What size of fuse is required for this small 24V system?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15161

    #16
    Originally posted by Amy@altE
    The fuses used are slow blow fuses. See the attached graph. The Xantrex fuse can handle 250% of its rating for 10 seconds, over 300% for 1 second. [ATTACH=CONFIG]6675[/ATTACH]
    +1. Got it. Thanks.

    Comment

    • Wakie
      Junior Member
      • Nov 2014
      • 12

      #17
      Originally posted by SunEagle
      It is not necessarily the battery chemistry that determines the size of your inverter it is the Ah and voltage rating. Also over sizing the inverter (even for short time high wattage loads) can drain your battery faster due to the higher "no load" wattage losses with just the inverter on. A 1500 watt inverter with a even a 5% no load loss will use 75 watts just sitting there. It's a vampire load which reduces the amount your battery can deliver.
      All my inverter draw only 1 amp or lot less with no load
      1000 w msv draw 200 milliamp on 12 v
      Another 1000w 12 v msw draw 1 amp ( the worst)
      2300 w. Msw 24 v draw 250 milliamp

      It s far from 5%

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15161

        #18
        Originally posted by Wakie
        All my inverter draw only 1 amp or lot less with no load
        1000 w msv draw 200 milliamp on 12 v
        Another 1000w 12 v msw draw 1 amp ( the worst)
        2300 w. Msw 24 v draw 250 milliamp

        It s far from 5%
        Sounds like you have a very efficient inverter. Some of those cheap ones will drain a battery faster than you can blink.