Well yes and no. Problem is 4-stage solar charge controllers cannot really be used. You paid for something that cannot be used effectively. The 4th stage is Equalize which is a controlled overcharge which takes up to 24 hours. Try to find a place on earth with a 24 Sun Hour day. Only way to EQ a battery is with a AC powered battery charger running on either commercial AC power or generator.
OK to answer your question I have to make some caveats here because sure enough some of you will run off and try this without all the facts and destroy your batteries. For this to work your system has to be designed properly where you use 20% or more of your battery capacity daily, and the panel wattage sized to replace that energy daily. IT DOES NOT APPLY TO OCCASIONAL USERS like weekend cabins.
Second the actual voltages vary by manufacture and battery type being either AGM or FLA. So the actual voltages need to come the OWNERS MANUAL. What follows is generic based on either FLA or AGM chemistry.
AGM
Bulk = Absorb = 2.4 to 2.6 Vpc. Lower range in summer warm months, higher in winter.
Float = 2.25 Vpc
FLA
Bulk = Absorb = 2.5 to 2.7. Lower range in summer, higher in winter.
Float = 2.2
OK to answer your question I have to make some caveats here because sure enough some of you will run off and try this without all the facts and destroy your batteries. For this to work your system has to be designed properly where you use 20% or more of your battery capacity daily, and the panel wattage sized to replace that energy daily. IT DOES NOT APPLY TO OCCASIONAL USERS like weekend cabins.
Second the actual voltages vary by manufacture and battery type being either AGM or FLA. So the actual voltages need to come the OWNERS MANUAL. What follows is generic based on either FLA or AGM chemistry.
AGM
Bulk = Absorb = 2.4 to 2.6 Vpc. Lower range in summer warm months, higher in winter.
Float = 2.25 Vpc
FLA
Bulk = Absorb = 2.5 to 2.7. Lower range in summer, higher in winter.
Float = 2.2