Panels: LG310N1C-G4 310w (Currently have 14, will double that is the plan)
CC: 48V Victron MPPT 100/20
Would like some input from the pros
Plan is to run 48v battery bank, 8, 6v (trojan industrial then lithium or whatever is better in 3-5y) batteries (although unsure if that will provide the needed rating, if for instance we're running 25-40a off each inverter) and run 2 panels per-controller in series to get the voltage needed to charge the battery bank.
The inverter side I'm planning on running 2 Victron Quattro 48v\10,000W (to start, adding a 3rd, for 3-phase later).
I was going to run 5000w units as it would more than handle my loads but having the oversized components for around 800$\More - $1600 total seemed like a no-brainer to jump from 5kW to 10kW inverter. These will be running as an appliances\grid0 programmed via victron software, and each Quattro will also be connected to a 2000w Honda EU2000i generator for winter issues with lots of snow.
Tell me what's wrong, thoughts, opinions
CC: 48V Victron MPPT 100/20
Would like some input from the pros

Plan is to run 48v battery bank, 8, 6v (trojan industrial then lithium or whatever is better in 3-5y) batteries (although unsure if that will provide the needed rating, if for instance we're running 25-40a off each inverter) and run 2 panels per-controller in series to get the voltage needed to charge the battery bank.
The inverter side I'm planning on running 2 Victron Quattro 48v\10,000W (to start, adding a 3rd, for 3-phase later).
I was going to run 5000w units as it would more than handle my loads but having the oversized components for around 800$\More - $1600 total seemed like a no-brainer to jump from 5kW to 10kW inverter. These will be running as an appliances\grid0 programmed via victron software, and each Quattro will also be connected to a 2000w Honda EU2000i generator for winter issues with lots of snow.
Tell me what's wrong, thoughts, opinions

Comment