Now you are beginning to understand. No External Lithium battery charger and NO SOLAR CHARGE CONTROLLERS DOES THAT. You would have to have a integrated BMS/Charger to do that. Most Balance or Vampire Boards are dumb passive devices. Even centralized like my Orion is just a simple Bypass. To do what you describe is to have the Balance Boards communicate with the charger so when th every first Balance Boards Turns On, it signals the charger to cut back current to what only the bypass board can bypass. Otherwise if the current is greater than what the balance board can bypass, the remaining flows through the already fully charged cell. There is no reason to ever go to full charge.
Mechanisms that decrease the Lifespan of Lithium-Ion batteries and how to avoid them
Collapse
X
-
-
Sorry cannot edit, so have to double post.The power that isn't burned off in the resistors stays in the cell. This is why you need to cut charger current back during the balance phase--if the balancers can't keep up, the high cell is still getting overcharged. The energy you don't want to keep in the high cell has nowhere to go but the balance resistor, or into the cell itself. The other cells in the series aren't getting any more power than they were before the balancers kicked on.MSEE, PEComment
-
Sorry cannot edit, so have to double post. Now you are beginning to understand. No External Lithium battery charger and NO SOLAR CHARGE CONTROLLERS DOES THAT. You would have to have a integrated BMS/Charger to do that. Most Balance or Vampire Boards are dumb passive devices. Even centralized like my Orion is just a simple Bypass. To do what you describe is to have the Balance Boards communicate with the charger so when th every first Balance Boards Turns On, it signals the charger to cut back current to what only the bypass board can bypass. Otherwise if the current is greater than what the balance board can bypass, the remaining flows through the already fully charged cell. There is no reason to ever go to full charge.Solar Charge Controllers DO NOT HAVE ANY ABILITY to communicate with a BMS. Even Genasum the only company to make a Solar Charge Controller, is just a Simple Float Charger fixed at 14.4 volts. It has no I/O ports to communicate with a BMS.
A 14.4 Volt charger is fine too. If the setpoint of the charger cannot overcharge a balanced pack, you're good unless you've got severe imbalance prior to charge, which would indicate that something else is wrong [that's why you need cell-level monitoring to shut things down if the situation becomes dangerous for any single cell]. As you approach 100% SOC, the voltage delta between the cells and the charger goes down, so current becomes self-limiting. Balancers should never have a problem dealing with the small imbalance that develops between charge cycles in such a system. 14.4 Volts = 3.6 Volts per cell, when your charger current falls to zero (or very near to it), you should have a perfectly balanced pack at 100% SOC, every time. With no automatic balancers, I'd rather turn that down charger down to 14.0-14.2 and manually balance periodically. I've used this technique with no problems on several of my smaller packs for years now---but it's a hassle and I've gotten tired of it. To me it's much better and safer to have automatic balancing every charge cycle. This insures you won't run into the problem you describe here. Cell-level monitoring and shutoff control take care of the times where something has gone truly awry...and you want this whether you have automatic balancing or not.
But my point was this--when balancers are turned on, all other cells in the pack are still getting the same amount of energy they were getting before. They don't get the "surplus power" from the high cell as some kind of extra bonus that brings them up faster than if the balancers weren't there at all. Saying "balance current gets shunted to lower cells" is, to me, a very misleading way of putting things, especially for beginners.Comment
-
Who gives a damn about an EV on a Solar Forum? Solar Charger, even the one MPPT model out there do not have any means to communicate with a Balance Board. This is not a EV forum using AC powered EV chargers. This is a Solar Forum, we use Solar Charge Controllers. Your world does not apply. That is what you do not understand. It would be a rare event to ever get a battery fully charged on solar, does not matter what kind of battery be it lithium or Pb. Solar is a Soft Source with unknown very limited power. With Solar and LFP there are very few things you can add on to it. You can use Balance Boards but they are worthless because they cannot communicate with the Charge Controller to cut back on current when the first board comes on. Nor would you ever want to do that in a Solar System. You want to utilize every bit of solar power you can. So if by chance your batteries were to fully charge by noon, last thing you want to do is turn the solar off and run on batteries when you still have plenty of daylight left. That would be just plain STUPID. You want to Float at less than 100%. So if you got to say 80% when th ebatteries quit ccharging, any loads can use Solar power when demanded so you can save your battery power when there is no sun light. Bottom line is with Solar you basically have a 4 hour window to get your batteries charge between 10 am and 2 pm. As for DIY EV, almost none of the chargers made for lithium DIY EV have the ability to communicate with the charger. They are all CC/CV set to 3.6 vpc and rely on Vampire Boards to bleed off energy. If you really did hang out of DIY EV forum you would know that, and you would also know there are hundreds who use no BMS and Bottom Balance. Heck there is a thread there running right now no BMS is required.MSEE, PEComment
-
Who gives a damn about an EV on a Solar Forum? Solar Charger, even the one MPPT model out there do not have any means to communicate with a Balance Board. This is not a EV forum using AC powered EV chargers. This is a Solar Forum, we use Solar Charge Controllers. Your world does not apply. That is what you do not understand. It would be a rare event to ever get a battery fully charged on solar, does not matter what kind of battery be it lithium or Pb. Solar is a Soft Source with unknown very limited power. With Solar and LFP there are very few things you can add on to it. You can use Balance Boards but they are worthless because they cannot communicate with the Charge Controller to cut back on current when the first board comes on. Nor would you ever want to do that in a Solar System. You want to utilize every bit of solar power you can. So if by chance your batteries were to fully charge by noon, last thing you want to do is turn the solar off and run on batteries when you still have plenty of daylight left. That would be just plain STUPID. You want to Float at less than 100%. So if you got to say 80% when th ebatteries quit ccharging, any loads can use Solar power when demanded so you can save your battery power when there is no sun light. Bottom line is with Solar you basically have a 4 hour window to get your batteries charge between 10 am and 2 pm. As for DIY EV, almost none of the chargers made for lithium DIY EV have the ability to communicate with the charger. They are all CC/CV set to 3.6 vpc and rely on Vampire Boards to bleed off energy. If you really did hang out of DIY EV forum you would know that, and you would also know there are hundreds who use no BMS and Bottom Balance. Heck there is a thread there running right now no BMS is required.Comment
-
TA 14.4 Volt charger is fine too. If the setpoint of the charger cannot overcharge a balanced pack, you're good unless you've got severe imbalance prior to charge, which would indicate that something else is wrong [that's why you need cell-level monitoring to shut things down if the situation becomes dangerous for any single cell]. As you approach 100% SOC, the voltage delta between the cells and the charger goes down, so current becomes self-limiting. Balancers should never have a problem dealing with the small imbalance that develops between charge cycles in such a system. 14.4 Volts = 3.6 Volts per cell, when your charger current falls to zero (or very near to it), you should have a perfectly balanced pack at 100% SOC, every time. With no automatic balancers, I'd rather turn that down charger down to 14.0-14.2 and manually balance periodically. I've used this technique with no problems on several of my smaller packs for years now---.MSEE, PEComment
-
Geez dude you just agreed with me. What the hell do you think I have been talking about all this damn time. Run below 100% and th ecells self balance and if they should ever become unblanced is really simple to be re-balanced. I personally have not had to in 8 moinths, and if you go to DIY EV Forum or EVTV you will find hundreds of people who have not had any balance problems in 3 years. I grant you on a large EV high voltage pack Cell level monitors have benefit. But that is only because of the number of series cells is so much greater 3 to 6 volts is not noticeable. But trust me 3 volts low on a 12 volt system is going to get your attention real damn quick when nothing turns on and you notice your battery is 8 to 11 volts. You do not need a cell monitor to tell you something is wrong. Your Inverter already caught it and shut down.
Li cells don't self-balance...you can say it til you're blue in the face but it still won't be true. As I explained above, the illusion of "self balance" is in fact an expression of cell variation--the very thing that should be telling you why you DO need to balance, and the more often the better.Comment
-
Li cells don't self-balance...you can say it til you're blue in the face but it still won't be true. As I explained above, the illusion of "self balance" is in fact an expression of cell variation--the very thing that should be telling you why you DO need to balance, and the more often the better.Comment
-
Li cells don't self-balance...you can say it til you're blue in the face but it still won't be true. As I explained above, the illusion of "self balance" is in fact an expression of cell variation--the very thing that should be telling you why you DO need to balance, and the more often the better.MSEE, PEComment
-
Not able to edit my replies and not what I meant. I couldn't fix it. It should have read " If Floated to less than 100% re-balance should not be a problem even though lithium cells are not self balancing. with no parasitic loads lithium only imbalance of any significance is self discharge which is extremely low so any differences are so small and insignificant can be ignored.
Couple all that together with LFP batteries that are extremely safe by default, operated in kind conditions, and operate at Low Voltages of 12, 24, and 48 do not need as stringent controls. I know you are talking about cell level, but with 4, 8, and maybe 16S at low discharge rates do not really need it.Comment
-
The one area I have interest in is the saturation phase of charging. Since charging is a leading voltage and the battery voltage is a lagging voltage, how long should the saturation phase be or to what level. If it is measured by say, ending amps ?? The higher the charge rate, the more disparity I see with shunt counted amp hrs returned. By only using a termination voltage of the charge controller there is a undercharge that accumulates by the cycle.
But the question is always, great, but at what voltage? since it really depends upon the application. And should it be measured after hours of rest or during charge? 3.45v *at rest* is considered a fully charged cell. There is some variance, as a GBS prismatic can be from 3.38 to 3.45 or so...
Probably the best thing I've seen is an actual formula for it! It goes something like this for charging:
3.45 + (IR * A)
Where 3.45 is considered the full voltage at rest
IR is your cell internal resistance
A is the charge amperage
Maybe the big guns can comment.
Getting those values can come from a prismatic manufacturer if you ask or perhaps special-order them can be done, so that your cells are individually matched for capacity and internal resistance, and will supply a document sheet matching each one's barcode. Not sure if you can special order small cylindricals this way, or as WB9K points out, impractical to do for commercial projects.Comment
-
This is an interesting question. I don't believe I've ever seen data on pwm-based charging, but I have no reason to believe it makes much if any difference at all to the cells. Many automotive applications drain the cells with high-current PWM at frequencies in the kHz range and nobody considers that a problem. Charging should be no different.
I think - disclaimer - the above comes from an amateur like myself.
The worst part about this is now you have given me a justification to actually look at something like a Fluke 289! (I'm a fluke nut) Dang it - my wallet is bleeding now...
What you are really seeing with cells "drifting together" is the expression of different DC resistances of the series cell-busbar combination. The higher the current, the greater the spread. When you switch from CC to CV(or PWM) the main difference as far as the cell is concerned, is that charge current goes down. The voltage rise (vs. rested voltage) across the whole pack decreases, and so do the differences between cell voltages. Less current, less "Peukert-type" losses, less voltage delta.
In my case with the A123 cells, and also my GBS prismatics, is that the cells have to be SANELY close to each other to begin with, and the drift takes MANY cycles, not just a single day's charging. Of course quality cells make the world of difference. Other NEW cells I pulled from other powersport batteries which were a total JOKE inside, were a waste of time and they just drifted immediately to the recycling center.
Also not that my solar usage is for realatively low-voltage (typically 12v / 4S configs), not mobile, and not critical. No bleeder boards, just common sense HVC, LVC and dose of monitoring since I like to do battery maintenance. Wouldn't hand it over to my neighbor though.
Thanks for the feedback. Anything that makes me want to study deeper is allright!Comment
-
A side note about degradation --
We throw voltage settings around like so much candy (here and elsewhere), and while user lifepo4 projects are valuable for data, I take them with a grain of salt and consider them anecdotal when I can't determine if they are using a quality standard for measurement.
Far too many times I've seen guys building mega-buck battery systems, and then calibrated and monitored by a shirt-pocket or throw-away meter that hasn't been vetted for accuracy. Or not even taking the time to check that the cheapo Junsi cell monitor is even in the ballpark!
I use Fluke for out-of-box trust, but this isn't really a multimeter thread and I don't care what one uses, as long as they TRUST it or have calibrated it. And THEN, using that calibrated meter as the standard for everything else.
I just wonder how many systems dutifully follow the experience of others, only to be bagged by using a throw-away meter, and giving us false data in the forums?
Ok - degradation issue about meter rant over ...Comment
-
Getting back to degradation itself, I have always wondered if any degradation studies have been done for LiFePo4 prismatics (or A123 cells if you prefer) in regards to the fact that as solar users, our charge controllers use PWM in the "absorb" phase (what little there is when fed by decent current!).
In other words, we don't REALLY use CC/CV, but CC/PWM. Typically the pwm is done at about 300hz or so. If looked at on a waveform, this simply means that our controllers just close the circuit during bulk, but once a setpoint has been reached, instead of CV, pwm is actually used. Ie, the voltage can actually shoot up to 4.5 volts per cell! - BUT of course at 300hz, the averaging takes place.
What I noticed when using both prismatics, and my prized A123's from Braille and Antigravity brand batteries was that unlike CV which stops current when the first cell is fully charged, with pwm, they tend to "drift together" - and not an exact balance. We've covered balance enough, but my main interest was how lifepo4 reacts to pwm, since that is what we use in the field. (be it a low-end pwm controller, or an mppt which uses pwm during absorb too actually).
SimonOff-Grid LFP(LiFePO4) system since April 2013Comment
-
The one area I have interest in is the saturation phase of charging. Since charging is a leading voltage and the battery voltage is a lagging voltage, how long should the saturation phase be or to what level. If it is measured by say, ending amps ?? The higher the charge rate, the more disparity I see with shunt counted amp hrs returned. By only using a termination voltage of the charge controller there is a undercharge that accumulates by the cycle.
This is the major difference between charging with a constant current source and the sun. With constant current you can charge to a predictable SOC by charging with constant current to a set voltage cutoff and then terminating the charge. As the amount of sun reaching our solar panels is variable we do not get the same amount of charge in the battery every time it is charged. I have found that when charging to around 3.4 volts/cell and ending the charge at a charge rate of C/20 that the final SOC achieved can be anything between around 80% and 90+%. If it is sunny for the whole period that the battery is being charged the final SOC will be around 80%, if it is cloudy or it is nearly the end of the day when the charging is nearly finished the final SOC can be greater than 90%. I have reduced this problem by ending the charge at C/50 rather than the C/20.
SimonOff-Grid LFP(LiFePO4) system since April 2013Comment