    230 watt solar panels question

    I am building a small system for an offgrid outbuilding in Asheville NC. I have 4-230watt 24v sharp solar panels. I am wanting to upgrade the system to 4 more panels (230w) later (for a total of 8 panels) and I have a wind turbine that will provide 1kw. What is the best quality charge controller and inverter size? and how many 6v golf cart batteries would I need.

    Here are the specs for the panels and wind turbine:

    230 WATTS X 8 Solar Panels = 1840 WATTS
    Open Circuit Voltage (V) 37.1
    Short Circuit Current (A) 8.48


    1000 WATT 24v WIND TURBINE (Max Amps 34, Max Voltage 33.6) Max power 1142 Watts per hr

    2840 WATTS


    I have heard that it is better to hook the wind turbine to its own charge controller with dump load.
    I am going to run various items with this power mainly a small 120v radio, a 12v water pump and some lights.
    Any advice would be appriecated.
  • Naptown
    Solar Fanatic
    • Feb 2011
    • 6880

    #2
    That amount of wattage really should be at 48V unless you plan to separate into several smaller systems.
    NABCEP certified Technical Sales Professional

    [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

    [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

    [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

    Comment

    • ttallos
      Junior Member
      • Apr 2012
      • 6

      #3
      48 volts is fine

      Since I only have the panels I could do anything I want 48 volts sounds good. I could hook up half the panels in parallel 2 times and then wire both halves in series. What do you think?

      Comment

      • Naptown
        Solar Fanatic
        • Feb 2011
        • 6880

        #4
        How you connect the panels depends on the Vmp on the panels. What is it. You may be better off with either 6 or 9 panels. You need to keep the voltage high enough to charge the batteries but below the rated voltage of the charge controller at Voc on the coldest recorded temperature for your area.
        You will need at least a 45A MPPT charge controller for the Solar (based on a 48V system).
        NABCEP certified Technical Sales Professional

        [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

        [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

        [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          Untill you know what your loads are, you should not be talking panels and batteries.

          1 define the loads
          2 loads define the batteries
          3 size of batteries defines the array to recharge them.

          But now you have the cart in front of the horse, and we all know how that generally works out.
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • Naptown
            Solar Fanatic
            • Feb 2011
            • 6880

            #6
            Originally posted by Mike90250
            Untill you know what your loads are, you should not be talking panels and batteries.

            1 define the loads
            2 loads define the batteries
            3 size of batteries defines the array to recharge them.

            But now you have the cart in front of the horse, and we all know how that generally works out.
            To add one more thing to the list daily insolation. This will also determine battery bank size as for instance in a place like Seattle where there is very little insolation therefore the wattage on the panels will necessarily need to be high. one must be careful of charge rates on the batteries so as not to destroy them by feeding in too much current.
            NABCEP certified Technical Sales Professional

            [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

            [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

            [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

            Comment

            • ttallos
              Junior Member
              • Apr 2012
              • 6

              #7
              I see what you mean

              This stuff is a gift the 8 panels so I am just going to hook up a radio some lights and a frige or freezer if this small size will handle it. I realize that it may NOT. I have a friend that has been off the grid for 2 years. He told me that it is best not to spend alot of $$ on batteries the first go around because most novice users just burn them up anyway. I am getting 12v (105Ah) golf cart batteries as a result.


              It sounds like I need to figure out what kind of load I would need to run.
              Then compute the battery bank size needed.
              Then figure the array size based on that.

              Still I am going to get these 8 panels I was thinking 8 12v batteries to start

              Thanks for the advice on the 45w charge controller. I am going to go with Outback or Xantrex

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                Originally posted by ttallos
                ....
                Thanks for the advice on the 45w charge controller. I am going to go with Outback or Xantrex
                Also consider the Morningstar MPPT 45 & 60, and the Midnight Classic , both of which I feel have a better human/computer interface than Outback or Xantrex.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • Naptown
                  Solar Fanatic
                  • Feb 2011
                  • 6880

                  #9
                  Originally posted by ttallos
                  This stuff is a gift the 8 panels so I am just going to hook up a radio some lights and a frige or freezer if this small size will handle it. I realize that it may NOT. I have a friend that has been off the grid for 2 years. He told me that it is best not to spend alot of $$ on batteries the first go around because most novice users just burn them up anyway. I am getting 12v (105Ah) golf cart batteries as a result.


                  It sounds like I need to figure out what kind of load I would need to run.
                  Then compute the battery bank size needed.
                  Then figure the array size based on that.

                  Still I am going to get these 8 panels I was thinking 8 12v batteries to start

                  Thanks for the advice on the 45w charge controller. I am going to go with Outback or Xantrex
                  Avoid batteries in parallel instead of 8 12V batteries get 8 6 volt batteries in the end they will work better and may give you a higher AH rating for the same cost. Besides most golf cart batteries are 6V anyway.
                  NABCEP certified Technical Sales Professional

                  [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                  [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                  [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                  Comment

                  • ttallos
                    Junior Member
                    • Apr 2012
                    • 6

                    #10
                    Thanks for the clarification check this picture out

                    4 group (s) of 2 batteries in series at 12 volts & 200 AH produce a 12 volt battery bank at 800 Amp Hours capacity.

                    By the way I love the Morningstar MPPT 60, it looks like a good fit for me. They also have a really great String Calculator to help with the design!

                    I will upload a picture of the array config next. And before I finish this thread I will have a schematic of my whole system. Thanks for all the help!
                    Attached Files

                    Comment

                    • Naptown
                      Solar Fanatic
                      • Feb 2011
                      • 6880

                      #11
                      Originally posted by ttallos
                      4 group (s) of 2 batteries in series at 12 volts & 200 AH produce a 12 volt battery bank at 800 Amp Hours capacity.

                      By the way I love the Morningstar MPPT 60, it looks like a good fit for me. They also have a really great String Calculator to help with the design!

                      I will upload a picture of the array config next. And before I finish this thread I will have a schematic of my whole system. Thanks for all the help!
                      The problem is equal charging and discharging on a parallel battery bank. The batteries in the middle will fail first taking out the entire bank with them. Series stringing on batteries is always better in the long run.
                      If you have not purchased the batteries yet please seriously reconsider going to 6 volt in series.
                      And it actually produces an 800AH bank at 24V
                      Series batteries voltage builds parallel batteries amperage builds.
                      So the way you have them configured in 4 parallel strings of 2
                      2 200AH batteries in series is 200 AH @ 24V
                      4 24V 200AH batteries in parallel is 24V @800 AH =9600 watt hour which is what you calculate in
                      If you insist on 12V batteries go 48V with 2 strings of 4 batteries in series.
                      Several things will happen
                      1- it will be easier to balance the battery charge/discharge to maintain longest life.
                      2- Wiring from battery to inverter will be smaller.
                      3- Higher voltage from the array will be better managed.
                      4- You will be able to put more wattage from the array on the same charge controller
                      (remember amperage on the CC is output amps.) divide wattage of array by battery voltage.
                      So 2400W @24V = 100A
                      2400W @ 28V = 50A
                      Last edited by Naptown; 04-23-2012, 09:56 PM.
                      NABCEP certified Technical Sales Professional

                      [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                      [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                      [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                      Comment

                      • ttallos
                        Junior Member
                        • Apr 2012
                        • 6

                        #12
                        6 Volt Sounds good

                        OK I think the 6v was the cheaper battery! I will switch to that
                        Attached Files

                        Comment

                        • Naptown
                          Solar Fanatic
                          • Feb 2011
                          • 6880

                          #13
                          Originally posted by ttallos
                          OK What about this array design check out this picture.
                          Better for design and charging but bank will be 48V 200AH
                          Remember series voltage builds
                          Parallel amperage builds
                          NABCEP certified Technical Sales Professional

                          [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                          [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                          [URL="http://www.gaisma.com"]www.gaisma.com[/URL]