Generator tripping 240v circuit breaker

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • hammick
    Solar Fanatic
    • Jul 2015
    • 368

    #16
    Both wires were black and it didn't even dawn on me they were separate legs. I guess the fact that there is only one 120v duplex outlet on the genny should have clued me in. I didn't notice the tab removed on the outlet I replaced. The other 120v outlet is a 30a RV plug.
    Conext XW5548
    Conext MPPT60-150

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #17
      Originally posted by hammick
      Both wires were black and it didn't even dawn on me they were separate legs..
      That is inexperience and lack knowledge of electrical codes and color codes. Black = Hot, White = Neutral, Green = Ground...

      I am not criticizing you, just pointing out any electrician who sees two black wires automatically knows what he has (L1 and L2). So when you seen 2-Black, 1-White, and 1-Green should tell you immediately you have a 4-wire 240/120 circuit. It is what you did not know that got you into trouble.

      I am glad you figured it out, and thankful it was just a generator output and not utility power. If it had been utility power a tripped breaker would have been the least of your problems. You would have had an ARC FLASH to deal with. Which brings us back to your batteries again. Make that mistake with them and you will be introduced to Arc Flash 101. With Arc Flash 101 there are only two grades the teacher issues. One is nice and Adorable, and the other is a big fat Fire
      Last edited by Sunking; 02-19-2016, 06:25 PM.
      MSEE, PE

      Comment

      • Bala
        Solar Fanatic
        • Dec 2010
        • 734

        #18
        Originally posted by Sunking

        That is inexperience and lack knowledge of electrical codes and color codes. Black = Hot, White = Neutral, Green = Ground...

        I am not criticizing you, just pointing out any electrician who sees two black wires automatically knows what he has (L1 and L2). So when you seen 2-Black, 1-White, and 1-Green should tell you immediately you have a 4-wire 240/120 circuit. It is what you did not know that got you into trouble.
        As there are a few people on the forum from other parts of the world, those wire colors and configurations may not apply. So make sure you know what you are doing.

        For Australia we have only 240V for households, small gensets. Only 3 wires know as active neutral and earth. Active and neutral have a few color variants. Earth is always green. White is not used for AC here.

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #19
          Originally posted by Bala

          As there are a few people on the forum from other parts of the world, those wire colors and configurations may not apply. So make sure you know what you are doing.
          Well Hammick is in the USA. This being a DIY site means most have no clue what they are doing. If they did, they would not be here in the first place.
          MSEE, PE

          Comment

          • Logan005
            Solar Fanatic
            • Nov 2015
            • 490

            #20
            I know when wiring a half duplex switched outlet in homes, I break the tab, to split the receptacle. seems designers don't do it as much these days. All 3 bedrooms in our house are wired like this.
            4X Suniva 250 watt, 8X t-105, OB Fx80, dc4812vrf

            Comment

            • hammick
              Solar Fanatic
              • Jul 2015
              • 368

              #21
              Well Sunking I have to disagree. First I am no electrician but I have a lot of wiring experience. Two black wires doesn't always mean L1 and L2. There are often at least four outlets on a 20a or 15a circuit. Two black wires on all but the last outlet and the tab is intact. One black travels to the next outlet.
              Last edited by hammick; 02-20-2016, 12:01 AM.
              Conext XW5548
              Conext MPPT60-150

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #22
                Originally posted by hammick
                Well Sunking I have to disagree. First I am no electrician but I have a lot of wiring experience. Two black wires doesn't always mean L1 and L2. There are often at least four outlets on a 20a or 15a circuit. Two black wires on all but the last outlet and the tab is intact. One black travels to the next outlet.
                That would be 6-wires (2 black, 2 white, 2 green).You would not break the TAB at any daisy chained outlet in the scenario you just mentioned. The last outlet would only have 3 wires of L>N>G. You had a dedicated outlet with 4-wires making it 2 dedicated circuits. One circuit on L1, and another on L2.
                Last edited by Sunking; 02-20-2016, 12:45 AM.
                MSEE, PE

                Comment

                • hammick
                  Solar Fanatic
                  • Jul 2015
                  • 368

                  #23
                  Removed the tab on the outlet and the generator runs and puts out power like new.
                  Last edited by hammick; 02-21-2016, 07:11 PM.