Hello,
I have noticed a decrease in the production from one of my solar strings.
Background.
48 volt system. 3 Mitsubishi MF175 in series feeding an Outback MX60 charge controller. 30voc @ 7.92a short circuit for each panel.
Short circuit testing the string is 76 vdc @ 5.6adc. We are in the tropics. With the heat I think that is about normal.
I walked the voc/short circuit tests through the wiring all the way up to the charge controller inputs with no change in what I measured.
Here is the question......
Only 2 or 3 adc are seen by the charge controller.
Anyone ever seen this before?
I have noticed a decrease in the production from one of my solar strings.
Background.
48 volt system. 3 Mitsubishi MF175 in series feeding an Outback MX60 charge controller. 30voc @ 7.92a short circuit for each panel.
Short circuit testing the string is 76 vdc @ 5.6adc. We are in the tropics. With the heat I think that is about normal.
I walked the voc/short circuit tests through the wiring all the way up to the charge controller inputs with no change in what I measured.
Here is the question......
Only 2 or 3 adc are seen by the charge controller.
Anyone ever seen this before?