Hey guys,
I'm assembling a new LFP for my RV out of Chinese cells. These are 100Ah prismatics, and I have 112 of them for 16s7p. My plan is to add isolators for each 16s string so they can be pulled out for service or disconnected automatically if something is amiss.
Meanwhile, I was hoping to manage this bank passively (and conservatively) just using pack-level voltages for LVD and charge termination. I'm using a large Victron Quattro inverter that somehow seems to have a lot more limitations on how it can be set up than I expected. Here are the issues I am observing:
1. The inverter can be set to alarm (A), shutdown (B), and restart (C) at voltages A/B/C respectively. However, C must be 4.0v > B. For now I am setting B to 47.0v and C to 51.0v. In normal use the pack should never get here, because I will add logic to start the charger (and genset if needed) much earlier.
2. The charger has a CC limit (X), a voltage (Y) to transition to CV/absorption, and then a "max absorption length" time (Z) with increments of one hour and a minimum of 1.0h.
On my test run so far with a bottom-balanced, smaller 16s1p pack, I've charged at X=50A to Y=55.2V, but I had to manually stop the charge after only 20 minutes of CV because a cell hit 3.6v (actually, 3.65v before I caught it). I will try again at 54.8v tonight, hoping that that leads to a longer absorb window. But the 1.0h timer limitation seems arbitrary and problematic.
Victron actually documents a method to set a tail charge current termination percentage, which is what I think we really want, but somehow that feature has disappeared from the latest firmware. I've asked them where that feature went, but I haven't received any response yet.
I can buy or build a cell-level voltage-monitoring system and use that to control the charge, but I was hoping to avoid having to wire 112 sensors and all the complexity/extra cost that that presents. If I'm willing to use 80% of the pack capacity, do you guys see a way to pull this off without going this route given the above?
I'm assembling a new LFP for my RV out of Chinese cells. These are 100Ah prismatics, and I have 112 of them for 16s7p. My plan is to add isolators for each 16s string so they can be pulled out for service or disconnected automatically if something is amiss.
Meanwhile, I was hoping to manage this bank passively (and conservatively) just using pack-level voltages for LVD and charge termination. I'm using a large Victron Quattro inverter that somehow seems to have a lot more limitations on how it can be set up than I expected. Here are the issues I am observing:
1. The inverter can be set to alarm (A), shutdown (B), and restart (C) at voltages A/B/C respectively. However, C must be 4.0v > B. For now I am setting B to 47.0v and C to 51.0v. In normal use the pack should never get here, because I will add logic to start the charger (and genset if needed) much earlier.
2. The charger has a CC limit (X), a voltage (Y) to transition to CV/absorption, and then a "max absorption length" time (Z) with increments of one hour and a minimum of 1.0h.
On my test run so far with a bottom-balanced, smaller 16s1p pack, I've charged at X=50A to Y=55.2V, but I had to manually stop the charge after only 20 minutes of CV because a cell hit 3.6v (actually, 3.65v before I caught it). I will try again at 54.8v tonight, hoping that that leads to a longer absorb window. But the 1.0h timer limitation seems arbitrary and problematic.
Victron actually documents a method to set a tail charge current termination percentage, which is what I think we really want, but somehow that feature has disappeared from the latest firmware. I've asked them where that feature went, but I haven't received any response yet.
I can buy or build a cell-level voltage-monitoring system and use that to control the charge, but I was hoping to avoid having to wire 112 sensors and all the complexity/extra cost that that presents. If I'm willing to use 80% of the pack capacity, do you guys see a way to pull this off without going this route given the above?