Hi all,
I'm running both 48VDC power (from battery bank) and 120VAC power (from inverter) to load distribution panels in a shipping container located 40 feet away. The 48VDC will be converted to 12VDC via a buck converter at the shipping container prior to the branch circuits, and then distributed to DC refrigerator, lighting, and USB outlets. The 120VAC will be used for a split system and a few outlets.
I've been reading about grounding/bonding, circuit protection, and wire sizing until I'm crosseyed. For the DC run, I am planning on running 8awg from a 30A DC breaker at the battery bank to the 30A shipping container buck converter and 10awg from a 30A AC breaker at the inverter to the shipping container AC load dist panel. I'll be installing a ground rod at inverter/battery bank, to which the battery neg, inverter gnd, and inverter neutral will be bonded (plus solar charging and inverter equipment enclosures). Will also be installing a ground rod at the shipping container, which AC ground wire, 48VDC neg wire, and the shipping container itself will be bonded to (plus load dist panel enclosures). AC neutral and gnd will not be bonded at shipping container subpanel.
If this all sounds right so far, my questions are:
-Do I bond the shipping container 12VDC buck converter output negative to ground, in addition to the 48VDC negative? or instead of?
-Can the AC ground wire from the inverter to the shipping container also serve as the 48VDC negative wire between the battery bank DC circuit breaker and the shipping container buck converter? If so, can I run 4 conductors in a single conduit to the shipping container - one AC hot, one AC neutral, one 48VDC pos, and one AC gnd/48VDC neg? I assume, if the AC gnd wire can in fact double as DC neg, that one would need to be of a much larger size... 4awg?
-For the branch circuits in the shipping container - can the shipping container itself serve as the DC negative return path, and AC ground? Meaning, I just run a single conductor from 12VDC (+) to each DC end-use appliance/outlet (+) input, and then bond the appliance (-) to shipping container, and run AC hot and neutral to each AC appliance/outlet, and bond the appliance/outlet gnd to shipping container?
I'm almost certain that this doesn't stack up to code, so I'd love to know what code says - but also know that parallel DC and AC circuits is extremely uncommon, so would love to know the feasibility/safety of this beyond what the code says.
Many thanks to this forum community, the knowledge shared here is immensely helpful!
I'm running both 48VDC power (from battery bank) and 120VAC power (from inverter) to load distribution panels in a shipping container located 40 feet away. The 48VDC will be converted to 12VDC via a buck converter at the shipping container prior to the branch circuits, and then distributed to DC refrigerator, lighting, and USB outlets. The 120VAC will be used for a split system and a few outlets.
I've been reading about grounding/bonding, circuit protection, and wire sizing until I'm crosseyed. For the DC run, I am planning on running 8awg from a 30A DC breaker at the battery bank to the 30A shipping container buck converter and 10awg from a 30A AC breaker at the inverter to the shipping container AC load dist panel. I'll be installing a ground rod at inverter/battery bank, to which the battery neg, inverter gnd, and inverter neutral will be bonded (plus solar charging and inverter equipment enclosures). Will also be installing a ground rod at the shipping container, which AC ground wire, 48VDC neg wire, and the shipping container itself will be bonded to (plus load dist panel enclosures). AC neutral and gnd will not be bonded at shipping container subpanel.
If this all sounds right so far, my questions are:
-Do I bond the shipping container 12VDC buck converter output negative to ground, in addition to the 48VDC negative? or instead of?
-Can the AC ground wire from the inverter to the shipping container also serve as the 48VDC negative wire between the battery bank DC circuit breaker and the shipping container buck converter? If so, can I run 4 conductors in a single conduit to the shipping container - one AC hot, one AC neutral, one 48VDC pos, and one AC gnd/48VDC neg? I assume, if the AC gnd wire can in fact double as DC neg, that one would need to be of a much larger size... 4awg?
-For the branch circuits in the shipping container - can the shipping container itself serve as the DC negative return path, and AC ground? Meaning, I just run a single conductor from 12VDC (+) to each DC end-use appliance/outlet (+) input, and then bond the appliance (-) to shipping container, and run AC hot and neutral to each AC appliance/outlet, and bond the appliance/outlet gnd to shipping container?
I'm almost certain that this doesn't stack up to code, so I'd love to know what code says - but also know that parallel DC and AC circuits is extremely uncommon, so would love to know the feasibility/safety of this beyond what the code says.
Many thanks to this forum community, the knowledge shared here is immensely helpful!