Solaredge inverter synchronizing with Victron multiplus or quattro

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Baytep
    Junior Member
    • Mar 2014
    • 5

    #1

    Solaredge inverter synchronizing with Victron multiplus or quattro

    hi all,

    Does any of you have experience using a solaredge SE 2200 inverter together with a Victron battery inverter?

    The setup is on a ship.
    the Victron inverter provides a a pure sine wave 230 VAC ± 2% Frequency: 50 Hz ± 0,1%
    Victron says that most solar inverters have an off-grid mode, I couldn't find it in the manual of Solaredge.

    Thanks for your help!
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    if you are trying to pair a grid-tie inverter with a battery inverter, you will have GREAT difficulty. Generally it does not work. If the manual does not describe how to do it, it's not happening.

    Problem: When loads are light, and the sun is bright, the "local grid" voltage gets driven very high, and if the GT inverter does not disconnect fast enough at 260VAC, some other gear of yours will fry.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Baytep
      Junior Member
      • Mar 2014
      • 5

      #3
      Thanks Mike.

      the problem seems to be narrowed down to islanding protection.

      In case of off-grid situation the Victron Quattro monitors the load and battery capacity. Based on that it can toggle a relay that can switch off the solar inverter, or re-route it to a dump resistance (waterheater) in case of low load and topped up battery.
      Then the batteries will supply power to the (light) load until their capacity reaches a lower level and the relay switches the solar inverter again because sufficient load is available (charging the batteries).
      So it looks like the Victron takes care of that part.

      The grid monitoring function in the Solaredge inverter seems to be the problem here.
      Victron requires that this function can be disabled in the solar inverter as the grid impedance is different from the "island" impedance. They supply a separate impedance monitor to be places only between solar inverter and the grid.
      The Solaredge inverter has this function disabled by default but it seems that it will not work in that mode (the manual is not clear at this), and you have to select this function according to the country you are in. This country selection then determines which grid monitoring you use.

      So there are 2 questions:
      Will the Solaredge SE2200 inverter work with the grid monitoring function disabled?
      Can you select a country so that this function is not active?

      Thanks for any advice!

      Comment