LiFeP04 Batteries for Solar & BMS
Collapse
X
-
-
In a Solar System you are fighting one HUGE BATTLE every day. Time, you don't have enough of it to mess around with any SATURATION. You DO NOT NEED and Saturation as it destroy CYCLE LIFE. Why would any fool want to do that? Lithium batteries are extremely easy to charge. To get to 90% SOC all they require is a Constant Current applied until the cell voltage reaches reaches 3.45 volts. So back to TIME and SOLAR. You do not have TIME on your side. The fastest way to 90% SOC is CONSTANT CURRENT, as much power as your panels can generate.
What is so damn hard you cannot understand Willy. Even a child can understand that. EV manufactures understand that. Most of the DIY EV understands that. Why can't you?. Yes you are stuck in a Pb World because you still use the 4-stage Pb mentality. Lithium Charge is clearly defined, has been for 10 years and you still do not know it. I will tell you what it is, CC/CV. It is that simple. If you only want to go to 90% to maximize battery life, Constant Current to 3.4 to 3.5 volts per cell and you are DONE. Saturate them like you are doing and you cut cycle life 30 to 50%. I am not going to allow you to tell people to destroy their batteries because of your ignorance and incompetence.
Winston is LFP aka LiFeP04. When you use a Solar Panel with a conventional off the shelf charge controller, the charge controller never terminates the charge until darkness. Even if you set BULK, ABSORB, and FLOAT to 14.3 volts as you claim you are saturating the batteries to 3.575 volts which is above 100% SOC.
There are two ways to charge a Lithium Ion Battery:
1. Is a 2-stage Constant Current / Constant Voltage method which is basically what you are forced to do with Solar Charge Controllers on the Market.
1. As you have said Set the Bulk, Absorb and Float voltages to be the same (I think a lot of controllers on the market will not let you do this). The charge controller will charge the battery at whatever variable current the panels will supply until the controller voltage equals the set voltage at which point the current will start tapering off till it reaches zero.
2. Set the Bulk voltage to the charge voltage you want, set the Absorb time to zero if possible and set the Float voltage to less that the rest voltage of the battery at the SOC that you have charged it to. If the output from the solar panels is constant you will get the fast charge method you outlined in your method 2.
3. Set the Bulk voltage to the charge voltage you want, set the Absorb time to 30 minutes or so and the Absorb end current to whatever current you want to terminate the charge at, say C/20
SimonOff-Grid LFP(LiFePO4) system since April 2013Comment
-
I don't know of any that use loose electrolyte. Some spiral roll the cells up and they look like a coke can. The cells are vented to the atmosphere that I know of ,GBS, CALB, Winston, Hipower , but the pouches I don't know . I sure someone will find some kind of battery that is different.
Polyymer lithium batteries are not real useful because they have very high internal resistance limiting charge and discharge rates to less than 1C. They last forever, but poor performance. Chi-Com Thundersky design is a 2 to 4C rate battery burst up to 10C. Only a Gel, Paste, or liquid electrolyte can do that. Polymer plastic sheets just don't cut it and can get the surface contact area close enough to have low resistance. Polymer ar great for low power applications, but not capable of high power.MSEE, PEComment
-
You just lost all credibility here. Even a first year electrical student knows SOLAR PANELS ARE CURRENT SOURCES, not Voltage Sources like a battery or utility. Look it up. Hint: Isc/Imp and Bulk mode charge phase.MSEE, PEComment
-
This is not true of all the programmable charge controllers I have come across. Charge controllers will stop charging an LFP battery after the battery reaches the Bulk Termination voltage, has gone through the Absorb phase at the Absorb voltage for a fixed or programmable time period or on some controllers until the charge current has dropped to a programmable level and then drops down to the Float voltage and the Float voltage is set low enough.
To charge a LFP battery as fast as possible with a off the shelf Charge Controller you set Bulk = Absorb = Float = Target SOC%. This forces the controller to operate in CC/CV mode. The CC will pump as much current into the batteries as the panels can generate. This is the Constant Current phase to charge as fast as possible. When the voltage reaches Set Point the CC then switches to Constant Voltage and the current will Taper Off to Zero Amps when battery voltage = charger controller voltage Lithium is the only battery that will stop charging when its battery voltage = supply voltage. All others have self discharge and thus never stop charging.
Once equalized as long as there is no load applied current will stop flowing, but the charge controller is still active siting in a FLOAT or Constant Voltage mode. If a load demands current, the panels will supply that power via Charge Controller assuming the load demand does not exceed what the panels can deliver. Works like any Float Service. The charge controller never shuts off until the sunset period end of story. The only question is did your batteries get fully charged up before sunsets
Sorry but you just clearly demonstrated you do not know what you are talking about. You do not know the basic principles of voltage sources, current sources, or even basic fundamentals electrical principles. You are not fooling anyone except yourself.MSEE, PEComment
-
Comment
-
Solar panels are Constant Current Sources operating between Vmp and Isc meaning Constant Current at any operating point on the IV curve. Solar Panels are Voltage Sources operating between Vmp and Voc.MSEE, PEComment
-
That wasn't the context, he was answering you about Constant Current battery charging from solar panels.Comment
-
Off the shelf controllers are not designed to charge Lithium Batteries. Some of them can be set up to work with them if you can set Bulk, Absorb, and Float to any value yyou want and set the to all be equal. That forces them to behave like a Float Charger with Current Limit. Set the voltage to something less than 100% SOC and the controller will be in a Constant Current Mode until the Controller Voltage and Battery Voltage are equal and all current stops flowing assuming there is no load. The Controller will sit there in Float mode acting as a Voltage Source so if a load demands current the power comes from the panels rather than the battery.
To take a Lithium battery to 100% SOC safely, there are two methods.
1. The charger and battery must be matched perfectly. You set the voltage to 3.64 vpc and current limit to as low as C/10 and as high as the manufacture sets limit to like 1C. So for a 12 volt battery like you have would be 3.65 volts x 4 = 14.6 volts. You apply that charge and initially the current is going to be whatever limit is set either from the panel wattage or regulator in the conventional charger say 50 amps on a 100 AH battery. 50 amps will until the battery voltage reaches say 14.5 volts and begin to taper off. You terminate when the current reaches .03C or C/33
2. The second method is a bit easier but much slower. Using a simple CC/CV Float Charger power supply. You set it up to 3.6 volts per cell. Any charge rate can be used within manufactures spec. So for you that would be 14.4 volts. Apply charge until current stops and terminate. Terminate means turn the dang charge off. If you let it float you will damage the batteries. There is the point you can work with using a Solar Charger. You set all the voltage to one setting below 100% like 3.4 volts per cell or 13.6 volts. When the batteries reach 13.6 volts charge current stops, but the Controller is now floating and will supply power to the load when the sun is shinning. Batteries will not supply power to load until the load demands exceeds panels capabilities or after sunset. Exactly what you want to happen. It is not that hard to understand if you know basic electrical fundamentals. If you do not understand you are hopelessly lost and only fooling yourself.
Now get out of my thread or I will nuke it.MSEE, PEComment
-
SimonOff-Grid LFP(LiFePO4) system since April 2013Comment
-
Simon you have proven again you do not understand Charge Controller or Lithium batteries. Charge controller never stop supplying power with sun light striking the panels. Absorb. Float, and EQ are all Constant Voltage Modes. Bulk is Constant Current. Look it up. You do not understand what they mean or do.
To charge a LFP battery as fast as possible with a off the shelf Charge Controller you set Bulk = Absorb = Float = Target SOC%. This forces the controller to operate in CC/CV mode. The CC will pump as much current into the batteries as the panels can generate. This is the Constant Current phase to charge as fast as possible. When the voltage reaches Set Point the CC then switches to Constant Voltage and the current will Taper Off to Zero Amps when battery voltage = charger controller voltage Lithium is the only battery that will stop charging when its battery voltage = supply voltage. All others have self discharge and thus never stop charging.
Once equalized as long as there is no load applied current will stop flowing, but the charge controller is still active siting in a FLOAT or Constant Voltage mode. If a load demands current, the panels will supply that power via Charge Controller assuming the load demand does not exceed what the panels can deliver. Works like any Float Service. The charge controller never shuts off until the sunset period end of story. The only question is did your batteries get fully charged up before sunsets
Sorry but you just clearly demonstrated you do not know what you are talking about. You do not know the basic principles of voltage sources, current sources, or even basic fundamentals electrical principles. You are not fooling anyone except yourself.
SimonOff-Grid LFP(LiFePO4) system since April 2013Comment
-
You are right that Absorb, Float and EQ are Constant Voltage modes. If the battery voltage is greater than the voltages set for the same charging phase the controller will supply no current to the battery, no current means no power, i.e it will stop supplying power to the battery.
Go educate yourself and read up on 3-stage Pb Battery Charging using this link. All commercial off the shelf Charge Controllers except for maybe GenSun, are made for Pb batteries. It starts real clearly describing the 3-Stages every Charge Controller goes through and what each stage does.
Lead acid batteries should be charged in three stages, which are [1] constant-current charge, [2] topping charge and [3] float charge. The constant-current charge applies the bulk of the charge and takes up roughly half of the required charge time; the topping charge continues at a lower charge current and provides saturation, and the float charge compensates for the loss caused by self-discharge.
Bulk MPPT: This stage of the Classic means; that the Classic will be putting out as much current as it can trying to charge the batteries to the absorb voltage set point. This is also known as constant current mode.
The BULK stage involves about 80% of the recharge, wherein the charger current is held constant (in a constant current charger).
MSEE, PEComment
-
Some graphs for the bottom/top balance debat
What is the difference?
Here the red cell is 95 Ah, the green cell 100 Ah and the blue cell 105 Ah. For a pre-balanced pack the charge you can use is always depending on the weakest cell.
LiFePo Top Balanced web.png
LiFePo Bottom Balanced web.png
LiFePo Not Balanced web.png
Just don't start without pre-balancing.Only shared knowledge can grow.Comment
-
In context that is incorrect. The charger has not stopped providing power, it is still on and active like a wall socket in your home. The battery would be in higher energy state which only happens when you switch from Absorb to a lower Float voltage. That only happens with Pb batteries, what Charge Controller are designed to work with. As soon as the surface charge is absorbed or the load demands power the controller is then providing current. At no point does it ever turn off power except at night. Duh!All commercial off the shelf Charge Controllers except for maybe GenSun, are made for Pb batteries.
Here is my explanation for how the terminology "Constant Current" has been adopted by some of the solar controller manufacturers to describe how their products charge a battery.
Before the advent of solar power most batteries were charged by current limited chargers connected to a generator, the power grid or whatever. This current limit was constant and so we get the term Constant Current Charging, this had been going on for over 50 years before solar controllers came along and everyone, both engineers and lay people got used to the term and it correctly described what was happening.
The solar controller manufacturers adopted the same terminology that had been used in the past that everyone understood, so they adopted the term Constant Current Charge even though from an engineering point of view it is not true, as the current from solar panels is not necessarily constant. For Lead batteries it probably doesn't matter whether or not the current is a fixed constant as any variation in the SOC achieved by the battery because of the differing charge current is balanced out by the Absorb phase of the charging. The term "Constant Current Charging" has stuck even though it is not strictly true.
Lead acid batteries should be charged in three stages, which are [1] constant-current charge, [2] topping charge and [3] float charge. The constant-current charge applies the bulk of the charge and takes up roughly half of the required charge time; the topping charge continues at a lower charge current and provides saturation, and the float charge compensates for the loss caused by self-discharge.
The BULK stage involves about 80% of the recharge, wherein the charger current is held constant (in a constant current charger).
Bulk MPPT: This stage of the Classic means; that the Classic will be putting out as much current as it can trying to charge the batteries to the absorb voltage set point. This is also known as constant current mode
SimonOff-Grid LFP(LiFePO4) system since April 2013Comment
-