how many panels to a 40 amp mppt controller
Collapse
X
-
-
980W divided by 12 is 81A. That is more than 40A. So two panels max. Most PWM CCs do not allow you to have too high an input power from the panel array. Most MPPT CCs can simply ignore the extra power, but it will do you no good.
You would be better off with a 24V battery system, where you could use all four panels with the single 40A CC.
Putting multiple 12V batteries in parallel to get the capacity you need is also a bad idea. Increase the system voltage first, then go to lower voltage batteries (2, 4, 6 or 8V) to make up one string at the right capacity.SunnyBoy 3000 US, 18 BP Solar 175B panels. -
245W times four is about 980 watts.
980W divided by 12 is 81A. That is more than 40A. So two panels max. Most PWM CCs do not allow you to have too high an input power from the panel array. Most MPPT CCs can simply ignore the extra power, but it will do you no good.
You would be better off with a 24V battery system, where you could use all four panels with the single 40A CC.
Putting multiple 12V batteries in parallel to get the capacity you need is also a bad idea. Increase the system voltage first, then go to lower voltage batteries (2, 4, 6 or 8V) to make up one string at the right capacity.
would it be ok to have the panels wired in parallel? Or will the panels need to be wired in series
as well?Comment
-
Answer your own question. 40 amp MPPT has a limit of
500 watts at 12 volt
1000 watts @ 24 volt
2000 watts @ 48 voltMSEE, PEComment
-
Comment
-
A PWM CC will usually explicitly limit the input power (in this case the Imp and Isc) to not more than 10% above the CC output current rating.
Even when it is allowed, the higher panel wattage will usually not produce any higher output from the CC.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
OK then if my batteries are set up as series to 24 volts then the panels should be OK wired in parallel.
I have a 12 volt inverter and a few 12 accessories. How would I go about hook them up?
If I hooked the inverter to one of the batteries would I be pulling power from all the batteries or just one?Comment
-
There are special converters that attach to both batteries in a 24V string and produce one 12V output, but they might be more expensive than getting a 24V inverter.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
You can only use 2 panels if you insist on 12 volts. For your panel wattage really screams 24 and even 48 volts.MSEE, PEComment
-
OK then if my batteries are set up as series to 24 volts then the panels should be OK wired in parallel.
I have a 12 volt inverter and a few 12 accessories. How would I go about hook them up?
If I hooked the inverter to one of the batteries would I be pulling power from all the batteries or just one?
You can either have a 12V system (over 80 amps) or a 24V system (close to 40 amps) But you can't mix voltages in a system- it's either ALL 12V gear, or ALL 24V gear.
More than 2 panels in parallel, you need fuses/combiner box for each panel
You could get around that with a combination of 2 panels in series, and then parallel the 2 series strings. Gives you a 80V array at 17A,Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Comment
-
Uh oh.
You can either have a 12V system (over 80 amps) or a 24V system (close to 40 amps) But you can't mix voltages in a system- it's either ALL 12V gear, or ALL 24V gear.
More than 2 panels in parallel, you need fuses/combiner box for each panel
You could get around that with a combination of 2 panels in series, and then parallel the 2 series strings. Gives you a 80V array at 17A,
i use 12v and 24v gear. have 12v dc chargers, 12 inverter, 24v inverters, 24v solar setup. when i need to charge off the gen i switch the cables around from series to parallel, if its raining for a couple of days leave it in parallel and use the 12 inverter. use 100amp alligator clips on everything for easy reconfigurationComment
-
Well, if you enjoy rewiring the system, and the losses and risks from using gator clips, you can continue as is, and just make a good home video for your heirs, for when it all goes up in smoke.
Combiner boxes are designed to securely hold fuses or breakers, and contain the wire splices, to prevent good panels from starting a fire if a panel goes bad.
Harvesting 328 watts in a 12v configuration gives less power than harvesting the same 328 watts in a 24V configuration, because of copper losses, internal contact resistance in the connectors, and the mismatch of your panel voltage to battery voltage when using the 12V PWM controller
MPPT controller gives you Watts In = Watts Out (with just a few % of losses internally)
PWM controller gives you a lot more losses (Sunking has the math nailed down)
Your panels are 31v @ 8 amps (roughly) for about 248 watts BUT your BATTERY charges at about 14V, at the same 8 amps,
so you only get 112 watts into the battery . That's HALF your panel wattage just gone and wasted.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Comment
Comment