The config string will vary depending on the inverter make/model. You can read the config string out and save it somewhere so you know how to "repair it" if necessary.
Here's a screenshot I took of a "serial port bridge" (utilizing a Parallax Propeller with a VGA "video driver"--actually on an older touchscreen LCD computer monitor) showing communication between the TS-3000 and the PC software (for "hacking" the protocol):
Untitled.jpg
Blue is the TS-3000. Red is the PC software. You can see the "Q" command for reading status, the "I" command for reading configuration, and the "W" command for writing configuration.
I noticed the "Download" countdown, but do not have any documentation for how that is intended to work.
Yes, the MeanWell HF inverters are quite good for their price range and topology (HF inverters). My only complaints with the MeanWell were:
If you don't, you'll end up with this:
Untitled2.jpg
(screenshot from a chat with the guy I sold my MeanWell to, a year or 2 later...he'd bought a second one shortly after buying the one I had, and I have no idea which one bit the dust here!)
The inverter in question here hit the dumpster before I was aware of it; I'd have been curious to see what exactly went wrong with it.
More people than you think want to run A/Cs on their off-grid systems. It's actually a very common question--well, when you think about it, most people want to "live like normal on solar", instead of stripping down their requirements to the bare minimum.
I'm the "Sid" in said videos...yeah, the explosions were definitely unnerving (sounds like a gun going off when all that power gets misdirected in the FETs)...but we did get it solved.
Yes, it could be said that starting from scratch could be better--BUT if I can redesign based off an existing design, then I don't completely have to "reinvent the wheel." As of right now, the next batch of GS inverters will not use a single PJ board--every single board in the inverter will have been designed on my desk, with all specification design requirements determined in the same place.
Worth noting: the no-load current of the GS 12kw inverter prototype seen in said videos...is significantly LOWER than that of the 3kw Mean Well TS-3000 (0.7-0.8A vs 1.0A). Just sayin'
As of right now, I have zero plans to make an HF inverter...because their surge capacity is extremely low (due to designing the boost converter for the stated redline output and no further)...and the output FETs / IGBTs don't have any "protection" against dirty loads / backfeed. Adding to that, HF inverters have to have a completely separate "Battery charge" circuit--I am not aware of any HF inverter that can use the existing "inverter" circuitry in reverse to charge the battery. LF inverters are considerably more versatile in design by that regard, as no extra circuitry has to be added for battery charge. LF inverters can also (if properly designed/programmed!) easily handle grid-tie solar arrays, using excess power from them to charge the batteries, and shutting the grid-ties down when the batteries are full, etc.
Here's a screenshot I took of a "serial port bridge" (utilizing a Parallax Propeller with a VGA "video driver"--actually on an older touchscreen LCD computer monitor) showing communication between the TS-3000 and the PC software (for "hacking" the protocol):
Untitled.jpg
Blue is the TS-3000. Red is the PC software. You can see the "Q" command for reading status, the "I" command for reading configuration, and the "W" command for writing configuration.
I noticed the "Download" countdown, but do not have any documentation for how that is intended to work.
Yes, the MeanWell HF inverters are quite good for their price range and topology (HF inverters). My only complaints with the MeanWell were:
- Could not adjust the OVP shutdown to 60v (as I thought I should be able to from the datasheet). Fine if you're using Lithium-based batteries--but if you're using lead-acid with temperature compensation, you're out of luck.
- No-load current was a solid 1A at 48-60v. (That's at least double what a 6kw LF Genetry Solar inverter runs at no load.) Notice that this specification is not listed in any of the documentation--they only list the "power save" draw, which is with the inverter basically off.
- Maximum efficiency of 91% listed is not significantly greater than a good LF inverter (=85%+)
- Couldn't start a window A/C unit--I have video of this. Didn't blow up though.
If you don't, you'll end up with this:
Untitled2.jpg
(screenshot from a chat with the guy I sold my MeanWell to, a year or 2 later...he'd bought a second one shortly after buying the one I had, and I have no idea which one bit the dust here!)
The inverter in question here hit the dumpster before I was aware of it; I'd have been curious to see what exactly went wrong with it.
More people than you think want to run A/Cs on their off-grid systems. It's actually a very common question--well, when you think about it, most people want to "live like normal on solar", instead of stripping down their requirements to the bare minimum.
I'm the "Sid" in said videos...yeah, the explosions were definitely unnerving (sounds like a gun going off when all that power gets misdirected in the FETs)...but we did get it solved.
Yes, it could be said that starting from scratch could be better--BUT if I can redesign based off an existing design, then I don't completely have to "reinvent the wheel." As of right now, the next batch of GS inverters will not use a single PJ board--every single board in the inverter will have been designed on my desk, with all specification design requirements determined in the same place.
Worth noting: the no-load current of the GS 12kw inverter prototype seen in said videos...is significantly LOWER than that of the 3kw Mean Well TS-3000 (0.7-0.8A vs 1.0A). Just sayin'

As of right now, I have zero plans to make an HF inverter...because their surge capacity is extremely low (due to designing the boost converter for the stated redline output and no further)...and the output FETs / IGBTs don't have any "protection" against dirty loads / backfeed. Adding to that, HF inverters have to have a completely separate "Battery charge" circuit--I am not aware of any HF inverter that can use the existing "inverter" circuitry in reverse to charge the battery. LF inverters are considerably more versatile in design by that regard, as no extra circuitry has to be added for battery charge. LF inverters can also (if properly designed/programmed!) easily handle grid-tie solar arrays, using excess power from them to charge the batteries, and shutting the grid-ties down when the batteries are full, etc.