 6 panels in parallel to get the max 80 amps at peak (with 5 panels in parallel I only get 70-72 amps at peak)
my question with the 12v system I use now: can I wire more than 6 panels in parallel to get the 80 amps even in early mornings and late afternoons? ..voc and vmp will remain unchanged.
thanks.