Here's the breakdown of my power usage:
Lights: ~200W total in the RV. On for 5-6 hours a day max.
Water: powered by 90W pump, only on when using water (let's say 1 hour a day?)
Laptop: ~90W power adapter. Generally on this thing a lot, let's say 8 hours a day (more now, but traveling, I assume that will decrease).
Phone: using as hotspot, will need to keep plugged in = 10W for ~12 hours day
Speakers: 120W x 2 = 240W, plus about 200W max from the subwoofer and its amp, and then I have an audio interface that uses 24W = ~470W total, probably on for 6 hours out of a day.
Misc: random power tools, things I'm using occasionally when working on projects, let's say 200W, for 1 hour a day.
Total power per day:
+200W for 6 hours = 1200Wh
+90W for 1 hour = 90Wh
+90W for 8 hours = 720Wh
+10W for 12 hours = 120Wh
+470W for 6 hours = 2820Wh
+200W for 1 hour = 200Wh
TOTAL: 5150Wh / day
With that said, seeing as I'd be smart to have a battery bank that won't see < 50% DOD, 10kwh seems like a good mark, especially considering I should plan for reserves. Yeah?
As for the solar panels, yeah, I had planned to have about 1500W on the roof. There should be plenty of room for 6*250W or 300W panels. I also had ideas to put them on the sides, on hinges, that I'd prop up when stationary, but only if that's necessary.
@OldSmokey... the T-105 is a 6V battery? What's the deal here, guys? Should I not have any batteries in parallel at all, or is that always going to be a requirement at some point, to meet the 12V, whatever Ah I need (10kwh @ 12v = ~800Ah). With a 6V battery, I'd go in series twice, then everything else in parallel. I'm a little confused as I don't see a way around having to do some in parallel.
8x T105 is approx 10.8 Kwh like your initial value, but that's not your real issue here. your power estimate I think is way off..
My wife and I boondock a lot and our first power estimate was high like yours, after some analysis our figures decreased a lot.
here are some estimates based on real world numbers that we average with our RV combined with your consumption with an inverter for 120V loads.
first are 12 Volt loads..
Lights: we have 18 lights in our RV, they are LED and 5 watts each. Rarely do we have them all on at one time, our average use is
6 on at any one time so call that 30 Watts for 5 hours = 150 Wh
Water: Our pump is typical rv and is a 100 Watt motor, we have 2 showers at 5 mins each and approx 10 mins other usage
so call that 20 mins at 100 W per day. ( 20 minutes runtime is a LOT of water.. ) = 34 Wh
Fridge on propane is approx 18 W and assume 75% duty cycle 18 * 24 * 0.75 = 324 Wh
Phone via 12 V USB adapter : 10W * 12 = 120 Wh
total 12 Volt Wh rounded up is approx = 628 Wh
next is 120 V loads via inverter.
Speakers, well we dont have any, but I assume you will not be at full tilt with these for 6 hrs ?
perhaps a reasonable estimate is more like 200 W so let's say 200 * 6 = 1200 Wh
Misc:.. ok, 200 it is .. = 200 Wh
Laptop: I have a Dell laptop with 90W supply, in actual use my Kill-A-watt shows an average demand of 25W.
so thats 25W for 8 hrs = 200 Wh
so this total is : 1600 Wh, now allow for inverter efficiency of 85% = 1882 W
your total battery Wh is now approx: = 1882 + 628 Wh = 2510 Wh
the second issue is that you have not accounted for cloudy days.
we have experienced 3 consecutive days without sun, you need capacity or "autonomy" to cover this before you
get the generator out. if you read Sunking's tutorial he states to cover this with battery capacity for 5 days
so using 2510 Wh and 50% DOD we get approx 2510 Wh * 5 days * (100%/50%) = 25100 Wh and using 48V = 523 Ah capacity
if you go 4 days then 2510 Wh * 4 Days * (100%/50%) = 20080 Wh at 48 V = 418 Ah.. that's a good match for a 6 Volt Trojan L16P
so eight of those would cost approx $2400 and weigh approx 910 lbs
1500 W panels requires a 30A minimum controller at 48 V
charge rate is a little low at C/13 however
also you will need a 48V to 12V buck converter to provide 12V power
and a combined 48V inverter/charger is a reasonable option.
please read the offgrid and battery tutorials to get a better idea..