Hi forum folks,
Long-time reader here, first-time poster. Thanks for the many years of great insight you've all provided on this forum!
I'm designing an off-grid solar PV and battery system that will supply power to a laundry shed and two individual yurts. The 1.44 kW solar array will be mounted on the roof of and the ~27kWh 48V battery bank, charge controller, AC-to-DC battery charger (for backup generator charging), and inverter supplying the washer and dryer will be housed within the laundry shed. I am then running 48VDC supply wiring to a metal-enclosed "power center" mounted on a 4x4 just outside of each yurt (yurts are located approximately 120' from the laundry shed, in opposite directions), which will then power the almost entirely DC yurt end-uses (lighting, refrigerator, DC computer charger, USB outlets) via a 48V to 12V buck converter and a DC fuse block with the exception of a single 375W 48V inverter at each yurt that will provide power to a couple of outlets if ever needed. Each yurt will draw max 17A @48V from the battery bank, and the laundry shed will draw max 62A @48V from the battery bank.
Here is a link showing a schematic of the design - only one yurt is shown, since the other is the exact same.
My main question is about bonding and grounding. After reading the stickies on this forum about the subject, and other research, I am preliminarily thinking that I will:
-Ground the solar array frames directly to a ground rod located the shortest possible distance away (directly underneath closest corner of array).
-Bond the charge controller enclosure, AC-to-DC charger enclosure, and inverter enclosure to the negative terminal bus (directly connected to negative battery terminal), and run a ground wire from that bus to the same ground rod.
-Install a separate ground rod outside each yurt enclosure, and ground the metal enclosure. Bond the negative 48V supply terminal to the enclosure.
Does this sound right? I've read some places about installing two ground rods - would you recommend that I do this at each location (so 6, total?). And any other feedback is welcomed!
Many thanks!
Long-time reader here, first-time poster. Thanks for the many years of great insight you've all provided on this forum!
I'm designing an off-grid solar PV and battery system that will supply power to a laundry shed and two individual yurts. The 1.44 kW solar array will be mounted on the roof of and the ~27kWh 48V battery bank, charge controller, AC-to-DC battery charger (for backup generator charging), and inverter supplying the washer and dryer will be housed within the laundry shed. I am then running 48VDC supply wiring to a metal-enclosed "power center" mounted on a 4x4 just outside of each yurt (yurts are located approximately 120' from the laundry shed, in opposite directions), which will then power the almost entirely DC yurt end-uses (lighting, refrigerator, DC computer charger, USB outlets) via a 48V to 12V buck converter and a DC fuse block with the exception of a single 375W 48V inverter at each yurt that will provide power to a couple of outlets if ever needed. Each yurt will draw max 17A @48V from the battery bank, and the laundry shed will draw max 62A @48V from the battery bank.
Here is a link showing a schematic of the design - only one yurt is shown, since the other is the exact same.
My main question is about bonding and grounding. After reading the stickies on this forum about the subject, and other research, I am preliminarily thinking that I will:
-Ground the solar array frames directly to a ground rod located the shortest possible distance away (directly underneath closest corner of array).
-Bond the charge controller enclosure, AC-to-DC charger enclosure, and inverter enclosure to the negative terminal bus (directly connected to negative battery terminal), and run a ground wire from that bus to the same ground rod.
-Install a separate ground rod outside each yurt enclosure, and ground the metal enclosure. Bond the negative 48V supply terminal to the enclosure.
Does this sound right? I've read some places about installing two ground rods - would you recommend that I do this at each location (so 6, total?). And any other feedback is welcomed!
Many thanks!